Controlling Three way switch
This thread has 5 replies. Displaying all posts.
Post 1 made on Tuesday January 27, 2004 at 12:29
marainwa
Long Time Member
Joined:
Posts:
January 2004
35
In my entertainment room, the can lights can be controlled by a swtich on either side of the room. Is there a certain X10 wall switch i need to get where I can turn the lights on or off, as well as dim them with a remote?
Post 2 made on Tuesday January 27, 2004 at 13:12
Bill E.
Founding Member
Joined:
Posts:
July 2001
947
Just about every X10 switch on the market has available slaves for 3-way applications. You will also need an IR543 to convert from IR to powerline control.

Look at this link for switch choices:
[Link: homeautomationnet.com]

Bill
www.homeautomationnet.com

Post 3 made on Wednesday January 28, 2004 at 03:54
davehk
Long Time Member
Joined:
Posts:
March 2003
123
I'm curious about something - why do Americans refer to a Single Pole Double Throw switch as a "3-way" switch. I know it has three terminals, but the current can only flow two ways and the switch has only two positions.

Confuses me every time as we in the UK refer to this as "two way". I guess you could call it "4-way" as there are four combinations of positions for the pair of switches!
Post 4 made on Wednesday January 28, 2004 at 13:10
Larry Fine
Loyal Member
Joined:
Posts:
August 2001
5,002
No, that's not confusing enough.

We call the (one or more) switches between three-ways for additional control locations "4-way switches". They do, indeed, have four terminals, and are actually DPDT switches with crossover jumpers, rendering them reversing switches.

I guess we don't have any 2-way switches; the closest we come is double-pole switches, which again have four terminals. Yikes!

Larry
www.fineelectricco.com
Post 5 made on Thursday January 29, 2004 at 06:26
davehk
Long Time Member
Joined:
Posts:
March 2003
123
Yes, we have those, we call them "intermediate" switches.

Whilst I'm here - am I right in thinking that the 220v domestic "two phase" supply you guys use is actually 110-0-110, with the neutral on the OV centre/center tap?
Post 6 made on Thursday January 29, 2004 at 08:41
Larry Fine
Loyal Member
Joined:
Posts:
August 2001
5,002
That is correct. Center tap is the grounded neutral. This limits the voltage to ground.

Larry
www.fineelectricco.com


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.