On April 11, 2006 at 21:57, ultimate trunk slammer said...
Doing a commercial 70volt dist audio system.
One tech told me I need to ground the shielded
speaker cable with the emt while another told
me that I didn't need to. So who's right?
I'm running the 18-2 inside the same conduit as
my coax+power for the 24ac cameras, so I decided
to use twisted pair shielded speaker cable that
comes with a drain wire and 100% aluminum foil.
The reason the tech advised you to ground the 70 volt audio system (which was probably in conduit for part of it's circuit) was so that some poor bastard like larry's camp counsellor wouldn't ground something to your floating conduit and think that itwas properly grounded, then proceed to shock himself to death. As soon as you start putting things in conduit, most electrical codes require that your conduit system be properly grounded, even if it is a very limited system. A welder might pop a ceiling tile and see your un grounded conduit and think that he will have a pipe to ground to.
A good example is a system in which you run all of your 70 volt audio system using let's say 18G or 20 G 2 conductor signal wire in an open ceiling cavity without conduit or a raceway. You run into a situation where you want to protect the conductors mechnically for a short distance such as a publc hallway, or a bridge between concealed ceiling cavities that might protect otherwise vulnerable wiring. Then you use a limited amount of EMT to physically protect those circuits ( a short bridge). That's when you run into having to conform to adhering to 120 volt AC electrical code requirements. All that will be required to meet the code requirements is to bond any of your pipe to the nearest confirmed building electrical ground or a conduit system that is grounded. The circuit within the conduit isn't actually grounded , but the conduit or bridge containing it is.
Last edited by teknobeam1
on April 15, 2006 03:14.