Post 1 made on Thursday April 3, 2014 at 13:05
SOUND.SD
Loyal Member
Joined:
Posts:
April 2006
5,523
We have a client that would like to have a UPS on two office computers.

2 problems exist. First, he doesn't want the bulky and unsightly UPS on the floor or visible in the room. Second, he wants to protect both machines which will be physically located on opposite sides of the room.

My solution is to put the ups in the rack and run two outputs into two separate powerlinks as essential an in wall rated extension cable.

In theory this feels like a good, and might a say genius, solution. The clients IT guy had to some concerns about extending the wire. This seems like a valid concern based on wire gauge and heat etc.

Thoughts?
Bulldog AV - San Diego, CA
www.bulldog-av.com
[Link: facebook.com]
Post 2 made on Thursday April 3, 2014 at 13:13
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
We have a client who is running his entire theater on a UPS... it can be done. This UPS takes up two racks, each one of which would swallow up our average rack.

Put the UPS in the room with the circuit breakers. Run power from there to outlets at each computer. Done.

I don't understand the reference to heat being a problem. 14 ga wire, which is standard for extending an outlet as you would do if you had the UPS in the room, is NOT going to get warm when powering a computer. A toaster, well, maybe. A computer? No. Get out your table of wire gauges, diameters, resistance, etc (you DO have that as part of your engineering armamentarium, no?) and calculate the amount of power the wire would dissipate per foot of wire for, say ten amps, which is way more than a computer would draw. When that figure turns out to be exceedingly low, you will have proof that there will be no problem.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 3 made on Thursday April 3, 2014 at 13:20
Neurorad
Super Member
Joined:
Posts:
September 2007
3,011
No problem, if you can get the Romex where you need it.
TB A+ Partner
Believe nothing, no matter where you read it, or who said it, no matter if I have said it, unless it agrees with your own reason and your own common sense. -Buddha
Post 4 made on Thursday April 3, 2014 at 14:10
Mogul
Senior Member
Joined:
Posts:
May 2010
1,164
Yes, it is genius...And I do it on nearly every installation ;-).

I install a rack UPS and have Sparky wire 12AWG "extensions" from an inlet near the UPS to an outlet at the piece of equipment I want to support.
"Whatever is rightly done, however humble, is noble." [Sir Henry Royce]
Post 5 made on Thursday April 3, 2014 at 14:23
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
You might want to have Sparky check the NEC.

The gauge of wire that is installed is not only supposed to be large enough to carry the necessary current, its gauge signals to subsquent electricians how much current they should expect will come from that piece of wire. It's my understanding that any such branch from an outlet that comes from a breaker (naturally) is supposed to be 14 ga. Don't tell an electrician, by the size of the wire that's installed, that 15 amps are available when only five or ten are.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 6 made on Thursday April 3, 2014 at 14:50
ericspencer
Active Member
Joined:
Posts:
December 2011
536
Sections 210.19(A), 215.2 and 230.42(A) require the conductor to be sized no less than 100% of the noncontinuous load, plus 125% of the continuous load. I  check the breaker, but also look to be sure the wire is sized correctly for the breaker to verify what that circuit will carry.
Not my circus, not my monkeys
Post 7 made on Thursday April 3, 2014 at 15:28
para19
Long Time Member
Joined:
Posts:
December 2012
124
On April 3, 2014 at 14:10, Mogul said...
Yes, it is genius...And I do it on nearly every installation ;-).

I install a rack UPS and have Sparky wire 12AWG "extensions" from an inlet near the UPS to an outlet at the piece of equipment I want to support.

+1

Only thing I would add is that you should make sure the UPS Supported receptacle is marked that it is powered from the UPS (ie. Red Receptacle with label "UPS Supplied").

Just in case some body wants to do work on the receptacle they will know to unplug it from the UPS.

Last edited by para19 on April 3, 2014 15:38.
There is always money in the banana stand...
Post 8 made on Thursday April 3, 2014 at 15:47
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
eric,
I was remembering what I first learned over a dozen years ago about wire sizes on branch circuits. I guess I confuzzled that with an overseas spec I recently ran into where the wire's size is also limited to a maximum size for the available amperage. The reasoning is that you don't want an electrician to run across, say, an 8 gauge wire coming from a branch from an outlet on a 7 amp breaker (Euro 230V value) because the electrician would then expect that A LOT of current was available, when it was not.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 9 made on Thursday April 3, 2014 at 16:06
para19
Long Time Member
Joined:
Posts:
December 2012
124
On April 3, 2014 at 15:47, Ernie Gilman said...
eric,
I was remembering what I first learned over a dozen years ago about wire sizes on branch circuits. I guess I confuzzled that with an overseas spec I recently ran into where the wire's size is also limited to a maximum size for the available amperage. The reasoning is that you don't want an electrician to run across, say, an 8 gauge wire coming from a branch from an outlet on a 7 amp breaker (Euro 230V value) because the electrician would then expect that A LOT of current was available, when it was not.

Ernie, I fell you are a little confused with wire gauge vs. current available.

Its very common to up size the wire to combat voltage drop but no "qualified" electrician would look at wire size and from that alone figure out available current.

In theory every outlet in the house has unlimited current at it. Breakers are the method that we us to limit the current to safe levels to protect the wire and device from damage
There is always money in the banana stand...
OP | Post 10 made on Thursday April 3, 2014 at 17:34
SOUND.SD
Loyal Member
Joined:
Posts:
April 2006
5,523
Awesome guys. Thanks!
Bulldog AV - San Diego, CA
www.bulldog-av.com
[Link: facebook.com]
Post 11 made on Thursday April 3, 2014 at 19:07
Dave in Balto
Super Member
Joined:
Posts:
January 2008
2,771
I do it all the time with projectors, don't see why it should be a problem, just label it as said before.
Hey, careful man, there's a beverage here!

The Dude


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.