I'm overseas waiting for some equipment that is weeks late and I've finally run out of things to do, so I'm looking up stuff. I found my -- probably our -- concept of ground loops is not quite right. This is from a T&B White Paper on grounding and bonding a STP system,
[Link: ampnetconnect.com].
I have to start by pointing out what they say here about grounding and bonding. Grounding is connection to the actual earth ground, or to the structural steel of a building. Bonding is connecting together the chassis and shields of equipment so that there is a low resistance path to the ground. That is, all of our cable shields, RCA plugs, F connectors, etc do not ground the cable but rather bond it to the bonding system that is connected to the ground. So when they say "bonding" below, they mean what we usually mean when we say "grounding."
TESTING FOR GROUND LOOPS AND PROPER GROUNDING & BONDING
In an electrical system, a ground loop refers to an unwanted current that flows in a conductor connecting two points that are at different voltages.
Guess what: it's not a ground loop if it is only a ground path that you can define as a loop because of what is connected to what; it is only a ground loop if there is a problem! A ground loop is not a wiring layout, it is the name given to a
current under certain circumstances!
Another misconception surrounding shielded cable is that ground loops will always be a problem.
Now that we know that it's only called a ground loop if there is a problem, that totally makes sense. [The article did not previously list a misconception with shielded cable.]
However, ground loops that affect network performance can only occur when a system has more than one path to ground and the voltage difference between the two points are more than 1 Volt.
Now that's sloppy writing and perhaps sloppy thinking. It should be "the voltage difference... IS more than 1 Volt."
This was illustrated at the Middle Atlantic grounding seminar of a couple years ago, but they used ground current as the indicator. You can measure milliamps of current from location to location much more easily than you can measure small voltages between loactions.
If the components of a telecommunications system are properly bonded, and the system is effectively bonded to the building's grounding electrode system, there is virtually no condition where a ground loop is possible.
Again, confirmed at that seminar. They showed cables that had ground resistance, that is, poor bonding, created hum bars in a TV while cables with very low resistance did not. The trick, too, was that the noisy cable was expensive while the quiet one was a piece of crap.
The only way to ensure proper grounding and bonding for either a UTP or STP system is to test upon completion.
I love this one. I once moved a ridiculously complicated set of two A/V systems for a guy. He was in an apartment where they were on opposite sides of a wall. He them moved to where they were thirty feet apart. Halfway through the interconnection, I gave him TV to watch, and it had horrible hum bars. He wanted me to fix it. I demurred, offering to fix it when all the wiring was done. When all the wiring was done, with no special effort on my part, the hum bars were gone, too. The whole thing had to be in to be tested.
Ground potential difference should not exceed 1 Volt.
This is really hard to test. AC current on the shield is good enough, and 10 mA is usually a problem. The thing is, you'll need to spend $250 to get a current meter that can read that small of a current because you have to use a clip-on type.
Testing for ground potential difference can be done using an Earth Ground Resistance Tester with the entire building in operation. In other words, nothing needs to be shut down to test the grounding and bonding. Earth Ground Resistance Testers can be purchased pretty much anywhere telecommunications testers are sold.
I was shocked --
shocked, I say! -- to find out that if an actual loop circuit of ground wiring has no problem, then it is not a ground loop. It makes sense, though -- we only notice a loop in the ground when we see a problem.