Post 1 made on Wednesday February 2, 2005 at 20:52 |
cowboy Long Time Member |
Joined: Posts: | November 2003 188 |
|
|
I've got a 20x24x36 cabinet with a pull out mid atlantic rack. A door is present with the little rubber bumpers that keep it from slapping shut. This leaves about a 1/8" crack around the perimeter of the door. Currently I have a double rack mounted fan unit on the top back of the rack, blowing towards the door. In the back of the cabinet, there are a couple of 4 inch holes to route the wires in. In spite of this, it still gets hot enough to warm a small house, so I end up opening the door and every couple of hours. Any good websites on how to's? Such as quite fans, filtering, fan placement, etc.
Thanks Roger
|
|
Post 2 made on Wednesday February 2, 2005 at 21:09 |
jeffh9020 Long Time Member |
Joined: Posts: | December 2003 105 |
|
|
If indeed the crack is a consistent 1/8" and the door is, say, 22" by 34", then you have the equivalent of a 14 sq. in. hole at the front of the cabinet; plenty for ventilation without even considering the holes in the back. However, blowing air toward the door won't do it. Get the air flow reversed and vent it out the top or back. The fan will need to be flush mounted to either of these to be effective. This will allow you you take advantage of the venturi effect; air that has to pass through a constriction speeds up. It sounds like the fan's current position is doing little more than blowing hot air around. Good luck! Jeff
|
|
Post 3 made on Wednesday February 2, 2005 at 21:11 |
AHEM Select Member |
Joined: Posts: | January 2004 1,837 |
|
|
Yes, as I recall, Mid Atlantic has a "cabinet cooling white pages" that has the ins and out of cooling. In fact, here's a link to the form that you have to fill out to DL it: [Link: repnet.middleatlantic.com]
|
|
Post 4 made on Wednesday February 2, 2005 at 21:44 |
oex Super Member |
Joined: Posts: | April 2004 4,177 |
|
|
|
Diplomacy is the art of saying hire a pro without actually saying hire a pro |
|
Post 5 made on Wednesday February 2, 2005 at 22:25 |
Marky_Mark896 Select Member |
Joined: Posts: | January 2004 1,545 |
|
|
oex, you beat me to it. This is what I have used, and it works great. I bought the system with the individual fans and controller for 4 fans. I cut a slit in the bottom of my cabinet for air intake (using a router) and then cut holes for the fans in the back top of each of the cabinets. Nothing but room temp in all three now.
Mark
|
It's not just a hobby, it's an obsession... |
|
Post 6 made on Thursday February 3, 2005 at 00:33 |
Ahl Founding Member |
Joined: Posts: | October 2001 1,241 |
|
|
if the front of your cabinet is shaped like this:
| <----door |___ | |____________(floor)
put air holes in the horizontal section
|
We can do it my way, or we can do it my way while I yell. The choice is yours. |
|
|
Before you can reply to a message... |
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now. |
Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.
|
|
|
|