We are bidding on a commercial project whereby everything needs to be run through conduit. The client is concerned about critters chewing into the wire. There are multiple runs of AV, Data / Com, Security, Control and Cameras. The average distance for each device to the head end is approximately 200 feet. All of the cabling needs to be run off of scissor lifts because of ceiling height. The electrical contractor will be installing 1" EMT conduit for us. Is there a formula that anyone uses to caculate time requirements needed to prewire a job like this?
I have posted a dupicate of this at IP if anyone wants to comment privately. Thanks!
|
|
|
| Post 2 made on Saturday August 11, 2012 at 08:01 |
highfigh Loyal Member |
Joined: Posts: | September 2004 8,192 |
|
|
On August 11, 2012 at 07:20, Gman said...
We are bidding on a commercial project whereby everything needs to be run through conduit. The client is concerned about critters chewing into the wire. There are multiple runs of AV, Data / Com, Security, Control and Cameras. The average distance for each device to the head end is approximately 200 feet. All of the cabling needs to be run off of scissor lifts because of ceiling height. The electrical contractor will be installing 1" EMT conduit for us. Is there a formula that anyone uses to calculate time requirements needed to prewire a job like this?
I have posted a dupicate of this at IP if anyone wants to comment privately. Thanks! How many cables need to run through each conduit? Don't expect to be able to fill them and still pull the cables, especially through bends. Any HDMI cables, or just Cat5e with extenders at the ends? If you have a scrap of 1" conduit, use a bundle of scrap wire that's the same as what you need to run, to test the fit. I don't think I would use anything smaller than 1-1/2", but it's impossible to say without knowing how many cables will be in it.
|
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder." |
|
| Post 3 made on Saturday August 11, 2012 at 08:04 |
ichbinbose Select Member |
Joined: Posts: | August 2011 1,822 |
|
|
were working on a large commercail space right now and are using 2" emt for all pull locations. 1" will fill up quick
|
|
| Post 4 made on Saturday August 11, 2012 at 08:06 |
Mario Loyal Member |
Joined: Posts: | November 2006 5,680 |
|
|
1" may not be enough for all but few cables. As far as pulling them, if you have a pull-string in the conduit, than it goes faster than pulling thru open stick construction. I would have sparky run and bill for all the conduits, and just bill my regular per pull cable rates.
|
|
|
| Post 5 made on Saturday August 11, 2012 at 08:58 |
drewski300 Super Member |
Joined: Posts: | January 2007 3,848 |
|
|
Do as others have suggested, run 2"!!
I can't remember what size it was but it was either 3/4" PVC or 1" PVC and we were only able to pull 5 cat5e's and 2 coax in each conduit (I believe it was a 1"). If there is more than 360° in bends you are really going to struggle especailly because low voltage wires do not have a jacket good for pulling through conduits. You'll have to determine the number of wires needed and pull all of them at the same time. I think a rule of thumb would not fill the conduit with more than 75% of wire otherwise you won't make it past the first bend.
There is a calculation for electrical conductors but I don't know if there is for cat5.
|
"Just when I thought you couldn't possibly be any dumber, you go and do something like this... and totally redeem yourself!" |
|
| Post 6 made on Saturday August 11, 2012 at 09:14 |
pilgram Loyal Member |
Joined: Posts: | November 2004 5,684 |
|
|
Here's a chart for cat cable [Link: cabling-design.com]Unless your really stuffing it full,it usually takes me about the same amount of time as it does running cable without conduit.
|
Every day is a good day.......some are just better than others!
Proud to say that my property is protected by a high speed wireless device! |
|
| Post 7 made on Saturday August 11, 2012 at 10:07 |
SB Smarthomes Super Member |
Joined: Posts: | July 2007 2,634 |
|
|
200' is a long pull through 1" conduit unless it's a very straight run and you only have 2-3 cat5 wires. If there are more than three 90° sweeps, you might consider requesting a junction box in the middle to help with the pulls. 2" EMT is going to cost a fortune if you have more than a few runs and will also be logistically difficult to install around other mechanicals. I really don't think 2" is necessary for category & coax cable and if the runs are that long, you won't be pulling HDMI through them anyway. Can the low volt be run through plastic flex like Carlon resi-gard, or does it have to be EMT? Here's a few photos from a job I did last summer with everything in conduit. It's all 1" EMT with 10x10 junction boxes placed in stategic locations to help with the pulls.    Most of these runs were less than 100ft from the junction boxes to head end or wall plate so pulling was a breeze.
|
www.sbsmarthomes.comSanta Barbara Smarthomes |
|
| Post 8 made on Saturday August 11, 2012 at 13:23 |
77W Advanced Member |
Joined: Posts: | June 2012 971 |
|
|
I'd rather do conduit pulls like what Paul posted than do open stick wiring. A well laid out conduit design will make your life SO much easier. The junction box and sticking to smaller and more accessible/easier to work with 1" EMT will work really well.
If you have to do all the work on scissor lifts then this should be pretty quick with a smartly designed conduit system. Plan your junctions and runs and then pull away. The only time we've ever had trouble with conduit is if we try to jam too much into it (turns into a lube fest) or if someone doesn't read our spec right and puts in 3/4" (electrician usual) instead of the 1 or 1-1/4" we as k for.
PS thanks for the "official" conduit chart. I'd drawn up my own using loose end cuts of wire and a trip to HD.
|
|
| OP | Post 9 made on Saturday August 11, 2012 at 13:51 |
Gman Select Member |
Joined: Posts: | February 2009 2,211 |
|
|
Thanks for all of the replies.
The project is a horse arena and emt has to be used instead of pvc flex conduit due to potential problems with mice etc. The equipment list so far is 32 cameras, 50 zones of security, 10 audio zones, 10 data drops, 10 telco drops and 2 or 3 video zones. Telco and security will be head ended in a control room and the AV, data and cameras in an office area. As suggested, junction boxes will be necessary because the runs will be coming from everywhere in the building.
|
|
|
| Post 10 made on Saturday August 11, 2012 at 18:42 |
Innovative A/V Select Member |
Joined: Posts: | December 2007 1,966 |
|
|
On August 11, 2012 at 08:04, ichbinbose said...
were working on a large commercail space right now and are using 2" emt for all pull locations. 1" will fill up quick +1 on at least 2", but we usually run 2 1/2"
|
www.goinnovativeaudiovisual.comCedia certified installer ISF Certified 'It's not how many times you get knocked down but it's how many times you get back up and go forward" |
|
| Post 11 made on Saturday August 11, 2012 at 19:44 |
SB Smarthomes Super Member |
Joined: Posts: | July 2007 2,634 |
|
|
On August 11, 2012 at 08:04, ichbinbose said...
were working on a large commercail space right now and are using 2" emt for all pull locations. 1" will fill up quick On August 11, 2012 at 18:42, Innovative A/V said...
+1 on at least 2", but we usually run 2 1/2" Are you guys really running 2 - 2.5" EMT to all the location, or just for the main trunks to pull boxes? These jobs really need to be thought out well and designed properly. The main runs will need large conduit, but drops down to wall plates, speakers, alarm contacts, etc. may only need to be 1/2" or 3/4".
|
www.sbsmarthomes.comSanta Barbara Smarthomes |
|
| Post 12 made on Saturday August 11, 2012 at 20:49 |
Innovative A/V Select Member |
Joined: Posts: | December 2007 1,966 |
|
|
On August 11, 2012 at 19:44, SB Smarthomes said...
|
Are you guys really running 2 - 2.5" EMT to all the location, or just for the main trunks to pull boxes? These jobs really need to be thought out well and designed properly. The main runs will need large conduit, but drops down to wall plates, speakers, alarm contacts, etc. may only need to be 1/2" or 3/4". sorry paul.... usually multiple 1" depending what I need to the rooms, 2 1/2 main trunks to pull boxes....then drop down....I like the 2 1/2 to drop into panduit at the rack...
|
www.goinnovativeaudiovisual.comCedia certified installer ISF Certified 'It's not how many times you get knocked down but it's how many times you get back up and go forward" |
|
 |
Before you can reply to a message... |
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now. |
Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.
|
|