Residential smoke detector in a return air duct
This thread has 13 replies. Displaying all posts.
Post 1 made on Thursday January 16, 2020 at 16:41
Craig Aguiar-Winter
Senior Member
Joined:
Posts:
September 2002
1,489
Hey all.

I have rental property in Hamilton Ontario. It’s house which has had the basement converted to an appartment and I am going through the process of legalizing the appartment.

One of the things the city wants is a smoke detector in the cold air return which will shut off the gas supply to the furnace when activated.

Can anyone here direct me to a product I can use for this? I’ve looked through what my wholesalers have and as expected they are all meant to interface with a fire alarm panel, which this house doesn’t have. My thinking is that the relay contact would simply be used to interrupt the trigger that controls the gas valve.

For example: I see a System Sensor D4120 4 wire detector. 24v AC in could be powered by the furnace. It has 2 sets of Aux contacts with NC and NO contacts that could control the valve. No need for the alarm initiating circuit. Perhaps I could connect a local signalling circuit, like a buzzer and a light for example, so that if there is a false or malfunction the tenant will be alerted so I can get it serviced before it gets cold. Seems like it would work to me.

I’m not opposed to hiring a pro to install this if that prudent/required. However if it’s something I can do then obviously I’d like to save the money.

Thanks for your input. Any insight is appreciated.

Craig.
My wife says I can't do sarcasm. She says I just sound like an a$$hole.
Post 2 made on Thursday January 16, 2020 at 19:40
davidcasemore
Super Member
Joined:
Posts:
January 2003
3,352
Two things:

1. Are you sure they mean "shut off the gas supply", or do they mean "shut off the furnace". Shutting off the gas supply could mean installing a motorized valve prior to the furnace. Shutting off the furnace would be done by putting the contacts of the relay into the thermostat wiring. Usually, shutting off the furnace is the goal - this is to stop smokey air from being distributed throughout the house via the duct work. This method shuts down the blower motor - whether it's for heating, cooling or just fan mode.

2. I don't think a standard smoke detector is designed to be installed inside of duct work. System Sensor, and many others, make duct sensors designed for this purpose.


[Link: systemsensor.com]
Fins: Still Slamming' His Trunk on pilgrim's Small Weenie - One Trunk at a Time!
OP | Post 3 made on Thursday January 16, 2020 at 20:24
Craig Aguiar-Winter
Senior Member
Joined:
Posts:
September 2002
1,489
On January 16, 2020 at 19:40, davidcasemore said...
Two things:

1. Are you sure they mean "shut off the gas supply", or do they mean "shut off the furnace". Shutting off the gas supply could mean installing a motorized valve prior to the furnace. Shutting off the furnace would be done by putting the contacts of the relay into the thermostat wiring. Usually, shutting off the furnace is the goal - this is to stop smokey air from being distributed throughout the house via the duct work. This method shuts down the blower motor - whether it's for heating, cooling or just fan mode.

2. I don't think a standard smoke detector is designed to be installed inside of duct work. System Sensor, and many others, make duct sensors designed for this purpose.

[Link: systemsensor.com]

Thank you for your response. The detector you linked to is the same one I mentioned in my post so at least I’m on the right track!

You make an interesting point about the gas. I took the guys description to mean the gas but it would be better probably to shut the whole thing down. The furnace has an electronically controlled gas valve in it already which I figured I would be able to interrupt using it’s trigger wire. But your suggestion makes more sense to me as it would work, as you pointed out, during either the heating, cooling , or just fan modes.

Thanks again.

Craig.
My wife says I can't do sarcasm. She says I just sound like an a$$hole.
Post 4 made on Thursday January 16, 2020 at 22:02
alihashemi
Select Member
Joined:
Posts:
June 2006
1,891
Craig:

We usually use a SL-2000-N-C with the tube kit for this application and generally we use the relay to turn off the furnace to stop air flow altogether. This should also shutoff the gas valve inside the unit.

The one you linked to will work perfectly as well.
Ali Hashemi
OP | Post 5 made on Thursday January 16, 2020 at 22:28
Craig Aguiar-Winter
Senior Member
Joined:
Posts:
September 2002
1,489
On January 16, 2020 at 22:02, alihashemi said...
Craig:

We usually use a SL-2000-N-C with the tube kit for this application and generally we use the relay to turn off the furnace to stop air flow altogether. This should also shutoff the gas valve inside the unit.

The one you linked to will work perfectly as well.

Thank you!
My wife says I can't do sarcasm. She says I just sound like an a$$hole.
Post 6 made on Friday January 17, 2020 at 13:45
SWOInstaller
Select Member
Joined:
Posts:
October 2010
1,594
Craig,

Is there already interconnected smoke detectors in the house?

If so both First Alert (BRK) and Kidde make a relay that can be added to the smoke detectors that would allow you to wire it into the furnace switch or something else to turn off the furnace.

The First Alert/BRK relay part number is RM4 and the Kidde relay part number is SM120X.
You can't fix stupid
OP | Post 7 made on Friday January 17, 2020 at 19:47
Craig Aguiar-Winter
Senior Member
Joined:
Posts:
September 2002
1,489
On January 17, 2020 at 13:45, SWOInstaller said...
Craig,

Is there already interconnected smoke detectors in the house?

If so both First Alert (BRK) and Kidde make a relay that can be added to the smoke detectors that would allow you to wire it into the furnace switch or something else to turn off the furnace.

The First Alert/BRK relay part number is RM4 and the Kidde relay part number is SM120X.

This sounds like a great idea. I’m using Kidde alarms through out. Upstairs has 4 wireless interconnected and downstairs has 3 wires interconnected. They all communicate with each other. I’ll look into that!

Craig
My wife says I can't do sarcasm. She says I just sound like an a$$hole.
Post 8 made on Monday January 20, 2020 at 16:56
EXT
Founding Member
Joined:
Posts:
August 2001
134
Before you do anything, get the inspector to clarify exactly what they want, in writing, so that there is no confusion, and "I didn't mean that, you have to do it over" moments.

If they want to prevent smoke from being spread throughout the house, using a relay to interrupt the thermostat won't do it. If the furnace is on and producing heat, or if the fan is switched mechanicaly on to continuously supply air circulation, the fan will continue to operate at least until the furnace cools down, as either the mechanical switch or the high limit switch will keep power to the fan motor.

It would seem that the smoke detector relay would have to operate a 120 volt relay to cut power to the whole furnace, so that everything, including the fan is shut down when detecting smoke.
OP | Post 9 made on Monday January 20, 2020 at 19:01
Craig Aguiar-Winter
Senior Member
Joined:
Posts:
September 2002
1,489
On January 20, 2020 at 16:56, EXT said...
Before you do anything, get the inspector to clarify exactly what they want, in writing, so that there is no confusion, and "I didn't mean that, you have to do it over" moments.

If they want to prevent smoke from being spread throughout the house, using a relay to interrupt the thermostat won't do it. If the furnace is on and producing heat, or if the fan is switched mechanicaly on to continuously supply air circulation, the fan will continue to operate at least until the furnace cools down, as either the mechanical switch or the high limit switch will keep power to the fan motor.

It would seem that the smoke detector relay would have to operate a 120 volt relay to cut power to the whole furnace, so that everything, including the fan is shut down when detecting smoke.

I will definitely do as you suggest for the exact reason that I don’t want to do it twice. I’m just learning what my options are. I didn’t even know the smoke detector relay was available. It is intended to switch a 120v signal so interrupting the power to the furnace would seem to be the way to use that device. It could switch low voltage too but it doesn’t include any means to separate the two inside its box and I think the electrical inspector will likely have an issue with that.

Craig.
My wife says I can't do sarcasm. She says I just sound like an a$$hole.
Post 10 made on Monday January 20, 2020 at 22:45
para19
Long Time Member
Joined:
Posts:
December 2012
124
On January 17, 2020 at 13:45, SWOInstaller said...
Craig,

Is there already interconnected smoke detectors in the house?

If so both First Alert (BRK) and Kidde make a relay that can be added to the smoke detectors that would allow you to wire it into the furnace switch or something else to turn off the furnace.

The First Alert/BRK relay part number is RM4 and the Kidde relay part number is SM120X.

We are located in BC and are an electrical contractor as well.

We install these relays all the time to do just exactly what you described.

KIDDE SM120X - SMOKE RELAY

[Link: kidde.com]

They are certified to work with the following detectors...

KIDDE P1275CA - SMOKE DETECTOR WITH BACK UP BATTERY
KIDDE 900-0119 - SMOKE/CO WITH BACK UP BATTERY
There is always money in the banana stand...
OP | Post 11 made on Tuesday January 21, 2020 at 14:12
Craig Aguiar-Winter
Senior Member
Joined:
Posts:
September 2002
1,489
On January 20, 2020 at 22:45, para19 said...
We are located in BC and are an electrical contractor as well.

We install these relays all the time to do just exactly what you described.

KIDDE SM120X - SMOKE RELAY

[Link: kidde.com]

They are certified to work with the following detectors...

KIDDE P1275CA - SMOKE DETECTOR WITH BACK UP BATTERY
KIDDE 900-0119 - SMOKE/CO WITH BACK UP BATTERY

Thank you. It’s interesting that it’s certified with specific alarms. Would it not work with any that are interconnected? It doesn’t just receive a trigger from the red wire? Or do these alarms have a smoke only trigger option so that CO doesn’t shut down the furnace?
My wife says I can't do sarcasm. She says I just sound like an a$$hole.
Post 12 made on Tuesday January 21, 2020 at 16:50
para19
Long Time Member
Joined:
Posts:
December 2012
124
On January 21, 2020 at 14:12, Craig Aguiar-Winter said...
Thank you. It’s interesting that it’s certified with specific alarms. Would it not work with any that are interconnected? It doesn’t just receive a trigger from the red wire? Or do these alarms have a smoke only trigger option so that CO doesn’t shut down the furnace?

Those were only 2 examples of detectors it is compatible with.

The module is only activated by a smoke alarm interconnect signal.

see spec sheet below...

[Link: shareddocs.com]
There is always money in the banana stand...
Post 13 made on Wednesday January 22, 2020 at 06:45
Gman
Select Member
Joined:
Posts:
February 2009
2,244
We recently used the Kidde version for a smoke /CO setup to the alarm panel. Works great
OP | Post 14 made on Thursday January 23, 2020 at 23:50
Craig Aguiar-Winter
Senior Member
Joined:
Posts:
September 2002
1,489
On January 22, 2020 at 06:45, Gman said...
We recently used the Kidde version for a smoke /CO setup to the alarm panel. Works great

If the inspector allows me to I’ll use it for sure. It’s the easiest and cheapest way for me to do this. The ceiling is finished but the detector is in the same hoist space that goes to the furnace room, so it’s an easy fish right to the box with the furnace switch. I could have this done in 20 minutes.

Hopefully the inspector is on board.

Craig.
My wife says I can't do sarcasm. She says I just sound like an a$$hole.


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.