Your Universal Remote Control Center
RemoteCentral.com
Custom Installers' Lounge Forum - View Post
Previous section Next section Previous page Next page Up level
Up level
The following page was printed from RemoteCentral.com:

Login:
Pass:
 
 

Page 1 of 2
Topic:
Can I run a 120 VAC LED light off of 240 volts?
This thread has 25 replies. Displaying posts 1 through 15.
Post 1 made on Friday December 10, 2010 at 21:06
Ernie Bornn-Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,076
I was hoping someone could apply what you know to what I think I know here:

I'm preparing a power, uh, box, that will convert 208 volt three phase power to 240 volt three phase power so I can run some JBL Synthesis amps to be used overseas. I've got the step-up transformers needed to do that, and I'd like to have an idiot light to tell me that power is present. One light for each phase, that is.

At Home Depot they have 0.25 watt 120VAC LED lamps intended to replace present incandescent night light bulbs. Do you see any reason why these would not work by simply placing a resistor in series with them?

I suppose, which itself is an issue, that these LED lamps have a pretty good power factor, meaning that a resistor would come close to cutting the power in half. I intend to use the stated wattage and a goal voltage of 110 volts to determine the resistor value, and to size the resistor at one watt.

Do you foresee any problems with this?

Thanks!
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 2 made on Friday December 10, 2010 at 23:01
edizzle
Loyal Member
Joined:
Posts:
March 2005
5,916
what you talking bout willis? sounds dangerous? i like it. :)

im no electrician but you should be able to put one bulb between neutral and hot1 (120) the other bulb between neutral and hot2 (120). this would let you know each side of the 240 is operating.
I love supporting product that supports me!
Post 3 made on Friday December 10, 2010 at 23:29
Gizmologist09
Advanced Member
Joined:
Posts:
May 2009
762
Question: Where are you getting 208 3-phase power? The amps do not use 3 phase. They are 120volt from what I found.

208 is the wild leg to neutral in a typ. US 3 phase system.
OP | Post 4 made on Saturday December 11, 2010 at 01:13
Ernie Bornn-Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,076
Our test setup has 208 3 phase. It's what's for dinner. I mean, it's what's on the wall here in Southern California.

I've got amps designed for use overseas. They want to see 230 volts single phase. They've got dumb brute force power supplies, and 208 VAC is too low.

If you use one phase of a three phase supply, then you have single phase. I didn't mean to say that the amps use three phase power, but that we have three phases, and we will use each as a single phase, balancing draw as much as possible.

Believe it or not, the projector, which draws 23 amps at 208 VAC, can run on 200 to 250 volts. The low power units, those with small switching power supplies, can run on just about anything, so they are not an issue.

I'm using step-up transformers to convert 208 3 phase to 240 3 phase, using 2 of those phases for the power amps and the other phase for the projector. So, yeah, it will be three phase in and three phase out. This mirrors the power available to us in Saudi, except they use a delta and we have Y. We're using EquiTech transformers anyway, so that will be dealt with.




Anybody have an answer about the LED?
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 5 made on Saturday December 11, 2010 at 02:20
JimInNJ
Long Time Member
Joined:
Posts:
February 2010
17
On December 10, 2010 at 23:29, Gizmologist09 said...
Question: Where are you getting 208 3-phase power? The amps do not use 3 phase. They are 120volt from what I found.

208 is the wild leg to neutral in a typ. US 3 phase system.

Yes and no. The 208v "wild" leg is generally found in US commercial installations that use a 240v "Delta" configuration. In my experience, this is much less common than the "wye" configuration, 208v 3 phase.

Check out this webpage: [Link: programmablepower.org]

As to the original question, how about putting 2 of these LED bulbs in series? No muss, no fuss, nothing that would make an inspector look twice.

Good luck!

JIM BATES
Post 6 made on Saturday December 11, 2010 at 08:49
Ozzie Glenn
Long Time Member
Joined:
Posts:
September 2008
395
Put two globes in series and use them as a voltage divider. 120V each.
Wireless speakers? Of course Sir. Choose the colour and size you like. As you don't seem to think sound quality is important, I will not plug them in.
Post 7 made on Saturday December 11, 2010 at 10:06
Innovative A/V
Select Member
Joined:
Posts:
December 2007
1,966
the 208 and 277vac are generally used for lighting loads in commercial buildings
www.goinnovativeaudiovisual.com
Cedia certified installer
ISF Certified 'It's not how many times you get knocked down but it's how many times you get back up and go forward"
Post 8 made on Saturday December 11, 2010 at 11:16
rogerdata
Long Time Member
Joined:
Posts:
September 2010
13
I would also be careful to look at the incomming frequency requirement.
Most european systems use 50 Hz and we use 60 Hz. you could cause considerable damage to these units if the frequency is ignored!
Pronto TSU9200,TSU9400
Post 9 made on Saturday December 11, 2010 at 11:27
Gizmologist09
Advanced Member
Joined:
Posts:
May 2009
762
Found a solution for you.

[Link: marcspages.co.uk]
Post 10 made on Saturday December 11, 2010 at 12:36
bcf1963
Super Member
Joined:
Posts:
September 2004
2,767
Ernie,

You certainly should have no problem adding a resistor.

If the power factor were not good, I would cause a problem. The only issue that could cause the power factor to be much off, would be that the forward voltage drop of a white LED is about 3.6V. So as the line voltage gets below 7.2V, the current will drop more than you'd expect, and will drop to zero somewhere a bit below 3.6V. But, I expect this to cause very little power factor, so I believe you'll be fine.

Certainly another option, which may be simpler, is to put two bulbs in series. This should also work fine.
OP | Post 11 made on Friday December 17, 2010 at 18:12
Ernie Bornn-Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,076
I thought this was such a simple question. The ENTIRE question is contained in the title of the thread: Can I run a 120 VAC LED light off of 240 volts? Forgetting that I since discovered that my conversion system will give me 230, not 240, that was it.


Thanks to those who addressed the question. I always appreciate it when people ask questions and give some background, as I'm experienced enough (and enough of a smartass) to think maybe instead of telling someone where to get the particular weirdass thing they've decided on, maybe I can come up with a better or more available solution. That's why I discussed the power.

To all who commented on the power, I see I forgot to say I am testing these amps here in the States, which is why I need to convert 208 to 230. To those who wanted to discuss the different aspects of power, and Y and Delta, I say ? ? I told you I had the voltage and wanted a pilot light, that's about all.

And what's available overseas? We're having custom transformers made, and the power there is 60 Hz.


On December 11, 2010 at 12:36, bcf1963 said...
Ernie,

You certainly should have no problem adding a resistor.

If the power factor were not good, it would cause a problem. The only issue that could cause the power factor to be much off, would be that the forward voltage drop of a white LED is about 3.6V. So as the line voltage gets below 7.2V, the current will drop more than you'd expect, and will drop to zero somewhere a bit below 3.6V. But, I expect this to cause very little power factor, so I believe you'll be fine.

However, this is an LED built into a night-light type bulb, with a candelabra tip on it, so it's meant to screw directly into 120 volts AC. I can't see how three volts of forward drop might be an issue if there's already something in there that handles the other 117 or so volts when this is powered from a regular socket!

You DID see the place where I said I'm getting this LED bub at Home Depot, not Mouser, right?

Certainly another option, which may be simpler, is to put two bulbs in series. This should also work fine.

Electrically, simpler. I do, however, have to figure out how to mount three candelabra sockets inside a big gray electrical enclosure, positioned so they are easily visible. Three resistors are WAY easier than mounting and wiring three more candelabra sockets somewhere.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 12 made on Saturday December 18, 2010 at 02:15
bcf1963
Super Member
Joined:
Posts:
September 2004
2,767
On December 17, 2010 at 18:12, Ernie Bornn-Gilman said...
However, this is an LED built into a night-light type bulb, with a candelabra tip on it, so it's meant to screw directly into 120 volts AC. I can't see how three volts of forward drop might be an issue if there's already something in there that handles the other 117 or so volts when this is powered from a regular socket!

Ernie,

Perhaps you should reread your post, before reading my answer again. LOL I was trying to explain to you why the power factor should be good, and hence will not be an issue.

Electrically, simpler. I do, however, have to figure out how to mount three candelabra sockets inside a big gray electrical enclosure, positioned so they are easily visible. Three resistors are WAY easier than mounting and wiring three more candelabra sockets somewhere.

I think mounting the candelabra bases should be easy. Some of the bases in the link below mount into a round hole cut in a panel. Looks super simple to me... (This was the first link good came up with on a search of "candelabra socket")

[Link: grandbrass.com]
Post 13 made on Saturday December 18, 2010 at 02:59
Ozzie Glenn
Long Time Member
Joined:
Posts:
September 2008
395
On December 17, 2010 at 18:12, Ernie Bornn-Gilman said...


Electrically, simpler. I do, however, have to figure out how to mount three candelabra sockets inside a big gray electrical enclosure, positioned so they are easily visible. Three resistors are WAY easier than mounting and wiring three more candelabra sockets somewhere.

But you didnt say you couldnt have more than one!
Wireless speakers? Of course Sir. Choose the colour and size you like. As you don't seem to think sound quality is important, I will not plug them in.
OP | Post 14 made on Saturday December 18, 2010 at 15:46
Ernie Bornn-Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,076
No, I did not. I was asking about running A LIGHT off of 240 volts, which I sorta thought implied I wanted to put in just one. When buying them, I had already thought of using two in series, so was examining other approaches.

Last edited by Ernie Bornn-Gilman on December 18, 2010 16:02.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 15 made on Sunday December 19, 2010 at 00:05
bcf1963
Super Member
Joined:
Posts:
September 2004
2,767
Ernie,

It seems like you want this to be easy...

So why didn't you just stop at an electrical supply house and buy an indicator lamp? It will probably be little more than the LED candelabra bulbs you bought, but will be made for panel mounting.

It also wouldn't have taken a week to figure it out!?
Page 1 of 2


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.