Post 6 made on Thursday April 3, 2014 at 14:50
ericspencer
Active Member
Joined:
Posts:
December 2011
536
Sections 210.19(A), 215.2 and 230.42(A) require the conductor to be sized no less than 100% of the noncontinuous load, plus 125% of the continuous load. I  check the breaker, but also look to be sure the wire is sized correctly for the breaker to verify what that circuit will carry.
Not my circus, not my monkeys