| Topic: | CB-8 pass 232? This thread has 8 replies. Displaying all posts. |
|
| Post 1 made on January 18, 2010 at 13:49 |
|
Joined: Posts: | January 2010 24 |
|
|
Hi there, It says in the manual that the connecting block passes IR to control system, but doesn't say anything about 232. Does it also pass 232? Here's my routing:
KP4 with 232 programmed buttons + IR programmed buttons going to CB-8 Also a KP3-V with 232 programmed buttons going to CB-8 CB-8 to RP-6 RP-6 232 out to different devices. I'm assuming it must, but have learned never to assume anything
Cheers
|
|
| Post 2 made on January 18, 2010 at 14:37 |
|
Joined: Posts: | October 2004 480 |
|
|
Do you mean a K4 and an RK-3? If so, Yes, you can do RS232 and controll a device! FASTLS
|
|
| OP | Post 3 made on January 18, 2010 at 15:10 |
|
Joined: Posts: | January 2010 24 |
|
|
You mean through the CB-8 connecting block right?
|
|
| OP | Post 4 made on January 18, 2010 at 15:33 |
|
Joined: Posts: | January 2010 24 |
|
|
 Another way of saying it.. Following the blue line from K4 -> CB-8 -> RP-6 Will the RP-6 output the 232 code I assigned in Integration Designer for the K4? I'm almost certain it will, but just making sure.
|
|
| Post 5 made on January 18, 2010 at 15:36 |
|
Joined: Posts: | October 2004 480 |
|
|
Yes, It can run the RS232 as long as you use the CM232. FASTLS
|
|
| OP | Post 6 made on January 18, 2010 at 15:43 |
|
Joined: Posts: | January 2010 24 |
|
|
|
| Post 7 made on January 18, 2010 at 18:35 |
|
Joined: Posts: | December 2007 4,149 |
|
|
On January 18, 2010 at 14:49, bencn said...
Hi there, It says in the manual that the connecting block passes IR to control system, but doesn't say anything about 232. The problem you are having is thinking that the commands are being held in the keypads. Thay aren't, not when you are using a processor like the RP-6. All the commands are stored on the RP-6, and the only thing being transmitted through the CB-8 are trigger codes for the processor. Now, in stand-alone scenario, a standard IR connecting block will NOT pas 232 codes, for that you will have to use a CPB-1.
|
"You can't fix stupid." |
|
| Post 8 made on January 19, 2010 at 01:40 |
RTI Installer Super Member |
Joined: Posts: RC XP: | March 2002 3,321 24⭐︎ |
|
|
On January 18, 2010 at 19:35, anyhomeneeds said...
The problem you are having is thinking that the commands are being held in the keypads. Thay aren't, not when you are using a processor like the RP-6. All the commands are stored on the RP-6, and the only thing being transmitted through the CB-8 are trigger codes for the processor. Now, in stand-alone scenario, a standard IR connecting block will NOT pas 232 codes, for that you will have to use a CPB-1. This is the correct answer
|
Never Ignore the Obvious -- H. David Gray |
|
| OP | Post 9 made on January 20, 2010 at 10:40 |
|
Joined: Posts: | January 2010 24 |
|
|
|
 |
Before you can reply to a message... |
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now. |
Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.
|
|
|
|
|