What is the idea ambient temperature range for a room in which a rack is located ?
This thread has 12 replies. Displaying all posts.
Post 1 made on Saturday October 3, 2020 at 05:39
james_aa
Long Time Member
Joined:
Posts:
January 2018
235
What is the idea ambient temperature range for a room in which a rack is located (not the temp for the rack itself) but the temp for the rack room ?
Post 2 made on Saturday October 3, 2020 at 09:07
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,321
On October 3, 2020 at 05:39, james_aa said...
What is the idea ambient temperature range for a room in which a rack is located (not the temp for the rack itself) but the temp for the rack room ?

As long as it doesn't affect the equipment, it really doesn't matter. Does the building have a basement with unfinished space? If so, vent the rack to the basement and craw supply air from somewhere cooler.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 3 made on Saturday October 3, 2020 at 09:56
tomciara
Loyal Member
Joined:
Posts:
May 2002
7,962
It doesn’t matter sounds pretty off the wall to me. You must mean something different than I am reading.

I don’t have the precise answer, but when I install simple cooling in a cabinet or closet, the fanS come on at about 90°. Temperatures over that in a room would call for remedial work in the form of larger exhaust fans or full on cooling.
There is no truth anymore. Only assertions. The internet world has no interest in truth, only vindication for preconceived assumptions.
Post 4 made on Saturday October 3, 2020 at 10:13
Mac Burks (39)
Elite Member
Joined:
Posts:
May 2007
17,518
Google says 68-71 degrees is typical for a server room. We have a bunch of proper equipment rooms out there and they are usually set to 72 except in Florida where they are usually set between 65-70.
Avid Stamp Collector - I really love 39 Cent Stamps
Post 5 made on Saturday October 3, 2020 at 11:38
buzz
Super Member
Joined:
Posts:
May 2003
4,371
There is no "one size fits all" temperature. The critical part is the operating temperature of box XYZ in the rack and this will depend on ambient temperature and air flow around each box.

Sometimes it can get strange. I had an EoP network switch that dumped a bit of heat into the space. For wire management reasons I mounted the switch upside down. Inside the switch, natural convection did not work very well in the inverted mounting scheme and the unit's fans went into overdrive -- they were annoying screamers. After some grumbles I remounted the switch, re-routed the cables, and the fans quieted down.

There is a scheme used in large infrastructure projects where the entire rack is filled with liquid Freon, using heat exchangers to pipe waste heat outside the building. In such an installation, air temp near the rack is not a major concern. This approach saves board space because processors and other high heat components are mounted raw -- no heat sink or fans required.
Post 6 made on Saturday October 3, 2020 at 11:40
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,321
On October 3, 2020 at 09:56, tomciara said...
It doesn’t matter sounds pretty off the wall to me. You must mean something different than I am reading.

I don’t have the precise answer, but when I install simple cooling in a cabinet or closet, the fanS come on at about 90°. Temperatures over that in a room would call for remedial work in the form of larger exhaust fans or full on cooling.

And I included "as long as it doesn't affect the equipment"- what's the problem if the temperature isn't ridiculously high?
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 7 made on Saturday October 3, 2020 at 12:42
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
All of everybody's comments confirm what I thought when I read the first post:

Why do you ask?

All of those answers are correct and all of them also miss some particular thing that's being asked.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 8 made on Saturday October 3, 2020 at 12:48
Brad Humphrey
Super Member
Joined:
Posts:
February 2004
2,594
No one reads white papers anymore? Go to trainings or webinars?
There are industry guidelines that have been in place for decades, that were arrived at after doing extensive research.

The one that stands out the most in my memory, is the white paper Middle Atlantic has (don't know where to download it these days, I have it stored on my NAS):
it states *for residential A/V racks or cabinets*, that for every 10°F (5.6°C) above 85°F (29.4°C), equipment lifespan will be cut by 50%. So it is recommended to keep the ambient temperature around equipment, below 85°F (29.4°C).

I haven't seen any updated guidelines from the manufactures or trainings about it from CEDIA in many years. So it could be with modern equipment, those guidelines need to be updated.
Also note (as most already know) a server room is a different animal and has different guidelines. Such as the recommended ambient temperature is much lower for that situation - as Mac's Google search hints to. But thinking about it, all of our racks and cabinets look more like IT racks everyday. So....
Post 9 made on Saturday October 3, 2020 at 19:05
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
On October 3, 2020 at 12:48, Brad Humphrey said...
The one (white paper) that stands out the most in my memory, is the white paper Middle Atlantic has (don't know where to download it these days, I have it stored on my NAS):
it states *for residential A/V racks or cabinets*, that for every 10°F (5.6°C) above 85°F (29.4°C), equipment lifespan will be cut by 50%. So it is recommended to keep the ambient temperature around equipment, below 85°F (29.4°C).

Yes, but surely this refers to temperature INSIDE those "residential A/V racks or cabinets," which doesn't directly address the ambient temperature of the room.

Thinking about it, the ambient temperature of the room will have to be lower than the temperatures specified for the "racks or cabinets" if that ambient air is not being pumped in and through the cabinets... at which point that air will rise in temperature. To get this right, the room and racks have to be built, then in-rack temperatures measured, in order to work out how much lower the ambient temperature of the room needs to be.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 10 made on Sunday October 4, 2020 at 00:14
tomciara
Loyal Member
Joined:
Posts:
May 2002
7,962
On October 3, 2020 at 11:40, highfigh said...
And I included "as long as it doesn't affect the equipment"- what's the problem if the temperature isn't ridiculously high?

Well in that case I guess your answer really wasn’t an answer at all. With your knowledge of electronics, you know that temperature is the enemy of anything electronic.

So saying it doesn’t matter unless it affects the equipment, maybe that is sort of an oxymoron, or maybe just a non-statement. I don’t know.

......................

As usual, Brad is front and center with valuable info. Does living in the sticks give him more than 24 hours per day, in order to amass this encyclopedic level of data?
There is no truth anymore. Only assertions. The internet world has no interest in truth, only vindication for preconceived assumptions.
Post 11 made on Sunday October 4, 2020 at 04:42
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,321
On October 4, 2020 at 00:14, tomciara said...
Well in that case I guess your answer really wasn’t an answer at all. With your knowledge of electronics, you know that temperature is the enemy of anything electronic.

So saying it doesn’t matter unless it affects the equipment, maybe that is sort of an oxymoron, or maybe just a non-statement. I don’t know.

......................

As usual, Brad is front and center with valuable info. Does living in the sticks give him more than 24 hours per day, in order to amass this encyclopedic level of data?

I actually included 'as long as it doesn't affect the equipment. The room and inside of the rack can be separate and I also wrote about supply & exhaust air. That should have told you something but, apparently, it didn't.

If living in the sticks adds time to the day, I suspect it's from not having to deal with constant bullcrap in the city.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 12 made on Sunday October 4, 2020 at 05:31
buzz
Super Member
Joined:
Posts:
May 2003
4,371
Ambient temperature is only part of the consideration. Waste heat must be removed from the area. One must consider the whole situation — equipment, lighting, sunlight, appliances, humans, etc.

In my home office summertime is a challenge as the air conditioner can barely cope and I’ll need to partially shut down equipment on stinking hot days. In the winter months, I barely need heat in that room.
Post 13 made on Sunday October 4, 2020 at 12:30
Trunk-Slammer -Supreme
Loyal Member
Joined:
Posts:
November 2003
7,459
57.

That way you can store your wine in the room as well as the equipment... :-)


Multitasking at it's finest....


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.