Post 1 made on Monday March 16, 2020 at 16:48
Chris L
Founding Member
Joined:
Posts:
October 2001
356
Posting this for a friend since some of the members here do lighting.

He installed the following equipment and sometimes when the lights are turned on the ArcFault trips. He has contacted Lutron and the are sending a different dimmer. That dimmer might not work correctly with the Juno lights.

Siemens
QA120AFC
Combination TT/PE ArcFault
Circuit Interrupter

Lutron
Caseta PD6
APP Controlled Dimmer

Juno
4RLA63 2700K
LED Recessed Light Trim

Any suggestions or can you point me to a message board or someone who might know the answer.

Thanks
Post 2 made on Monday March 16, 2020 at 17:22
davidcasemore
Super Member
Joined:
Posts:
January 2003
3,352
What is the quantity of the Juno lights on that one dimmer?
Fins: Still Slamming' His Trunk on pilgrim's Small Weenie - One Trunk at a Time!
OP | Post 3 made on Monday March 16, 2020 at 20:22
Chris L
Founding Member
Joined:
Posts:
October 2001
356
I will check with the electrician and report back.
Post 4 made on Monday March 16, 2020 at 21:44
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
David asks a good question. We'll probably need to know many more details to figure out the answer to this problem.

You/your friend may need to (and probably should have) contacted the manufacturers of each of these items for recommendations of products to use and to avoid in this setup.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 5 made on Tuesday March 17, 2020 at 09:08
SWOInstaller
Select Member
Joined:
Posts:
October 2010
1,596
Could also be a breaker issue. We (as an electrical contractor) have seen very sensitive AFCI breakers (typically when combined with GFCI protection). I would suggest installing a standard breaker and add a faceless AFCI receptacle [Link: leviton.com] at the panel. This will still meet the code requirement but bypass the sensitive breaker.
You can't fix stupid
Post 6 made on Tuesday March 17, 2020 at 11:09
drewski300
Super Member
Joined:
Posts:
January 2007
3,849
We moved away from Siemens do to their Arc Fault issues. There are so many different generations of breakers that it's tough to say what version they have and if replacing it will fix the problem. Basically each generation has improved their arc signature recognition but it still never solves every problem. David asks the question about the number of lights being dimmed on that particular circuit (not just the switch) because there is a max wattage per breaker (typically 1000 watts). This number is tough to reach with LED but super easy with incandescent lighting.

Long story short, it's the breaker and you may not be able to fix the problem by replacing the breaker unless it's an older gen arc fault breaker. The only fix is illegally pulling out the arc fault breaker and installing a standard breaker. Which we all know will work fine. The question is, do you want to take the liability on if there is a fire....
"Just when I thought you couldn't possibly be any dumber, you go and do something like this... and totally redeem yourself!"
Post 7 made on Tuesday March 17, 2020 at 11:43
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,322
On March 17, 2020 at 09:08, SWOInstaller said...
Could also be a breaker issue. We (as an electrical contractor) have seen very sensitive AFCI breakers (typically when combined with GFCI protection). I would suggest installing a standard breaker and add a faceless AFCI receptacle [Link: leviton.com] at the panel. This will still meet the code requirement but bypass the sensitive breaker.

Do AFCI still trip easily when a vacuum cleaner is used on those circuits and is the requirement to replace as soon as they trip?
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 8 made on Tuesday March 17, 2020 at 12:15
SWOInstaller
Select Member
Joined:
Posts:
October 2010
1,596
On March 17, 2020 at 11:09, drewski300 said...
We moved away from Siemens do to their Arc Fault issues. There are so many different generations of breakers that it's tough to say what version they have and if replacing it will fix the problem. Basically each generation has improved their arc signature recognition but it still never solves every problem. David asks the question about the number of lights being dimmed on that particular circuit (not just the switch) because there is a max wattage per breaker (typically 1000 watts). This number is tough to reach with LED but super easy with incandescent lighting.

Long story short, it's the breaker and you may not be able to fix the problem by replacing the breaker unless it's an older gen arc fault breaker. The only fix is illegally pulling out the arc fault breaker and installing a standard breaker. Which we all know will work fine. The question is, do you want to take the liability on if there is a fire....

Could also be a breaker issue. We (as an electrical contractor) have seen very sensitive AFCI breakers (typically when combined with GFCI protection). I would suggest installing a standard breaker and add a faceless AFCI receptacle [Link: leviton.com] at the panel. This will still meet the code requirement but bypass the sensitive breaker.

This is why I suggested adding the faceless AFCI at the panel. This still conforms to Code and allows to use a standard breaker. We do this all the time on Renovation projects or areas where we run into nuisance trips as stated. For some reason the Leviton AFCI devices are less sensitive than breakers.
You can't fix stupid
Post 9 made on Tuesday March 17, 2020 at 12:30
SWOInstaller
Select Member
Joined:
Posts:
October 2010
1,596
On March 17, 2020 at 11:43, highfigh said...
Do AFCI still trip easily when a vacuum cleaner is used on those circuits and is the requirement to replace as soon as they trip?

I would first look at the age of the vacuum. If it's an older unit my guess it uses an AC motor causing the ARC when it starts (same goes for cheaper/older treadmills and other workout equipment). If its a newer vacuum try it on another circuit and see if it trips that breaker as well. If it happens on multiple circuits my guess is its a vacuum issue not a breaker issue. If only happens on one circuit may be an over current issue or a sensitive breaker. I would not replace the breaker right away until investigating more.

We use Schneider electric panels and breakers and have never had a customer complain that their vacuum is tripping breakers.

One issue we did come across was Central Vacuums tripping AFCI breakers. Performing the diagnostic test on the breaker it was tripping on over current not ARC. We installed a standard (non-ARC) High inrush breaker with the faceless AFCI device and the issue stopped.

One other issue was when using a combination AFCI/GFCI breaker. These are a lot more sensitive and with some kitchen appliances plugged in (no real load just lights and clocks), the breaker would trip. We could not determine what appliance was actually causing this so added a GFCI receptacle and replaced the breaker with an AFCI only breaker which fixed the issue.
You can't fix stupid
Post 10 made on Tuesday March 17, 2020 at 15:40
edizzle
Loyal Member
Joined:
Posts:
March 2005
5,916
On March 17, 2020 at 09:08, SWOInstaller said...
Could also be a breaker issue. We (as an electrical contractor) have seen very sensitive AFCI breakers (typically when combined with GFCI protection). I would suggest installing a standard breaker and add a faceless AFCI receptacle [Link: leviton.com] at the panel. This will still meet the code requirement but bypass the sensitive breaker.

are you saying the inline arc device is less sensitive than arc fault breaker?
I love supporting product that supports me!
OP | Post 11 made on Tuesday March 17, 2020 at 17:11
Chris L
Founding Member
Joined:
Posts:
October 2001
356
Thanks for all of the responses, I will pass them along to the electrician.

He is in touch with Lutron and they are aware of the problem but do not have a fix yet.

I will post back the solution once I find out from the electrician. Hopefully it will help someone else out.
Post 12 made on Wednesday March 18, 2020 at 00:13
davidcasemore
Super Member
Joined:
Posts:
January 2003
3,352
On March 17, 2020 at 11:09, drewski300 said...
David asks the question about the number of lights being dimmed on that particular circuit (not just the switch) because there is a max wattage per breaker (typically 1000 watts). This number is tough to reach with LED but super easy with incandescent lighting.

It has to do with the inrush currents from LED drivers. Incandescents don't have this problem.

[Link: unvlt.com]
Fins: Still Slamming' His Trunk on pilgrim's Small Weenie - One Trunk at a Time!
Post 13 made on Wednesday March 18, 2020 at 10:25
drewski300
Super Member
Joined:
Posts:
January 2007
3,849
On March 18, 2020 at 00:13, davidcasemore said...
It has to do with the inrush currents from LED drivers. Incandescents don't have this problem.

[Link: unvlt.com]

So arc fault breakers weren't tripping prior to LED drivers? I believe the UL listing on arc fault breakers state they need to support at least 1000 watts of dimmed tungsten lighting load. Tungsten lighting loads typically have a higher in-rush than standard incandescent loads and are still considered incandescent.

We've seen plenty of problems with dimming and non-LED arc fault circuits. Including having Siemens engineers out to our job site to determine what's going on. They found random things on other breakers (same phase) causing an arc fault breaker to trip.

The overall point is that arc fault circuits can be tricky. The age of the breaker can and the manufacturer can play a huge role into the issues.
"Just when I thought you couldn't possibly be any dumber, you go and do something like this... and totally redeem yourself!"
Post 14 made on Wednesday March 18, 2020 at 13:02
edizzle
Loyal Member
Joined:
Posts:
March 2005
5,916
On March 18, 2020 at 00:13, davidcasemore said...
It has to do with the inrush currents from LED drivers. Incandescents don't have this problem.

[Link: unvlt.com]

yep
I love supporting product that supports me!
Post 15 made on Wednesday March 18, 2020 at 13:07
edizzle
Loyal Member
Joined:
Posts:
March 2005
5,916
On March 18, 2020 at 10:25, drewski300 said...
So arc fault breakers weren't tripping prior to LED drivers? I believe the UL listing on arc fault breakers state they need to support at least 1000 watts of dimmed tungsten lighting load. Tungsten lighting loads typically have a higher in-rush than standard incandescent loads and are still considered incandescent.

We've seen plenty of problems with dimming and non-LED arc fault circuits. Including having Siemens engineers out to our job site to determine what's going on. They found random things on other breakers (same phase) causing an arc fault breaker to trip.

The overall point is that arc fault circuits can be tricky. The age of the breaker can and the manufacturer can play a huge role into the issues.

this is true, but most folks do not understand that LED has a large in rush. in a lot if not all cases more than an equal amount of traditional incandescent loads
I love supporting product that supports me!
Page 1 of 2


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.