OP | Post 16 made on Friday December 23, 2011 at 19:05
brucewayne
Advanced Member
Joined:
Posts:
March 2006
895
Trunk slammer that was the plan to have a 350 cfm with 8 inch ducting pulling the hot air from the closet and bring it down to one side of the crawl space and a duct feeding from the other side of the crawl space bringing air in . I even had planned the inlet and out far apart to make sure the hot air wasn't going back to the closet . The issue with my plan was gc didn't want the 8 inch duct running down wall in mech room next door. it would have blocked the furnace shut off switch .
brucewayne
Post 17 made on Saturday June 2, 2012 at 15:31
Tom Ciaramitaro
Loyal Member
Joined:
Posts:
May 2002
7,851
Reviving an older thread with a few questions:

1. I've used a couple Cool Cube 80cfm units for closets. Basically one amp plus a cable box - other components are cool (DVD, CD, etc). Units run most of the time. I'd think you'd want enough capacity to have the thing off at least half of the time. Is 80cfm even worth messing with?

2. Bathroom fan idea - requires we be electricians for a half hour; negative in some jurisdictions. Line voltage thermostats equal simplicity, but the ones I see stop at around 85-90 degrees, a little on the cool side, considering you might want it to turn off a little higher than that.

3. Again, bathroom fan would have to be a quiet but still 150cfm or more unit I would think. Are the above mentioned fans both powerful enough and quiet enough?
There is no truth anymore. Only assertions. The internet world has no interest in truth, only vindication for preconceived assumptions.
Post 18 made on Saturday June 2, 2012 at 17:25
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,076
On June 2, 2012 at 15:31, Tom Ciaramitaro said...
Reviving an older thread with a few questions:

...thermostats... see stop at around 85-90 degrees, a little on the cool side, considering you might want it to turn off a little higher than that.

Seems to me that if the thermostat were lower in the rack or otherwise placed away from the heat, the effective temperature cutoff for the entire rack would be raised. Good old experimentation, often one of the first steps of "custom."

Fred Harding turned me on (above 90 degrees....) to a thermostat, enclosed in a box, with a power outlet. It works great. It's meant to be mounted on a duct and sample the air inside the duct. Strangely, when used out in the open, you pretend you want it to heat rather than cool, and set the temperature to the warmer temperature for a cooler environment. That is, it sets up backwards in free air.

It's a bit more than $30, but you'll have to contact Fred for the brand and model.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 19 made on Saturday June 2, 2012 at 20:16
Tom Ciaramitaro
Loyal Member
Joined:
Posts:
May 2002
7,851
[Link: suncourt.com]

It looks viable. Probably need an outlet in the attic if you wanted to use this with a bathroom fan. Romex connected like you do for a flat panel when it's powered by your surge device.

[Link: snapav.com]

How about 80cfm for a closet with a Comcast box and AVR?
There is no truth anymore. Only assertions. The internet world has no interest in truth, only vindication for preconceived assumptions.
Post 20 made on Saturday June 2, 2012 at 20:58
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,192
On December 15, 2011 at 18:56, brucewayne said...
What does everybody do for cooling . Clients have been asking us to put the rack in closets . In the clients defense some of the recent jobs like a pool house there is no other place for the rack. So we will have a 40 space rack with 3 cable boxes , receiver , camera DVr . Multi room ampm etc in a closet this stuffnis going to heat up the closet quickly. When I have tried fans that are around 100 cfm and it didn't cool the closet . I would open the door and it would be around 90 degrees. I started using 10 inch fans and it worked . I had just tried to integrate a 350 cfm fan . But gc and others want a 150 cfm ceiling fan. They said the fan I picked was to big . I know my fan will cool the closet but not sure if there fan will . But if it's not enough cooling 6 months From now won't I be the one blamed or my company eat the cost of the fried gear ?

Where have you been putting the fans if they don't work? Did you remove the hot air from the closet, or just blow it around inside the closet? The last way doesn't work, period.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 21 made on Saturday June 2, 2012 at 21:12
P2P
Long Time Member
Joined:
Posts:
April 2012
278
Just read through this thread quickly but I'm not getting something. It sounds like most are just including some arbitrary fans to exhaust some arbitrary heat. Are you guys really not taking the time to figure out how much heat your equipment is producing and equating that to how much air you need to move and exhaust in a cabinet, rack, or equipment room?

As a couple of folks have mentioned (and linked to), there are a lot of white papers readily available that teach you how to do this properly. It isn't hard and involves some pretty basic math skills.

We long ago started including power and heat loads as part of our equipment database and automated the whole process. A normal output of our engineering process is complete power requirements provided to sparky so we know we have enough power, and full heat loads calculated. If it is a smaller project, a small rack in a cabinet, etc. we handle the cooling ourselves. On larger projects, we supply the heat loads to the MEP engineer and / or HVAC company and coordinate for proper temperature, ventilation, and cooling of the larger equipment rooms.

Whatever you do, don't just guess. Figure it out!
Post 22 made on Saturday June 2, 2012 at 21:21
longshot16
Super Member
Joined:
Posts:
November 2009
3,439
Are you using specs or measuring the units in house?
The Unicorn Whisperer
Post 23 made on Saturday June 2, 2012 at 21:30
P2P
Long Time Member
Joined:
Posts:
April 2012
278
On June 2, 2012 at 21:21, longshot16 said...
Are you using specs or measuring the units in house?

Specs
Post 24 made on Saturday June 2, 2012 at 23:06
bcf1963
Super Member
Joined:
Posts:
September 2004
2,767
On December 18, 2011 at 22:21, brucewayne said...
update after it was giving to the hvac company to install the fan . I get forwarded an email that said there are using an 80 cfm bathroom fan and hvac company is not responible for av equipment. this is like 22% percent the cooling i asked for. I am going along with it but I am pushing for someone the make it clear to client the we are being told this is the only option. there are two pieces in the rack that i know are sensitive to heat and there around 3k each because there fore the most part there just computers . how do we make it clear that we asked for 4 times the cooling to be safe to make sure the gear was safe and couldnt get it and should not have to pay for new gear if heat messes up the gear and get paid for install time of replacing the gear

This seems like it is easy to me. Has the HVAC company asked for a list of the power consumption of all the equipment? Have they asked what the allowed temperature rise is? Have they given you an analysis that shows what the temp rise is, for the equipment in the closet? If they have not done an analysis, then you simply send them and the homeowner a letter, detailing that you will not warrant the equipment in the rack, as the HVAC company is dictating a solution, without having done an analysis. You state that manufacturer's warranty may still be valid, but you will charge to remove and ship, and a charge will be present if they wish "loaner" gear. Stipulate that if equipment is shutting off due to overheating (without damaging itself), that you will not be able to fix that without the HVAC contractor fixing the heat situation in the closet. Refuse to install the rack and equipment until the homeowner signs off, taking responsibility, or until you get an analysis you feel is complete. I guarantee upon getting such a letter, the homeowner will be all over the HVAC contractor. The HVAC contractor will likely not be very happy with you... but then again they've been refusing to work with you anyway... so how can this be worse?
OP | Post 25 made on Monday June 4, 2012 at 21:29
brucewayne
Advanced Member
Joined:
Posts:
March 2006
895
P2p ,
I did all of that when I started this thread . I spoke with the hvac company they agreed I had the right stuff . But to cool the room the closet I was affecting the hvac system in the whole house . There are so many other factors to move over 200 cfm of air you need a 6 inch ducts or bigger one .two you have to filter the air for dust . Three The air you draw in has to be from inside the living space so there isn't to much moisture . Four you can not have the inlet and outlet on same wall . have found that it is next to impossible to do all of these things builders just say they can't . I think you can only try your best and hope for the best
brucewayne
Post 26 made on Friday August 17, 2012 at 02:17
FrogAV
Long Time Member
Joined:
Posts:
March 2012
419
On December 18, 2011 at 23:49, Trunk-Slammer -Supreme said...
Fantech PB190

Noise will not be an issue.

Have done this in a house with a crawl space under the house.

Equipment closet is NOT vented to the room.

Simple recirculating system where you are pulling cool air in from under the house, and dumping hot air back under the house.

If no "crawl" I would then draw cool air in from the room and dump the hot air out to a much larger interior space. Again, a simple recirculation system.

Works very well.

Sorry, I'm feeling dense here. Based on the diagram on this page: [Link: residential.fantech.net] I'm having trouble visualizing the placement of the three components of the Fantech when they are both drawing and returning to the crawlspace. All I can see in my head is a closed loop that goes THROUGH the closet without affecting the air in it. Can you clarify for me?

Thanks.
Ryan Posner
Frog AV
OP | Post 27 made on Friday August 17, 2012 at 19:00
brucewayne
Advanced Member
Joined:
Posts:
March 2006
895
We ended up with a 130 cfm bathroom fan and it has done the job so far
brucewayne
Post 28 made on Sunday August 19, 2012 at 18:17
Mario
Loyal Member
Joined:
Posts:
November 2006
5,680
Anyone ever found or used attic mounted closed loop A/C system?
I still need to do full BTU calcs, but I have a small closet ~6'x5' with couple of DA amps, 2 DVRs, etc. that I need to cool.
Rather than using a vent to push hot air to another room, and use living space as makeup air (which I can if I had to), I'd like to see if others have actual experience using 1 room A/C units.
Size would depend on load calcs, but figured I can look at specific model/size once I have the numbers.

BTW, this is for my own house, if that matters.
Post 29 made on Monday August 20, 2012 at 06:01
Neurorad
Super Member
Joined:
Posts:
September 2007
3,011
Deleted, old thread.
TB A+ Partner
Believe nothing, no matter where you read it, or who said it, no matter if I have said it, unless it agrees with your own reason and your own common sense. -Buddha
Post 30 made on Tuesday May 14, 2013 at 00:42
77W
Advanced Member
Joined:
Posts:
June 2012
971
On June 2, 2012 at 21:12, P2P said...
Just read through this thread quickly but I'm not getting something. It sounds like most are just including some arbitrary fans to exhaust some arbitrary heat. Are you guys really not taking the time to figure out how much heat your equipment is producing and equating that to how much air you need to move and exhaust in a cabinet, rack, or equipment room?

As a couple of folks have mentioned (and linked to), there are a lot of white papers readily available that teach you how to do this properly. It isn't hard and involves some pretty basic math skills.

We long ago started including power and heat loads as part of our equipment database and automated the whole process. A normal output of our engineering process is complete power requirements provided to sparky so we know we have enough power, and full heat loads calculated. If it is a smaller project, a small rack in a cabinet, etc. we handle the cooling ourselves. On larger projects, we supply the heat loads to the MEP engineer and / or HVAC company and coordinate for proper temperature, ventilation, and cooling of the larger equipment rooms.

Whatever you do, don't just guess. Figure it out!

OK so the math is pretty simple.

(BTU per Hour) / (1.085 X DELTA T) = CFM

But how do you get the heat loss measurements? An amplifier rated for 1100w on the back isn't going to draw anywhere close to that.....and calculating it out, it yields a stupid high BTU number all on its own.

Total amperage x 400 = total BTU/Hr. @117v

I mean, I could guess. But short of powering up the units and driving some speakers and whatnot, how do you actually know?
Page 2 of 3


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.