|
|
|
The following page was printed from RemoteCentral.com:
NEC Standards for low voltage Commercial...
| |
|
Topic: | NEC Standards for low voltage Commercial work This thread has 20 replies. Displaying posts 1 through 15. |
|
Post 1 made on Wednesday November 1, 2006 at 19:55 |
Instalz Active Member |
Joined: Posts: | April 2005 628 |
|
|
Hi guys. I have been googling for the past hour trying to find some information on low voltage requirements pertaining to commercial work. 99.9% of my commercial work is retro, and I am about to start working up a quote for a new building. Well, it's not new, the exterior is existing, the interior will be new. It got me to thinking about the requirements for voice/data/audio cabling. For instance, wood structure vs. metal structure. I understand that speakers need to be in cans, but what other requirements are there? EMT for instance? I do allot of retro data and voice cabling in schools, I always use emt conduit and/or fireblock when going thru walls or between floors. Thanks all...
|
|
Post 2 made on Wednesday November 1, 2006 at 20:33 |
Fred Harding @ home Long Time Member |
Joined: Posts: | July 2005 414 |
|
|
|
OP | Post 3 made on Wednesday November 1, 2006 at 20:45 |
Instalz Active Member |
Joined: Posts: | April 2005 628 |
|
|
Hi Fred. I understand plenum vs. riser. I guess to be more specific, I am refering to the use of conduit. Using standard open back low voltage boxes vs. closed boxes. When EMT conduit has to be used. Are there any NEC standards that reference commercial low voltage wiring?
|
|
Post 4 made on Wednesday November 1, 2006 at 20:46 |
TouchCommander Active Member |
Joined: Posts: | December 2004 602 |
|
|
You need to find out what NEC codes (year) your local inspector uses. Some cities are many years behind the current NEC codes.
|
No job to small, many to big |
|
OP | Post 5 made on Wednesday November 1, 2006 at 20:47 |
Instalz Active Member |
Joined: Posts: | April 2005 628 |
|
|
By the way Fred, Dave B. is an awesome guy to work with....
|
|
OP | Post 6 made on Wednesday November 1, 2006 at 20:49 |
Instalz Active Member |
Joined: Posts: | April 2005 628 |
|
|
Thanks T.C. I am wondering about current code requirements.
|
|
OP | Post 7 made on Wednesday November 1, 2006 at 20:59 |
Instalz Active Member |
Joined: Posts: | April 2005 628 |
|
|
I have an example for you. A couple of months ago I had an electrician tell me that low voltage wiring can no longer be sitting on a drop ceiling. It must be tied up off the ceiling. Last week I watched an electrician run romex in a suspended ceiling, and lay it on the ceiling tiles. No, I didn't say anything :) Is low voltage wiring really that free so far as where we run, and how we run our cabling? By the way, most of the time, I secure my wiring above the tiles. I do this because I spend allot of time cursing people who don't, when I'm trying to put a ceiling tile back into place, and fire alarm wire keeps popping out.
|
|
Post 8 made on Wednesday November 1, 2006 at 21:43 |
skyflyer007 Long Time Member |
Joined: Posts: | July 2004 279 |
|
|
Each state has its own reuirements as far as what is required. You must find out what is required in your area.
Most low voltage companies never read the NEC or do their jobs by the book. Many states dont even require low voltage to be inspected.
A good place for information is the Mike Holt website which also includes a forum which addresses low voltage.
Any specific advice you receive here is useless until you know what is required in your state. Many counties and cities within a state also tack on their own unique code requirements. What state are you in ?????
|
|
Post 9 made on Wednesday November 1, 2006 at 22:15 |
briremo Senior Member |
Joined: Posts: | December 2005 1,374 |
|
|
Here's some general items for considerations that I've learned through osmosis. Of course some items may be different based on your AHJ but I've found these to be rather universal...
1) speakers need not be in boxes unless ceiling is plenum rated i.e. the air return is non-ducted. 2) All freewire or LV cabling must be off the ceiling tile and grid. This is mainly to prevent chafing and snags on the grids sharp edges (shorts). 3) Plenum rated cable is needed for freewiring in plenum rated ceilings only. To simplify, plenum rated cable does not give off noxious fumes when exposed to fire and has a slower burn rate. you can use CL rated cable in plenum ceilings as long as it's in conduit. 4)all drops down the wall must be in rigid conduit and terminate in a box. Which is bitch because getting a VC in box sucks. Use depp back boxes for everything. Use a grommet where the free wire goes into the conduit. 5) We usually wrte the spec so conduit is "by others" that way we can just show up and fly, plus the EC can do it cheaper. 6) If the client wants to save money, frequently we'll pull the wire and hang loops above the drop locations and sell the job as a prewire only "for future use". Then after CO we'll come in and drop all the wires down the wall freewired so the owner can avoid all the additional conduit costs. Generally we only do this for video and audio runs. Telco and data is different, it has to be there.
My .02
Brian @ Connect Source
|
feed a dog and he will not bite you. this is the principal difference between a man and a dog. Mark Twain |
|
Post 10 made on Wednesday November 1, 2006 at 22:23 |
idodishez Select Member |
Joined: Posts: | May 2003 2,433 |
|
|
We just did 27 data drops in an office/commercial building. I was battling some of the same issues. A lot of the existing drops WERE in rigid conduit, and closed back boxes. BUT, where they wanted NEW drops, they already had LV boxes (no back) and no conduit installed. They had pulls strings all ready for us to pull the drops. So, we used they boxes and no conduit that they provided. Hopefully we'll be ok.
|
No, I wont install your plasma with an orange extension cord hanging down the wall. www.customdigitalinc.com |
|
Post 11 made on Wednesday November 1, 2006 at 22:58 |
cma Super Member |
Joined: Posts: | August 2003 3,044 |
|
|
Don't forget fire rating, most fire districts will not allow two boxes in the same wall cavity back to back unless you wrap the box in fire putty.
|
|
OP | Post 12 made on Wednesday November 1, 2006 at 23:23 |
Instalz Active Member |
Joined: Posts: | April 2005 628 |
|
|
This is the stuff I'm talking about.... briremo, thanks for your list. idodishez, I've found myself in similar situations. Doing work, and crossing my fingers. That's why I'm asking this question. cma, that's not one that I was aware of. Thanks guys. Anyone else have anything to add?
|
|
Post 13 made on Thursday November 2, 2006 at 00:16 |
Ernie Bornn-Gilman Yes, That Ernie! |
Joined: Posts: | December 2001 30,104 |
|
|
Whenever you're dealing with code and you don't know what it is, get into the mindset of keeping people from being electrocuted, burned up, breathing poisonous fumes, or having stuff drop out of the ceiling on them. That last one is why stuff should not be laid across ceiling tiles. Also, Romex on a ceiling tile, in a fire, will first create poisonous fumes (is there plenum Romex?). Then, when the insulation melts, it will electrically energize the entire T-bar grid until a circuit breaker blows. On November 1, 2006 at 20:59, Instalz said...
I have an example for you. A couple of months ago I had an electrician tell me that low voltage wiring can no longer be sitting on a drop ceiling. It must be tied up off the ceiling. I first saw this enforced in a TI build-out in 1988. The code, taken literally, said that each low-voltage wire must be separated from each other wire by some distance which I forget. The upshot was that the code made it legally impossible to run 3-pair phone wire out to ten new stations. The answer? Ask the inspector what to do. He said to tie them together, just as we normally do, and attach ties so they are supported from the T-bar support wires that hold up the T-bar frame. Wires are to be between six and 12 incches above the ceiling tiles; supports are to be 48" max apart from one another. I can't see how this might have loosened up in the intervening time, but it might have gotten more stringent. By the way, most of the time, I secure my wiring above the tiles. I do this because I spend allot of time cursing people who don't, when I'm trying to put a ceiling tile back into place, and fire alarm wire keeps popping out. It is also amazing just how far you will go to meeting code if you just do the things like this that would keep you from being irritated if you had to service it.
|
A good answer is easier with a clear question giving the make and model of everything. "The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw |
|
Post 14 made on Thursday November 2, 2006 at 00:32 |
Barry Shaw Founding Member |
Joined: Posts: | June 2001 688 |
|
|
On November 1, 2006 at 23:23, Instalz said...
Thanks guys. Anyone else have anything to add? Take the time to introduce yourself to the inspectors in your area and always ask them IN ADVANCE when you have a question how *they* want to interpret the NEC code. So few people do this they will remember & maybe even respect you for asking. It's been my experience they have a MUCH better attitude when approached like this. The reason everybody you'll ask has different experiences & opinions is it's all in how *their* local inspectors read the code from area-to-area & year-to-year. The CORRECT answer is usually whatever your local guys say it is, and they can change their minds as they need and/or want to. They are not always just being inconsistent for sport, they learn about new *issues* all the time, just like we do. Some of their issues make the front pages, so that's their mindset sometimes. Edit... Ernie types faster than I do.. On November 2, 2006 at 00:16, Ernie Bornn-Gilman said...
The answer? Ask the inspector what to do. Yeah... what he said.
|
"Crestron's way better than AMX." |
|
Post 15 made on Thursday November 2, 2006 at 01:49 |
Dave E Long Time Member |
Joined: Posts: | September 2005 282 |
|
|
The National Electric Code (NEC) is published by the National Fire Protection Association 800-344-3555. Call them and request a catalog. You can order hundreds of code books written by NFPA. The NEC is NFPA70. It has requirements for low voltage grounding, TV Antennas, Cable TV, telephone lines, fire alarm wiring, security wiring, computer, intercom, music systems, satellite dishes etc. as well as requirements for high voltage. I would recommend that you purchase the NEC Handbook instead of the NEC code book. The Handbook has all of the NEC code plus commentary about why the code requires certain things. Knowing why helps you understand the need to do it the right way. It has a good explanation why the cable TV ground, antenna ground, satellite dish ground, telephone ground, security system ground and electrical panel ground must be tied together. Some areas may require permits to do low voltage work and other areas do not. Check with the AHJ (Authority Having Jurisdiction). The AHJ may be the local building department. If your local jurisdiction has adopted a version of the NEC then IT IS THE LAW. Even if you are not required to pull a permit, YOU ARE REQUIRED TO FOLLOW ALL REQUIREMENTS OF THE NEC THAT PERTAIN TO THE LOW VOLTAGE WORK YOU DO. If lightning strikes a building and someone is injured or a fire starts or expensive equipment is damaged because your low voltage work was not properly run or grounded, the insurance company and the attorneys will be contacting you. Remember Olin’s Law, “There will be a fatal fire tomorrow, and the next day you will be in court explaining why you did what you did and why you didn’t do what you didn’t do”.
Whew! I’ll step off the soap box now.
|
Experience is what you get when you don't get what you want. Any wire cut to length will be too short. I must be a near GENIUS. All my teachers told me I was at the very PEAK of the bell curve! |
|
|
Before you can reply to a message... |
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now. |
Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.
|
|