cat5 in HV electrical box?
This thread has 35 replies. Displaying posts 31 through 36.
Post 31 made on Tuesday February 14, 2006 at 08:34
Larry Fine
Loyal Member
Joined:
Posts:
August 2001
5,002
On February 13, 2006 at 19:53, ceied said...
ok larry in english what does it mean?

ed

It means that this is legal, as long as the low-voltage wires are (A) CL-3, CL-3R, or CL-3P, and (B) that at least 1/4" separation between the stripped portion of the low-voltage conductors and the power wiring is maintained, or a non-conductive sleeve is covering the stripped portion of the low-voltage wires.

By stripped, I mean where the outer sheath of the low-volateg cable has been removed.
Post 32 made on Tuesday February 14, 2006 at 09:16
CCD
Super Member
Joined:
Posts:
August 2005
2,731
On February 14, 2006 at 06:31, bcf1963 said...
I haven't looked, but perhaps someone else will
have seen this...

Anyone know of a clear plastic box divider. This
would allow for a single box. You could place
the blaster in the low voltage portion, and allow
it to blast through the clear plastic divider
to the IR controlled switch.

Such a low tech solution... so unlike me, now
the only question is, does anyone make one?

HMM...taking this a little further how about a hv box with a clear window. 1963... your idea is probably better but your partition only needs to house about 1 cu." for the blaster/emitter. Good thinking. Now that's thinking inside the "box". bad pun
Post 33 made on Tuesday February 14, 2006 at 11:40
ejfiii
Select Member
Joined:
Posts:
July 2003
2,021
I am sitting in a 3 day lighting class at Crestron right now and the instructor just said that a low voltage PLENUM RATED wire can sit IN the same box as the 120VAC wire. Of course we discussed this point for 20 minutes and he agrees that reality of inspections can be different.

Just thought I'd throw it out there.

Thoughts?
Post 34 made on Tuesday February 14, 2006 at 13:48
DIRTE
Active Member
Joined:
Posts:
February 2005
500
On February 14, 2006 at 08:34, Larry Fine said...
It means that this is legal, as long as the low-voltage
wires are (A) CL-3, CL-3R, or CL-3P, and (B) that
at least 1/4" separation between the stripped
portion of the low-voltage conductors and the
power wiring is maintained, or a non-conductive
sleeve is covering the stripped portion of the
low-voltage wires.

By stripped, I mean where the outer sheath of
the low-volateg cable has been removed.

I know what CMR(cable multi-use riser) and CMP(cable multi-use plenum) mean but tried researching the acronym CL and came up with nothing. My question is where can I find the translation of acronyms for a specialty field such as electrical? TIA
"Twenty years from now, you will be more disappointed with the things you didn't do than by the things you did… Explore. Dream. Discover" Mark Twain, 1879
Post 35 made on Tuesday February 14, 2006 at 14:12
Barry Shaw
Founding Member
Joined:
Posts:
June 2001
688
It's always up to your local inspectors.

The only advice I have is talk to the inspectors and the EC *BEFORE* you run LV in a HV box. Ours were very cooperative as we went over the NEC code.

Meet them at their office, take them to lunch, whatever, but *don't* have the first conversation on a jobsite with the prewire already completed. Almost like double-dog daring them to shut you down.

They can be held responsible for their decisions years down the road, so don't force them to make a call on the spot - you may not like the answer & it's not fair to sneak up on them. Sometimes it's all about how you approach authority, turf & egos issues.

We have been sued once over a lighting system that required Cat5 to control wall-box dimmers. The homeowners lawyers contended that LV in an HV box alone was proof that we violated code. The local inspector backed me up 100% because he had personally signed off on that exact application 3 years earlier. I felt very smart that day.
"Crestron's way better than AMX."
Post 36 made on Tuesday February 14, 2006 at 15:32
ceied
Loyal Member
Joined:
Posts:
February 2002
5,753
thanks larry
Ed will be known as the Tiger Woods of the integration business, followed closely with the renaming of his company to "Hotties A/V". The tag line will be "We like big racks and tight holes"...
Page 3 of 3


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.

Hosting Services by ipHouse