Post 2 made on Tuesday May 31, 2011 at 20:22
CPS Alarms
Long Time Member
Joined:
Posts:
January 2011
151
The commands are the same, the new panel runs at 9600 instead of 1200. How do you have it connected? Are you using tb4 or j9? If tb4, are you using txd to pin 2, rxd to pin 3, rts/dtr to pin 8, and gnd to pin 5 on your db9 connector?

The following group of fields must be set to use this panel with automation systems:

*05 enter 1 to send event messages on the serial port
*14 enter 1 to enable automation control input
1*78 enter 1 for extended home control events
1*79 enter 1 for each type of event you want to report
1*80 enter 0 if you want to send fault/restores for all zones to the processor

Last edited by CPS Alarms on May 31, 2011 20:30.