Sharp RS232 "ON" Command doesn't work @...
| |
|
| Topic: | Sharp RS232 "ON" Command doesn't work @ LC26P55E This thread has 10 replies. Displaying all posts. |
|
| Post 1 made on Thursday March 12, 2009 at 05:46 |
nielsy Junior Member |
Joined: Posts: | January 2009 4 |
|
|
Dear all,
I have a Sharp LCD ( LC26P55E ) with RS232 all commando's works great. But only the 'Power On' not...
I already try this : Send command "RSPW0001" from PC. (Enables TV to use ON command) Send command "POWR0000". => TV turn off. 4. Send command "POWR0001". => TV turn on. And if send "RSPW0000". => Shift to "Default" can not turn on TV with RS232
But without a good result... Who could help me? Thanx
ps. with all other rs232 commands works fine...
|
|
| Post 2 made on Thursday March 12, 2009 at 17:02 |
Oz AVI Advanced Member |
Joined: Posts: | November 2004 819 |
|
|
This is some infomation 39 Cent Stamp sent me that helped when I was having the same issues with Sharp RS232.
Menu/setup/standby mode/Mode 1 Should be enabled
Mode 2 offers power saving but causes the display not to come on via rs-232 power on command.
I didnt send any strings to it to change modes.
This should fix it!
Iain
|
Hermits have no peer pressure! |
|
| Post 3 made on Tuesday March 17, 2009 at 14:24 |
nielsy Junior Member |
Joined: Posts: | January 2009 4 |
|
|
Iain,
Thanx for your reply, I tried but I couldn't found it in the menu...
Maybe a secret menu??
or maybe a other solution??? Anyone have a tip?
|
|
| Post 4 made on Tuesday March 17, 2009 at 18:07 |
39 Cent Stamp Loyal Member |
Joined: Posts: | May 2007 5,408 |
|
|
The problem i was having was that the TV has energy saving settings that, when set to a specific mode, cause the TV to go into 'deep sleep' and RS232 cant wake it up.
Do you have the manual for the TV? If not try downloading it with this link [Link: tradenet.sharp.co.uk]
It appears, from the manual, that your menu may be slightly different. Hopefully you can navigate the confusion and find a menu with power settings that will allow you to solve the deep sleep problem.
Check page 14 for Power Management information. According to the manual it looks like the factory default may be to have the power saving settings OFF. And its quite possible that the manual is talking about something completely different and more confusing :). Poke around and see what you can come up with. Good Luck.
Adding... I didnt have to go into a secret service menu but anything is possible and your model may require you to do it. Im not aware of the steps to get into Sharps secret service menu (if it exists) though.
|
|
|
| Post 5 made on Tuesday April 7, 2009 at 01:26 |
We had this problem too. What you've got to do is turn the unit on and send the following hex string, ONCE ONLY, to turn off the Energy Saver mode.
52 53 50 57 30 30 30 31 0D
Worked for us. Unfortunately, if you turn it off with the IR remote after this, it forgets and puts energy saver mode back on after about 30 seconds.
So lose the IR remote!
Hope this helps.
|
|
| Post 6 made on Tuesday April 7, 2009 at 05:20 |
nielsy Junior Member |
Joined: Posts: | January 2009 4 |
|
|
Thanx, I will try it tonight!
Thanx for your reply! I will let you know if it also worked for me...
|
|
| Post 7 made on Thursday April 9, 2009 at 14:53 |
Tdurrant20 Junior Member |
Joined: Posts: | March 2009 21 |
|
|
your enable command is wrong
it should be this RSPW1 CR
there are three spaces between the 1 and the carriage return
which 232 controller are you using? that will turn it off permanetly
|
|
| Post 8 made on Thursday April 9, 2009 at 14:55 |
Tdurrant20 Junior Member |
Joined: Posts: | March 2009 21 |
|
|
sorry i ment that will turn off the energy saving mode permanently
btw, from my documentatation your power commands are wrong
they should be POWR1 CR for on POWR0 CR for on
noticeagain the 3 spaces
|
|
| Post 9 made on Monday April 20, 2009 at 03:57 |
nielsy Junior Member |
Joined: Posts: | January 2009 4 |
|
|
I use a AMX controller for rs232.
Your right about : POWR0 ,cr ect. In my program is that right. Everything works fine exept the ON command.
I give it a try to using RSPW1 CR and will see if then the ON command will works... Else I think it must be done by IR... but I hope this will work!
Thanx! I let you know...
|
|
| Post 10 made on Monday June 8, 2009 at 19:38 |
pilasz Regular Member |
Joined: Posts: | September 2007 100 |
|
|
Try RSPW1___CR - underscore equals three space characters. In URC speak that would be RSPW1\x20\x20\x20. Actually RSPW1 command is power save disable.
|
e-Age Services Art of politics - make them have it your way.. |
|
| Post 11 made on Thursday October 1, 2009 at 21:29 |
Tarzan2 Long Time Member |
Joined: Posts: | October 2004 23 |
|
|
RSPW1 \r This fixed the problem for me on a LC65E77UM.
Thanks.
|
|
 |
Before you can reply to a message... |
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now. |
Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.
|
|
|
|
|