Control4 Thermostat Remote Sensor Fluctuating with Common
This thread has 14 replies. Displaying all posts.
Post 1 made on Thursday December 8, 2011 at 19:24
teryglenn1
Long Time Member
Joined:
Posts:
September 2009
16
We are using 2.1.1, all thermostats are in basement, our HVAC installer is using Taco HVAC controls. The issue is when we hook up common from his system our remote temperature sensor starts fluctuating 5-6 degrees randomly. When we are on battery alone it works fine. We took a voltage reading and his system is giving us more than 24v, something like 28v we are getting. Has anyone encounter a situation like this before? Any help would be awesome.
Post 2 made on Thursday December 8, 2011 at 20:31
AnthonyZ
Select Member
Joined:
Posts:
September 2005
1,987
The 24VAC transformers are only NOMINALLY 24 volts. It is not, at all unusual to see HVAC transformers measuring much higher than 24. However, I typically see them in the 26 to 27 range. Just sayin'
"Just when I thought that I was out they pull me back in"
Post 3 made on Thursday December 8, 2011 at 23:05
scottedge267
Advanced Member
Joined:
Posts:
February 2003
790
I'd love to know the answer to this. Had a similar situation and had to do a little science project. if there are not good solutions I'll let you know but really it might not be a good solution for a client 
Post 4 made on Friday December 9, 2011 at 02:38
Audiophiliac
Super Member
Joined:
Posts:
August 2006
3,294
Can you temporarily connect your own 24V power supply and try to pinpoint the problem to a specific device/system?
"When I eat, it is the food that is scared." - Ron Swanson
Post 5 made on Friday December 9, 2011 at 02:43
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,076
You say battery, so that's DC. I sort of expect usual thermostats to run on AC. Of course, control types probably run on DC. I'm just saying, I suppose, that I don't know a lot of details about this.

That said, if it's DC, how much ripple is there? If the supply can output, say, 200 mA, when no current is drawn, the supply will be at a high DC voltage with zero ripple. When you draw near the total available amperage, its voltage will drop and ripple will appear. That means that this function might be affected by how much current is drawn for other functions.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 6 made on Friday December 16, 2011 at 04:55
scottedge267
Advanced Member
Joined:
Posts:
February 2003
790
 in my case the problem was the 24V AC coming from the controller. I was getting common from a radiant heat controller.

Ernie the thermostats take AC when powering them not by battery. you can connect a common wire from your HVAC/radiant heat and power the thermostats so they do not drain battery.

I had to connect a relay in between and power the thermostat from another power supply. I am guessing I could probably regulate the power from the controller some how. It must be fluctuating creating the jump in temperature from the remote sensor.  I really would love to know a solution to this
Post 7 made on Friday December 16, 2011 at 11:05
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,076
I can't yet understand the wiring. For instance, "common" usually is one wire, with the other considered "hot," but you've got 24 VAC and also a common. What does common mean here?

It makes total sense that you need a relay to switch between battery and AC. Otherwise the AC and the battery supplies would be damaged.

The experimenter could take the 24 volts AC, put it through a diode bridge to rectify it to pulsating DC, filter it, then put it through a regulator and adjust its voltage so that it provides a slight charge to the battery at all times, then leave the AC connected this way to the battery. No switching over at all. The big IF here is IF the battery is not degraded by a trickle charge. bcf1963 should have some GREAT input here.

A problem with doing that is the time involved in engineering a one-time solution that will undoubtedly void the warranty on some or all of the interconnected items. This fact separates the DIYer from the professional. The DIYer can dick with it all he wants and will take responsibility for it, though never silently, when the heater quits during a snowstorm. A pro has to install something available, with the backing of warranties, that he can walk away from knowing that it will continue to work. The pro might customize, but not usually at the level of power supply construction, more often at the level of appearance or clever combination of available goods.

Which brings me to... if the DC voltage is 24 volts, try to locate a product that's a 24 volt DC supply with its own built-in charging supply. An off-the-shelf item that supplies the proper DC voltage (at the proper current) might not void any warranties and give you DC from a battery that doesn't drain the battery when 120 VAC is available.

A caution about current, though -- be sure you understand the load. I once blew several relays in a lighting system because they were meant to be pulsed by an intentionally crappy 16 volt DC supply that dropped to 10 volts after a quarter second and could only power one relay at a time. It was supposed to work that way. I replaced it with a beefy supply that held steady at 16 volts, and holding down a lighting button would blow a relay.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 8 made on Friday December 16, 2011 at 11:28
BlackWire Designs
Senior Member
Joined:
Posts:
September 2006
1,401
are you using cat5 for the temp sensor wire?
BlackWire Designs
Post 9 made on Friday December 16, 2011 at 11:44
scottedge267
Advanced Member
Joined:
Posts:
February 2003
790
On December 16, 2011 at 11:28, BlackWire Designs said...
are you using cat5 for the temp sensor wire?

in my instance yes.

Post 10 made on Friday December 16, 2011 at 13:38
BlackWire Designs
Senior Member
Joined:
Posts:
September 2006
1,401
that is your problem.. It will NOT work properly on cat5. dont ask me why but it wont.

You must run solid core wire.
BlackWire Designs
Post 11 made on Friday December 16, 2011 at 13:40
BlackWire Designs
Senior Member
Joined:
Posts:
September 2006
1,401
pick up a spool of hvac wire and retro it in.. i promise it wont stop fluctuating until you do
BlackWire Designs
Post 12 made on Saturday December 17, 2011 at 00:38
scottedge267
Advanced Member
Joined:
Posts:
February 2003
790
On December 16, 2011 at 13:40, BlackWire Designs said...
pick up a spool of hvac wire and retro it in.. i promise it wont stop fluctuating until you do

to be more precise I have it running on both and it fluctuates on both. I forgot the majority of them are running on solid hvac wire. The install is a year old at this point and working by powering them with their own AC power supplies with a HAI 29A00-1. I would love to get rid of that science project though. reliability going forward is something I am concerned about. 
Post 13 made on Friday December 30, 2011 at 01:17
scottedge267
Advanced Member
Joined:
Posts:
February 2003
790
On December 16, 2011 at 11:05, Ernie Gilman said...

The experimenter could take the 24 volts AC, put it through a diode bridge to rectify it to pulsating DC, filter it, then put it through a regulator and adjust its voltage so that it provides a slight charge to the battery at all times, then leave the AC connected this way to the battery. No switching over at all. The big IF here is IF the battery is not degraded by a trickle charge. bcf1963 should have some GREAT input here.

this is a solution I would be looking to do. You can power the thermostats with 24 volts from the thermostat wire by connecting the common wire from your heating/ cooling source. In my instance its a radiant heating controller. That controller is not putting out a consistant 24V. I would not be using the battery at all. When the thermostat detects the 24V it powers off that and not the battery. Would this work?
Post 14 made on Friday December 30, 2011 at 05:06
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,076
On December 30, 2011 at 01:17, scottedge267 said...
this is a solution I would be looking to do.

I find that to be an odd comment as the rest of what you propose is not that at all.

You can power the thermostats with 24 volts from the thermostat wire by connecting the common wire from your heating/ cooling source.

Two problems I've had with this nomenclature from the beginning are that
~~"common" is very often used to mean the ground or negative connection
~~you can't just connect one wire, so does "common" mean two wires of some sort? I mean, is "common" the name you give to the two wires with 24 VAC on them?

In my instance its a radiant heating controller. That controller is not putting out a consistant 24V. I would not be using the battery at all. When the thermostat detects the 24V it powers off that and not the battery. Would this work?

More details, please. How do you switch from "that" to battery? How do you keep the battery charged?

The idea I proposed was to use the 24 volts to keep the battery charged, then run everything off the battery. Varying 24ish volts won't matter if the charging circuit is done correctly (bcf1963 could help, I might be able to help). You'd need a buck converter to make a voltage higher than 24 volts to charge the battery.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 15 made on Friday December 30, 2011 at 22:41
scottedge267
Advanced Member
Joined:
Posts:
February 2003
790
On December 30, 2011 at 05:06, Ernie Gilman said...
I find that to be an odd comment as the rest of what you propose is not that at all.

well I would like to take parts of your solution.



Two problems I've had with this nomenclature from the beginning are that
~~"common" is very often used to mean the ground or negative connection
~~you can't just connect one wire, so does "common" mean two wires of some sort? I mean, is "common" the name you give to the two wires with 24 VAC on them?

More details, please. How do you switch from "that" to battery? How do you keep the battery charged?

The idea I proposed was to use the 24 volts to keep the battery charged, then run everything off the battery. Varying 24ish volts won't matter if the charging circuit is done correctly (bcf1963 could help, I might be able to help). You'd need a buck converter to make a voltage higher than 24 volts to charge the battery.

in this instance common is a ground. by connecting the common wire to any thermostat that will accept it you can power the thermostat off the 24v coming to the thermostat over the heating and cooling wires. When a thermostat detects this voltage it does not use the battery at all. the problem in this scenario is that the common wire(ground) and remote temperature sensor ground on the control 4 thermostat share a connection. So both wires are connected to the same terminal. The fluctating 24v from the heat controller now affects the remote temperature sensor so it does not read a correct temperature. I probably will just leave well enough alone. 



Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.