ground loop isolators
This thread has 25 replies. Displaying posts 16 through 26.
Post 16 made on Thursday December 1, 2005 at 10:52
MN Installer
Founding Member
Joined:
Posts:
September 2001
91
On December 1, 2005 at 08:08, Audible Solutionns said...
I am unclear why you think dry, rocky dirt is
a poor conductor? There is no better conductor
than "earth." You may need an 8 foot grounding
rod but I have never heard--though that in of
itself says little--about different types of soil
conducting electricity better or worse. You need
to go down into that "soil" 8-10 feet but I do
not see why the contents of the soil would make
ground less of a conductor. The purpose of bonding
to metal plumbing pipes is precisely to take advantage
of the fact that plumbing pipes by code are burried
in the earth sufficiently deep to be used as effective
grounding conduits for stray voltages.

Alan:

I've got a wonderful book on lightning and EMP pulse protection for radio and TV broadcast plants that devotes about 90% of the book to getting good grounds in the field.

The one thing above all else it stressed was that earth was only a "good" ground when there was some level of moisture in the earth that contacted the grounding electrodes. In desert and rocky locations, it is nearly universal to specify "ufer" grounds (electrodes encased in concrete) because even when cured, the internal portions of the concrete retain moisture which helps to provide an effective path for electron movement. This moisture is so important, that on "ufer" grounds, if the electrode is less than 4" from the outside edge of the concrete, the current moving through it will cause the moisture to become steam and actually blow out the concrete.

Obtaining good earth grounds in dry/rocky climates is a continual challenge.

Brad
Post 17 made on Thursday December 1, 2005 at 14:48
Barry Shaw
Founding Member
Joined:
Posts:
June 2001
688
On December 1, 2005 at 08:08, Audible Solutionns said...
I am unclear why you think dry, rocky dirt is
a poor conductor?

Read the Ufer ground link I posted or google "ground rods" and you'll run into all kinds of notes on moisture & pH factors. As far I can tell, not all dirt is created equally.

Talked to one my favorite electricians this morning and he agrees that many ground rods in our "bad" local dirt are really only cosmetic after a few years.

He also says the local inspectors are finally pushing for Ufer grounds, especially after they did their own local measurements on new construction & 2-3 year old foundations. They think the Ufer maintains or actually improves as it ages.

Anyone who has dealt with an electrician with
respect to lighting control systems will tell
you that most do not understand loads let alone
AC vs DC electrial theory. Unfortunately, Larry
is so atypical of what I run into with respect
to electricans with respect to the amount and
type of knowledge he possesses.

Lighting systems are where I really started to interact with electricians, and yes, Larry is *way* atypical. That's exactly why I'm trying throw out my half-baked ideas here so he can edumucate me.

They do not need to understand dc
theroy nor do they need to deal with ground loops
as they don't encounter them often--save when
they have anoying A/V guys on the job.

I'm trying to walk that fine line of making my stuff actually work without becoming the annoying A/V guy.
"Crestron's way better than AMX."
Post 18 made on Thursday December 1, 2005 at 15:21
Barry Shaw
Founding Member
Joined:
Posts:
June 2001
688
On December 1, 2005 at 10:52, MN Installer said...
In desert and rocky
locations, it is nearly universal to specify "ufer"
grounds (electrodes encased in concrete) because
even when cured, the internal portions of the
concrete retain moisture which helps to provide
an effective path for electron movement. This
moisture is so important, that on "ufer" grounds,
if the electrode is less than 4" from the outside
edge of the concrete, the current moving through
it will cause the moisture to become steam and
actually blow out the concrete.

We had a home with lightning strike on a tree 50 yards from the house... split the tree like a toothpick and vaporized the underground PVC water line and a buried LV landscape wire as it followed them back to the house...

* Shattered the outside Phone demarc box, vaporized 25' of Cat5 leaving just little blue PVC gobules and scortched marks on the studs until it hit our Panamax KSU4x4. Toasted the 4x4, but protected all downstream phones & modems. I was impressed.

* Blew several light swtches completely *out of the wall*. Had to re-paint around many other switches.

* Wiped out what I thought were low-tech durable things like the toaster, washing machine motor, icemaker, but left almost all A/V & computer gear intact.

* The concussion blew out the main picture window in the Living Room. The wife was in the Kitchen. When she sees a storm coming now she literally hides in a downstairs closet.

* Popped sheetrock screws in wood studs out... where is the conduction path there?

* The crazy part is it took a 2' chunk of concrete out of the foundation as it entered. I never understood how, but maybe your moisture is the key. I'd always thought of concrete as an insulator.
"Crestron's way better than AMX."
Post 19 made on Thursday December 1, 2005 at 22:39
Larry Fine
Loyal Member
Joined:
Posts:
August 2001
5,002
The simple answer is that the heat from lightning boils the water, and the expansion explodes, just like popcorn. A tree splits because the water in the tree turns into steam, which has a much higher volume for the same amount of water molecules.

Ufer grounds are effective because of a combination of the sheer area in contact with the earth, below the frost line, which is typically 2 to 3 feet, and the rebar, which is wire-ried together, and must be bonded with a #4 copper conductor or equivalent.

Driven rods are not consistant in their impedances. Soil conditions do vary with the seasons, and that does have an effect on impedance. Sometimes, rods that can be screwed together end-to-end are driven 50 feet or more for certain applications.

The damage described by Barry points out the importance of EVERY conductive pathway into a building having proper lightning arrestors installed, or bonded, like metallic piping. Plastic underground piping has a wire added to make it traceable.

Cable-TV coax would be much less of a problem if the NEC requirements were enforced. They should be grounded not only to a rod nearest the cable entrance, but that rod should be bonded to the power rod with a #6 copper or equivalent.

It is NOT safe to say that all underground metal piping qualifies as a grounding electrode. To do so, it must be unbroken for at least 10 feet underground (how to verify?), and the connection must be within 5 feet of the pipe's entrance into the building.

However, with the exception of incoming cables, ground loops are usually caused, and cured, within the premises. Ground loops and different-phase issues are related, but are different. Ground loops can occur even with all equipment on one circuit.


"That's all I have to say about that." - Forrest Gump
Post 20 made on Thursday December 1, 2005 at 23:05
2nd rick
Super Member
Joined:
Posts:
August 2002
4,521
I have a friend who is a Leiutenant on a small town fire dept.
His best lighning strike story is when a metal clothesline frame took a direct hit and then the bolt jumped on to the underground phone line between the pedestal and the demarc.
He said it TRENCHED the run back open (his words "it looked like the little trail in the Bugs Bunny cartoon", and then the answering machine and phones exploded!!

All applicances and electronics were toasted, and there was a request for a full electrical inspection that came from either the Village or the Fire Marshal.
Rick Murphy
Troy, MI
OP | Post 21 made on Sunday December 18, 2005 at 23:46
Munson
Long Time Member
Joined:
Posts:
January 2003
499
,

Last edited by Munson on December 28, 2006 20:35.
Post 22 made on Monday December 19, 2005 at 07:15
AARON BROWN
Long Time Member
Joined:
Posts:
September 2004
400
6 grand!!!!????? Ouch...................
Post 23 made on Monday December 19, 2005 at 08:30
ejfiii
Select Member
Joined:
Posts:
July 2003
2,021
Holy Crap.
Post 24 made on Monday December 19, 2005 at 11:32
Ted Wetzel
Founding Member
Joined:
Posts:
November 2001
879
Yep. that's why it is CHEAP to make sure the power distribution is right to start with! But at least you found a solution and hopefully you didn't have to eat any of it.
Post 25 made on Monday December 19, 2005 at 12:00
Theaterworks
Founding Member
Joined:
Posts:
April 2002
1,898
Wow, 6K. I'm writing another exclusion in our warranty right now.
Carpe diem!
Post 26 made on Monday December 19, 2005 at 12:04
Ted Wetzel
Founding Member
Joined:
Posts:
November 2001
879
On December 19, 2005 at 12:00, Theaterworks said...
Wow, 6K. I'm writing another exclusion in our
warranty right now.

good thought....
Page 2 of 2


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.