Sections 210.19(A), 215.2 and 230.42(A) require the conductor to be sized no less than 100% of the noncontinuous load, plus 125% of the continuous load. I check the breaker, but also look to be sure the wire is sized correctly for the breaker to verify what that circuit will carry.