Slightly OT: Title 24 Crazy Outlet Requirement
This thread has 15 replies. Displaying all posts.
Post 1 made on Thursday July 2, 2015 at 15:33
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,076
My sons are discussing this online. Have you ever heard of this, or have you ever had to deal with anyone with an office like this?

From [Link: lutron.com], here's Item 10 on Page 6:

10) Automatic Receptacle Control
[Section 130.5(d)]
Controlled receptacles that automatically shut-off are required in private offices, open offices, lobbies, copy rooms, kitchenettes, and conference rooms
• At least one controlled receptacle must be within 6 feet of an uncontrolled receptacle; this can be accomplished by switching one of the two outlets in each receptacle
• Controlled receptacles need to be marked to differentiate them from uncontrolled receptacles
Note: Plug-in strips and other plug-in devices that incorporate an occupancy sensor can’t be used to comply with this requirement.

Lutron Solution:
• 20A PowPak® relay module
• 20A Energi Savr Node with SoftSwitch®
• XP switching module

From their discussion:
"But yes, decisions would have to be made by users as to where to plug in
what device.

"Alternatively, you simply install a Wacky Waving Inflatable Arm Flailing
Tube Man in every space to ensure that the occupancy sensor stays triggered."
(My son, related sense of humor)

The list of things that must be shut off when nobody is sensed includes:
OK by me: Computer monitors, computer speakers, plug-in space heaters (these were always iffy), fans, task lights, Displays, refrigerator and freezer case lighting, audio amplifiers (iffy if connected to the internet);

Not so ok: air purifiers (because pollen, mold, and dust wait for you to arrive before they invade), radios (your XM buffer is empty and it did not receive that update), coffee makers (with clocks), projectors, audio amplifiers, Water dispensers (with Hot and Cold)
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 2 made on Thursday July 2, 2015 at 15:38
jimstolz76
Loyal Member
Joined:
Posts:
December 2007
5,607
that was your 24,000th post.
Post 3 made on Thursday July 2, 2015 at 16:04
radiorhea
Super Member
Joined:
Posts:
May 2002
3,264
that is a lot of posts...
Drinking upstream from the herd since 1960
Post 4 made on Thursday July 2, 2015 at 16:04
radiorhea
Super Member
Joined:
Posts:
May 2002
3,264
i haven't even posted 2400
Drinking upstream from the herd since 1960
Post 5 made on Thursday July 2, 2015 at 17:33
kgossen
Super Member
Joined:
Posts:
March 2008
3,026
On July 2, 2015 at 16:04, radiorhea said...
i haven't even posted 2400

But your 2300 posts have 10 times more substance than his 24000.
"Quality isn't expensive, it's Priceless!"
Post 6 made on Thursday July 2, 2015 at 18:25
King of typos
Loyal Member
Joined:
Posts:
June 2002
5,265
On July 2, 2015 at 17:33, kgossen said...
But your 2300 posts have 10 times more substance than his 24000.

Where's that damn Like button?

KOT
Post 7 made on Thursday July 2, 2015 at 18:39
radiorhea
Super Member
Joined:
Posts:
May 2002
3,264
8.>/
Drinking upstream from the herd since 1960
Post 8 made on Thursday July 2, 2015 at 19:09
RandyWalters
Long Time Member
Joined:
Posts:
December 2006
97
Another big problem with these controlled receptacles is office workers plugging their PCs into the controlled portion. We're selling a lot of them on Title 24 TI projects.

[Link: leviton.com]
Randy
URC MX-890, MX-780, MX-450, R40, MX-500, Sony XBR-55X900E, Panny TC-P55ST60, Tivo Roamio Pro & Premiere & OTA, TWC Arris DVR, Onkyo 333 AVR, Roku Express 4K, Panasonic Blu-Ray
Post 9 made on Thursday July 2, 2015 at 21:22
mcn779
Senior Member
Joined:
Posts:
February 2003
1,070
"refrigerator and freezer case lighting" aren't these controlled already?
Post 10 made on Thursday July 2, 2015 at 23:04
King of typos
Loyal Member
Joined:
Posts:
June 2002
5,265
On July 2, 2015 at 19:09, RandyWalters said...
Another big problem with these controlled receptacles is office workers plugging their PCs into the controlled portion. We're selling a lot of them on Title 24 TI projects.

[Link: leviton.com]§ion=65370&minisite=10251

Then we're being force to making the grounding plug, prong, whatever you want to call it. In the up most position. It's not specified in the NEC as to the orientation of the receptacle at all, with out this label. However, with that imprinted label, I bet there will be.

So does this mean that we can no longer install receptacles on the floor or along the wall in landscape? It HAS to be on the wall in the portrait position now and with the grounding plug in the up most position?

Click here and then images... Then scroll down to the bottom. Rather interesting pictures huh? [Link: google.com]

KOT
Post 11 made on Friday July 3, 2015 at 09:40
Archibald "Harry" Tuttle
Advanced Member
Joined:
Posts:
May 2009
959
Who has 24,001 things to say?
I came into this game for the action, the excitement. Go anywhere, travel light, get in, get out, wherever there's AV trouble, a man alone.
OP | Post 12 made on Friday July 3, 2015 at 13:21
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,076
On July 2, 2015 at 23:04, King of typos said...
Click here and then images... Then scroll down to the bottom. Rather interesting pictures huh? [Link: google.com]

KOT

I get it. Sockets. Right.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 13 made on Friday July 3, 2015 at 17:53
Hi-FiGuy
Super Member
Joined:
Posts:
January 2004
2,826
It has become quit interesting using the restrooms in these modern and updated buildings in Downtown LA, when you are in the stall in sit-down mode and the freekin lights shut off and there is no windows. ALWAYS bring your phone with flashlight app installed.
Post 14 made on Friday July 3, 2015 at 18:28
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,192
On July 2, 2015 at 23:04, King of typos said...
Then we're being force to making the grounding plug, prong, whatever you want to call it. In the up most position. It's not specified in the NEC as to the orientation of the receptacle at all, with out this label. However, with that imprinted label, I bet there will be.

So does this mean that we can no longer install receptacles on the floor or along the wall in landscape? It HAS to be on the wall in the portrait position now and with the grounding plug in the up most position?

Click here and then images... Then scroll down to the bottom. Rather interesting pictures huh? [Link: google.com]

KOT

IIRC, that's common in commercial/industrial- Apparently, it reduces the chance of a direct short if something made from metal should fall on the plug.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 15 made on Saturday July 4, 2015 at 10:03
King of typos
Loyal Member
Joined:
Posts:
June 2002
5,265
On July 3, 2015 at 18:28, highfigh said...
IIRC, that's common in commercial/industrial- Apparently, it reduces the chance of a direct short if something made from metal should fall on the plug.

That is correct. As most commercial applications, the cover plate was made of metal. So after several hundred actuations of a plug going in and out. The screw for the cover plate would loosen and the plate would fall. If the grounding plug was on the bottom half, there was the chance of the metal plate shorting the ungrounded and grounded plugs together.

So someone thought about putting the grounding plug on the top part. Because we all know that business people are stupid with it comes to using a plug in an outlet. "Oh, the this metal thingy isn't attached any more. But I still need to plug my computer in." ZAP!!!

I am actually shocked, pun intended, that it's not in the NEC to have the grounding prong in the upper position. But like I said in my other posting, this new labeling appear to make us do just that. As so it can be read from an upright position.

KOT
Page 1 of 2


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.