On March 28, 2013 at 10:32, kgossen said...
I have yet to find a single integrator that was able to get the feedback working.
Now you have found one. The info below for the panel fields above is incomplete. You need to tell the panel what to report via field 1*70. Also ensure field 1*72 is set to 0 to disable the printer text output or you will have problems with large systems bogging the communications.
1*70 11111 (1) Report Alarmd, Check, Bypass, Open/Close, System, (test)