Basic Question About MOV Based Surge Protectors
This thread has 4 replies. Displaying all posts.
Post 1 made on Saturday August 3, 2019 at 09:07
crosen
Senior Member
Joined:
Posts:
April 2009
1,262
As I understand it, the MOVs on your typical surge protector continually degrade until the ability to absorb excess energy is no longer adequate. As such, you should replace surge protectors before the protection capability wears too low.

Well, if that's the case, then how is it that when you buy a surge protector from, say, Snap, there are no guidelines about when to replace it. In fact, there isn't even a mention of the fact that the protection degrades!?

And, since there is no visibility into the condition of the MOVs, how do you determine when to replace the surge protectors?

Also, if the surge capability degrades, then isn't IP controllable surge equipment a bad way to go? Shouldn't you instead use IP controllable outlet strips (and move the surge protection upstream of those strips), so that you don't need to replace the costly IP infrastructure when the protection degrades?
If it's not simple, it's not sufficiently advanced.
Post 2 made on Saturday August 3, 2019 at 09:21
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,324
On August 3, 2019 at 09:07, crosen said...
As I understand it, the MOVs on your typical surge protector continually degrade until the ability to absorb excess energy is no longer adequate. As such, you should replace surge protectors before the protection capability wears too low.

Well, if that's the case, then how is it that when you buy a surge protector from, say, Snap, there are no guidelines about when to replace it. In fact, there isn't even a mention of the fact that the protection degrades!?

And, since there is no visibility into the condition of the MOVs, how do you determine when to replace the surge protectors?

Also, if the surge capability degrades, then isn't IP controllable surge equipment a bad way to go? Shouldn't you instead use IP controllable outlet strips (and move the surge protection upstream of those strips), so that you don't need to replace the costly IP infrastructure when the protection degrades?

I'm not sure there's a way to estimate the life of this kind of device without knowing the quality of the power delivered. Most of what I have read recommends layers of protection, starting at the breaker panel with whole-building protection devices and then using something at the equipment, to catch surges that come from motors, switches and other sources IN the building.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 3 made on Saturday August 3, 2019 at 09:28
designed
Long Time Member
Joined:
Posts:
November 2012
296
Check out Surgex's booth at Cedia. They discuss exactly the problem you're talking about and why their equipment is better than MOV based protection.
Post 4 made on Sunday August 4, 2019 at 00:56
Brad Humphrey
Super Member
Joined:
Posts:
February 2004
2,603
Just to be clear, MOVs do not just degrade over time. They degrade when they handle a surge (when they conduct). Catastrophic failure of the MOV happens when the surge is more than its capacity.

It is impossible to know how much life a MOV has left in it. Many surge protectors have indicator lights, to let you know when the protection has failed. But an MOV based protector can be on the verge of failing (with little protection left in it) and that light will not be lit until it gets zapped for good.
OP | Post 5 made on Sunday August 4, 2019 at 07:26
crosen
Senior Member
Joined:
Posts:
April 2009
1,262
This seems like a significant shortcoming in our industry. You’d never think of installing expensive electronics without installing adequate surge protection, and yet it seems there are tons of projects out there with inadequate protection by virtue of having degraded MOVs.

I don’t get why this doesn’t get more attention in the trades, by vendors, in the forums, etc.

What are you all doing about this on your projects?
If it's not simple, it's not sufficiently advanced.


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.