*BOINGGGG!* Somebody call?
Glenn, breakers no. 1 and 2 share the same phase, 3 and 4 do, 5 and 6 do, etc. They alternate phase as you go down the panel, A, B, A , B, etc. Therefore, (in a single-phase panel) breakers 1,5,9,13,etc. are the same phase, as are 2, 6, 10, 14, etc. A pair of opposing breakers (#1 & 2, for example) share the same lug on one bus (metal bar) in a panel.
Just for info's sake, in a 3-phase panel, 1and 2, 3 and 4, etc, also share the same respective phase. However, to find the same phase on one side, which go A, B, C, A, B, C, etc, you'd have to use breaker nos. 1, 7, 13, 19, etc., Why do they do this? Glad you asked!
They try to make it
impossible to use the same phase more than once with a two- (or three-)pole breaker, because doing so would overload the neutral in a multi-wire circuit, and not provide differing potentials between (among) all hot wires.
A multi-pole breaker straddles the lugs of adjacent spaces, so a breaker installed anywhere in a panel will attach to one phase per breaker pole. A two-pole breaker hits both hot legs, and a three-phase breaker does likewise to all three hot legs in a three-phase panel.
By the way, in most instances, you can use a two-pole breaker in a three-phase panel to power a single-phase load. I won't go into the specifics here (unless someone asks), but suffice it to say that it's not a do-it-yourself task. In some services, one of the hot wires has a higher phase-to-neutral voltage than the others do (called the 'high leg').
Now that I've thoroughly confused you, the answer to your question is that any adjacent pair of poles is what you would use, just like any two-pole breaker in the panel does. You can do this, but I highly recommend hiring an electrician for the average user.
The proper way is to buy a new 15-amp, double-pole breaker, and
after turning off the main breaker, place it in a new position in the panel, hooking the white wire(s) from the coupler to the neutral bus (look for most of the white wires), and one black coupler wire to each breaker terminal. (If there are 3 blacks, cap the unused one with a wire nut)
I noticed you have a Federal-Pioneer panel. I'm familiar with Federal-Pacific, which may or may not be the same. Are the breakers called "Stab-lok"? That's the Federal-Pacific name for them. You might have trouble finding that brand, as it's kinda outdated. Let me know if you do, I may be able to help you.
Larry in TN needed the tandem breakers he mentioned because his panel was full. (Boy, was it ever!) Generally, a full panel (when new) is a sign of poor planning. There should always be room for adding circuits, even if that means installing two panels.
A panel is limited to 40 circuits, and even panels with fewer
spaces can be made to handle more circuits by using tandem breakers, which are two breakers that are either in half-size cases, or are two breakers in a single case.
One has to be extra careful to not place two circuits sharing a neutral on the same phase, which I mentioned a few hours ago in the beginning of this post. When using two-pole tandems, again it's imperative that the two poles stab onto separate phases.
Whew!
Larry