RP6 issues and ATON code issues...
This thread has 2 replies. Displaying all posts.
Post 1 made on Friday March 21, 2008 at 00:19
Groovit
Long Time Member
Joined:
Posts:
February 2008
269
So... I would love to hear any ideas on all or part of this... please...

Whenever any ATON DLA IR code is issued (codes from the .ccf from ATON) the RP6 locks up. The status light stays green, the high out port stays lit (the ATON codes are routed on the high out port to a connecting block) and all RP6 functions are locked up.

I disconnected the DLA from the IR connecting block and pulled the 12v power supply from the IR block but still had the same issues so it seems to be an issue on the processor. The ATON controls worked well on the bench using the same codes.

Here are the particulars and a list of other issues...

RP6 High out feeds Niles IR block to hard wire terminal on the ATON DLA, Direct IR (mono plug) in on Denon 2308CI and an emitter for the TV. The high out is run from the processor to the block via approximately 80 feet of CAT5 into another room. The kicker is that due to a skimpy prewire (I lost the original job to the original owner to a cheap bid) I had to use this one CAT5 to send analog audio (on a Niles Balun) to the remote location on 1,2,3 and 6, the signal back from a local RM433 on 4, the high out to the same remote location on 5, ground on 7 and voltage for the RM 433 on 8. Despite the potential issues with this, it worked well on the bench and seems to work fine in the installed environment, however, I do have some other mysteries...

All functions on the Denon receiver work fabulously except Power On. I am using all clean codes that I have used numerous times. The routing is good. One thought I had is that there may be some latency over the long run with shared signals so I may try ramping the repeats on the power on code or try inserting delays between codes in the macro. My thinking is that consecutive codes in the macro may be masking eachother due to any latency.

The Mitsubishi TV (I know... not my choice... but there are discretes) Power Codes for the same room (off of the IR block) do not work. Input commands do work. I have tried them all via standalone and they work fine. My next step is to try them as button commands to see if they work outside of the macros in light of my latency concerns. These are not cleanly generated... from the library...

Everything in the head end rack works well. It is just this remote room that is a pain.

Worst case... my whacked wiring solution causes issues with some codes and not others... but that does not solve the ATON code issues.

Last edited by Groovit on March 21, 2008 11:49.
Post 2 made on Friday March 21, 2008 at 20:37
tgrugett
Select Member
Joined:
Posts:
August 2004
1,850
In the field now...

It is a problem with the RP6, Niles MSU140 connecting block and the ATON codes.

With MSU140 power disconnected, all MSU140 emitter output ports disconnected (including Denon and ATON direct connections) and the highout and ground connected to the MSU140, the ATON codes (ONLY the ATON codes!) cause the RP6 to lock up and continually output on the high out. As soon as the high out is disconnected from the MSU140... problem gone. All other code issues for all other devices are fine. There seems to be no connection between the ATON DLA itself and the RP6 lockup.

WTF?
Post 3 made on Friday March 21, 2008 at 21:18
tgrugett
Select Member
Joined:
Posts:
August 2004
1,850
Another update...

the MSU140 is not the issue. Any completed circuit on the high out at the remote location causes the RP6 to lock up with an ATON code issue.

I am going to try a completed circuit at the processor...


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.