Fireplace Control Over a Long Distance
This thread has 8 replies. Displaying all posts.
Post 1 made on Monday May 5, 2008 at 18:46
cheesehead22
Long Time Member
Joined:
Posts:
May 2007
409
I have read here somewhere before but can not find the post so here is the question.

I have to control 2 different fireplaces that are each over 200 feet away from my RP-6. I have heard of people putting relaies or something at the fireplace switch location and haveing the RP-6 trigger the relay.

I would like to know how people are doing this and with what parts. All that I have going to the fireplace switch from the processor is a 18/2.

Thanks
Don't read my answer. Someone else will go into great detail as to why I am wrong rather than answer the original question...
Post 2 made on Monday May 5, 2008 at 19:12
tweeterguy
Loyal Member
Joined:
Posts:
June 2005
7,713
Probably already a toggle switch in place if it's existing right? Take switch out, should be 2 wires present. Touch them together and FP should fire up. Replace switch with a 12v relay and with your 18/2 connected to NO and Common. Close the relay from the processor. We always carry around DPDT (double pole double throw) relays for stuff like this but all that is needed is a SPST.

Last edited by tweeterguy on May 6, 2008 21:15.
Post 3 made on Monday May 5, 2008 at 21:31
oex
Super Member
Joined:
Posts:
April 2004
4,177
most fireplaces have wiring that basically interupts the safety loop and could easily be connected to the rp6. This is typically the wiring at the wall switch(NOT 120v).

this is how i control them from litetouch and all works well.

if you are trying to control hi voltage then your need to do something else.
Diplomacy is the art of saying hire a pro without actually saying hire a pro
Post 4 made on Tuesday May 6, 2008 at 07:38
dinom
Active Member
Joined:
Posts:
February 2004
643
Here's a good thread:

[Link: remotecentral.com]
Post 5 made on Tuesday May 6, 2008 at 18:51
Ernie Bornn-Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
Absolutely DO NOT use 120 volts to switch anything. EVER. Unless some company has designed a switch that has 120 volts in it already, you have an electrician's license, and you have the skill to know how to do it already.

By "safety loop," oex means the microvolt circuit, a circuit where the pilot light heats a thermopile which generates a tiny voltage with enough current to keep a gas valve open. This is what you've got on all water heaters where you hold down a button for about a minute after lighting the pilot light.

You wouldn't actually interrupt the safety loop, because that would shut off gas to the pilot light. Instead, such a heat source has a pair of wires coming out of it that turn on the gas in the main burner when shorted together. This is the pair of wires that go to a thermostat for a dumb floor heater, or to a switch ( = pair of relay contacts) for a fireplace, or are internally shorted in a water heater when the water is cold enough.

If the pilot light goes out, the microvoltage is not available, so gas can't run without the pilot light, which equals no rooms full of gas.

Run twelve volts via your 18-2 out to a 12 volt relay near the fireplace. Use a set of relay contacts on the XP8 or RP6 to turn that relay on and off, thus turning the fireplace on and off.

you may find that you have to run more than twelve volts out there if the wire 18-2 resistance lowers the voltage to the point where the external relay won't switch.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 6 made on Tuesday May 6, 2008 at 21:15
tweeterguy
Loyal Member
Joined:
Posts:
June 2005
7,713
On May 5, 2008 at 19:12, tweeterguy said...
Replace switch with
a 120v relay and with your 18/2 connected to NO and Common.

Ha...typo on my part, I meant 12v...obviously he gets it. I'll fix the post.
Post 7 made on Wednesday May 7, 2008 at 07:33
oex
Super Member
Joined:
Posts:
April 2004
4,177
jeez - there is a pair of wires in almost every gas fireplace that says connect remote switch/control here.
Diplomacy is the art of saying hire a pro without actually saying hire a pro
OP | Post 8 made on Wednesday May 7, 2008 at 21:37
cheesehead22
Long Time Member
Joined:
Posts:
May 2007
409
Hey oex, can you give me a rough idea as to were those wires might be. Never been in a gas fireplace before.
Don't read my answer. Someone else will go into great detail as to why I am wrong rather than answer the original question...
Post 9 made on Wednesday May 7, 2008 at 22:29
oex
Super Member
Joined:
Posts:
April 2004
4,177
in all ot the heat and glow unit they are at the bottom, behind the flip up vent. They are hanging right on the gas valve and I believe they are red with a sticker across them saying connect low voltage switch here.

The location is the same on the clean face units.

[Link: content.hearthnhome.com]

see diagrams on page 38
Diplomacy is the art of saying hire a pro without actually saying hire a pro


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.