On June 19, 2024 at 06:40, drs145 said...
That's good advice and I checked the power source and it seems ok.
Since this occurred after dusting and moving the cabinet I suspect it has something to do with cables, positioning, or perhaps pressing a wrong button somewhere.
To test = Remove the batteries from the MX780. Label the wires on the MRF350 going to the IR ports (1-6) and then unplug them (label them so you get them back in the correct ports). And lastly unplug the cable going to the RFX250. Plug power back into the MRF350.
1) If the power light still just continuously blinks, then you either have a defective power supply or defective MRF350. It can ONLY be one of the two, since nothing else is connected at this point.
When you 'checked the power source', how exactly did you do that? Do you have a DMM (Digital Multi Meter)? What was the reading? What does the label say on the power supply you are plugging into the MRF350?
2) If the power light no longer blinks, then unplug the MRF350 again. Plug the RFX250 back in, then plug the power back into the MRF350. If the power light starts blinking again, you have a defective RFX250. If not, go to step 3.
3) With the MRF350 powered on, start plugging the IR ports back in one at a time. If you plug one in and the power light starts blinking, that IR emitter is shorted (either cable or the emitter itself). Replace that IR emitter.
If everything is still working correctly (no blinking power light), go to step 4.
4) Put the batteries back in the MX780. If the power light on the MRF350 starts blinking, you have a problem with the MX780. Start by defaulting the remote, if the flashing power continues, replace the MX780.
Note = the MX780 will need to have the program reloaded. If you don't have the original file or working programming software - stop and call a local programmer.