Post 16 made on Saturday April 18, 2020 at 12:05
Neurorad
Super Member
Joined:
Posts:
September 2007
3,011
The real challenge is getting the bonding wire run from the LV cable entrance to the system bonding terminal.

What gauge wire would that bonding wire be?
TB A+ Partner
Believe nothing, no matter where you read it, or who said it, no matter if I have said it, unless it agrees with your own reason and your own common sense. -Buddha
Post 17 made on Saturday April 18, 2020 at 18:17
davidcasemore
Super Member
Joined:
Posts:
January 2003
3,352
On April 18, 2020 at 12:05, Neurorad said...
The real challenge is getting the bonding wire run from the LV cable entrance to the system bonding terminal.

What gauge wire would that bonding wire be?

In most cases a 10AWG solid copper wire is fine.

Do you have a copy of the NEC? Local jurisdictions can have their own regulations as well.

Typically the LV cable drop is located next to the electrical service drop. In my area a ground rod is used as a supplementary grounding electrode and is driven near the service entrance and meter enclosure. The system electrode grounding conductor is right there (coming out of the house and going to the ground rod). The electrician often times will attach a terminal to that wire with something like this:

[Link: aifittings.com]
Fins: Still Slamming' His Trunk on pilgrim's Small Weenie - One Trunk at a Time!
Post 18 made on Monday April 20, 2020 at 10:02
SWOInstaller
Select Member
Joined:
Posts:
October 2010
1,596
The reason to Bond your devices as opposed to ground/earth is you are providing one path to ground.

lets say you have a satellite dish and you install some type of grounding device (plate, rod, post, etc) and ground your dish to the device. You have the sat receivers inside the house that are electrically grounded to the building ground rod, plate etc. A surge comes in and rather than going direct to ground it now travels through the cabling (coax, HDMI, CATX, etc) and goes out to the dish ground.

Electricity flows in the path of least resistance. Although having to travel through multiple boxes and cables there may be less resistance to get to the satellite ground than going to the building ground.

Now if you were to Bond the satellite dish to the house/building ground then there would only ever be one path for the surge to go reducing the risk of the surge to go through all the devices in the rack first.
You can't fix stupid
Post 19 made on Monday April 20, 2020 at 11:27
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
On April 17, 2020 at 20:04, internetraver said...
If you know it's a picky point then why bother?  This is a forum, not an encyclopedia.  It ain't got to be perfect to get da point across......

That's true, but sometimes it's got to be perfect to get to the right answer the quickest way.

Beside that, I don't think this forum is just for people who know 99% of what's needed; I think it's for people early in their careers, too.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 20 made on Monday April 20, 2020 at 13:14
buzz
Super Member
Joined:
Posts:
May 2003
4,384
Earth and that ground rod contact with earth have a much higher resistance compared to copper on a terminal strip. If there is a lightning strike near one end of the house, there will be a huge voltage drop in the earth as the strike leaks away. If you have separate ground rods connected to your system at each end of the house, they are no longer at equal potential and your system must absorb this difference. Since quite a lot of energy is available from that strike, your system is overwhelmed. The bonding wire will have less resistance than the coax shields of your wire and the bond will absorb most of the energy.

There is also a personal safety risk at the instant of the strike. If you are touching an element of your system and a water pipe at that instant, there will be a voltage drop across your body. Good bonding insures that your system elements are at the same potential as that water pipe.
Post 21 made on Monday April 20, 2020 at 13:37
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
On April 20, 2020 at 13:14, buzz said...
Earth and that ground rod contact with earth have a much higher resistance compared to copper on a terminal strip. If there is a lightning strike near one end of the house, there will be a huge voltage drop in the earth as the strike leaks away. If you have separate ground rods connected to your system at each end of the house, they are no longer at equal potential and your system must absorb this difference. Since quite a lot of energy is available from that strike, your system is overwhelmed.
The bonding wire will have less resistance than the coax shields of your wire and the bond will absorb most of the energy.

Well... the bonding wire will have less resistance than the coax shields of your wire and the bonded path will (more) safely carry the energy to your single ground.

The bond itself is the point where wires electrically connect together, and bonds do not absorb the energy. They allow the energy to be safely carried to ground.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 22 made on Monday April 20, 2020 at 17:43
buzz
Super Member
Joined:
Posts:
May 2003
4,384
On April 20, 2020 at 13:37, Ernie Gilman said...
The bond itself is the point where wires electrically connect together, and bonds do not absorb the energy. They allow the energy to be safely carried to ground.

OK, I'm very sorry for the misuse of definitions. The bond wires only enable the system to be at equal potential (less a few relatively minor voltage drops) -- regardless of the less than ideal connection with earth.
Post 23 made on Monday April 20, 2020 at 22:04
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
That was for clarity, not because any apology was needed.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
OP | Post 24 made on Tuesday April 21, 2020 at 06:16
crosen
Senior Member
Joined:
Posts:
April 2009
1,262
On April 17, 2020 at 15:23, SWOInstaller said...
For those that are protecting the devices are you running a separate bond wire from the house or are you just connecting a wire/screw to a piece of metal which appears to be grounded?

Doing this incorrectly isn't providing any benefit and may cause more harm than good by creating two paths to ground.

I’m not sure I follow this. Can you describe the proper protection that should be in place for, say, an outdoor speaker? Assume without protection you simply have a 14/2 cable running from the speaker back to an amplifier in a rack. What exactly would you put in place for proper surge protection and grounding of this speaker?
If it's not simple, it's not sufficiently advanced.
Post 25 made on Tuesday April 21, 2020 at 08:20
SWOInstaller
Select Member
Joined:
Posts:
October 2010
1,596
On April 21, 2020 at 06:16, crosen said...
I’m not sure I follow this. Can you describe the proper protection that should be in place for, say, an outdoor speaker? Assume without protection you simply have a 14/2 cable running from the speaker back to an amplifier in a rack. What exactly would you put in place for proper surge protection and grounding of this speaker?

Many options have been provided to properly bond the speaker wire to the house.

internetraver provided a couple options Others have as well
Panamax has good options as well as Ubiquiti.

[Link: panamax.com]

[Link: ui.com]

What I was referring to and Buzz has re-iterated is that you don't want to just add a ground rod or use the pole the device is connected to as a grounding means. Ideally you should be pulling a bond wire to every external device. We don't work in an ideal world so companies like Panamax have provided solutions to help with this.

You want to ensure you are only providing one path to ground to help reduce the risk of equipment damage.
You can't fix stupid
OP | Post 26 made on Tuesday April 21, 2020 at 08:59
crosen
Senior Member
Joined:
Posts:
April 2009
1,262
Many options have been provided to properly bond the speaker wire to the house.

Let's use the Panamax as an example. The instructions say:

"If the cable has a shield or drain wire, connect it to the modules bonding-strap
connection located on the upper right portion of the module."

Let's say a drain wire is run from the speaker back to the module - what would it attach to at the speaker location?
If it's not simple, it's not sufficiently advanced.
Post 27 made on Tuesday April 21, 2020 at 10:29
SWOInstaller
Select Member
Joined:
Posts:
October 2010
1,596
On April 21, 2020 at 08:59, crosen said...
Let's use the Panamax as an example. The instructions say:

"If the cable has a shield or drain wire, connect it to the modules bonding-strap
connection located on the upper right portion of the module."

Let's say a drain wire is run from the speaker back to the module - what would it attach to at the speaker location?

The Metal bracket for the speaker (assuming a surface mount outdoor speaker). Using a spade/ring connector either tap a screw onto the speaker bracket or place it under the screw that secures the bracket to the house.

Edit* If you have a drain or bonding wire there really is no reason to use the Panamax device. Connect that wire to the bond screw in the equipment rack using a ring/spade connector. You are bonding your racks and equipment within the rack to the electrical ground?

Last edited by SWOInstaller on April 21, 2020 10:49.
You can't fix stupid
OP | Post 28 made on Tuesday April 21, 2020 at 12:53
crosen
Senior Member
Joined:
Posts:
April 2009
1,262
All low voltage cabling and services are supposed to be grounded and protected when they enter the structure.  This also means that low-voltage cable between a main house and a guest house needs to be grounded and protected when it enters BOTH structures.

It would seem to follow that all LV wire run from outside a structure needs to be shielded, correct? This makes me wonder why direct burial cabling seems so often to come without shielding? In fact, my main bulk cabling supplier does not even carry shielded direct burial category or speaker cabling.
If it's not simple, it's not sufficiently advanced.
Post 29 made on Tuesday April 21, 2020 at 13:31
Rob Grabon
Founding Member
Joined:
Posts:
November 2001
1,392
Frankly I would have my doubts that braided shielding (intended for noise rejection) would be able to carry any significant current and would most likely just vaporize close to the point of surge/lightning injection.
Technology is cheap, Time is expensive.
Post 30 made on Tuesday April 21, 2020 at 13:39
buzz
Super Member
Joined:
Posts:
May 2003
4,384
A shield for speaker wire would offer minimal protection from a nearby strike. Think of it as a high energy ground loop that will introduce a current in the protected wires anyway.
Find in this thread:
Page 2 of 4


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.