On 03/13/05 02:37 ET, Ernie Bornn-Gilman said...
Of course, this is a product which TELLS YOU to
run the low-voltage wire inside the electrical
box. Larry, how do they get away with that?
Here's what I could find in the 2002 NEC that may be pertinent:
725.2 Definitions. For purposes of this article, the following definitions apply.
Class 1 Circuit.
The portion of the wiring system between the load side of the overcurrent device or power-limited supply and the connected equipment. The voltage and power limitations of the source are in accordance with 725.21.
Class 2 Circuit.
The portion of the wiring system between the load side of a Class 2 power source and the connected equipment. Due to its power limitations, a Class 2 circuit considers safety from a fire initiation standpoint and provides acceptable protection from electric shock.
Class 3 Circuit.
The portion of the wiring system between the load side of a Class 3 power source and the connected equipment. Due to its power limitations, a Class 3 circuit considers safety from a fire initiation standpoint. Since higher levels of voltage and current than Class 2 are permitted, additional safeguards are specified to provide protection from an electric shock hazard that could be encountered.
725.26 Conductors of Different Circuits in the Same Cable, Cable Tray, Enclosure, or Raceway.
Class 1 circuits shall be permitted to be installed with other circuits as specified in 725.26(A) and (B).
(A) Two or More Class 1 Circuits.
Class 1 circuits shall be permitted to occupy the same cable, cable tray, enclosure, or raceway without regard to whether the individual circuits are alternating current or direct current, provided all conductors are insulated for the maximum voltage of any conductor in the cable, cable tray, enclosure, or raceway.
(B) Class 1 Circuits with Power Supply Circuits.
Class 1 circuits shall be permitted to be installed with power supply conductors as specified in 725.26(B)(1) through (B)(4).
(1) In a Cable, Enclosure, or Raceway.
Class 1 circuits and power supply circuits shall be permitted to occupy the same cable, enclosure, or raceway only where the equipment powered is functionally associated.
(2) In Factory- or Field-Assembled Control Centers.
Class 1 circuits and power supply circuits shall be permitted to be installed in factory- or field-assembled control centers.
725.55 Separation from Electric Light, Power, Class 1, Non–Power-Limited Fire Alarm Circuit Conductors, and Medium Power Network-Powered Broadband Communications Cables.
(A) General.
Cables and conductors of Class 2 and Class 3 circuits shall not be placed in any cable, cable tray, compartment, enclosure, manhole, outlet box, device box, raceway, or similar fitting with conductors of electric light, power, Class 1, non–power-limited fire alarm circuits, and medium power network-powered broadband communications circuits unless permitted by 725.55(B) through (J).
(B) Separated by Barriers.
Class 2 and Class 3 circuits shall be permitted to be installed together with Class 1, non–power-limited fire alarm and medium power networkpowered broadband communications circuits where they
are separated by a barrier.
(C) Raceways Within Enclosures.
In enclosures, Class 2 and Class 3 circuits shall be permitted to be installed in a raceway to separate them from Class 1, non–power-limited fire alarm and medium power network-powered broadband communications circuits.
(D) Associated Systems Within Enclosures.
Class 2 and Class 3 circuit conductors in compartments, enclosures, device boxes, outlet boxes, or similar fittings shall be permitted to be installed with electric light, power, Class 1, non–power-limited fire alarm, and medium power networkpowered broadband communications circuits where they are introduced solely to connect the equipment connected to Class 2 and Class 3 circuits, and where (1) or (2) applies:
(1) The electric light, power, Class 1, non–power-limited fire alarm, and medium power network-powered broadband communications circuit conductors are routed to maintain a minimum of 6 mm (0.25 in.) separation from the conductors and cables of Class 2 and Class 3 circuits.
(2) The circuit conductors operate at 150 volts or less to ground and also comply with one of the following:
a. The Class 2 and Class 3 circuits are installed using Type CL3, CL3R, or CL3P or permitted substitute cables, provided these Class 3 cable conductors extending beyond the jacket are separated by a minimum of 6 mm (0.25 in.) or by a nonconductive sleeve or nonconductive barrier from all other conductors.
b. The Class 2 and Class 3 circuit conductors are installed as a Class 1 circuit in accordance with 725.21.