Surge Protection for Power Amps
This thread has 70 replies. Displaying posts 1 through 15.
Post 1 made on Monday April 16, 2018 at 19:14
Krassyg
Long Time Member
Joined:
Posts:
April 2005
264
Curious what you guys use for surge protection on high current amps. Need to install a few Crown amps in a small hotel restaurant and I am hesitant to just plug them into the outlets. They are current models and should be more or less immune to surges but still.
Post 2 made on Monday April 16, 2018 at 19:35
lippavisual
Senior Member
Joined:
Posts:
December 2007
1,463
Furman or Surgex
Post 3 made on Monday April 16, 2018 at 19:39
ichbinbose
Select Member
Joined:
Posts:
August 2011
1,824
Surgex
OP | Post 4 made on Monday April 16, 2018 at 19:39
Krassyg
Long Time Member
Joined:
Posts:
April 2005
264
One per amp? I'll have about 4-5 separate amps.
Post 5 made on Monday April 16, 2018 at 20:01
Don Heany
Senior Member
Joined:
Posts:
September 2008
1,178
Go Torus if budget allows. Those clients are hard to find though.

[Link: toruspower.com]
Post 6 made on Monday April 16, 2018 at 22:17
vwpower44
Super Member
Joined:
Posts:
August 2004
3,662
Furman!
Stay Hungry, Stay Foolish...
Post 7 made on Tuesday April 17, 2018 at 08:23
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,322
On April 16, 2018 at 19:14, Krassyg said...
Curious what you guys use for surge protection on high current amps. Need to install a few Crown amps in a small hotel restaurant and I am hesitant to just plug them into the outlets. They are current models and should be more or less immune to surges but still.

Most power amps don't need it and many surge suppressors actually limit the peak current drawn by Class AB amps when they're operating at a high output level. Make sure whatever you use is able to handle what is being demanded. If the amps have a DSP, it's a different issue- most other amps aren't so delicate.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 8 made on Tuesday April 17, 2018 at 08:27
Fred Harding
Super Member
Joined:
Posts:
October 2001
3,460
Crown is very good at documenting current requirements, which makes doing power layouts a breeze. Strongly recommend Furman; it's what I use with my PA system, and what all my friends who run sound use.
On the West Coast of Wisconsin
Post 9 made on Tuesday April 17, 2018 at 08:48
buzz
Super Member
Joined:
Posts:
May 2003
4,376
On April 17, 2018 at 08:23, highfigh said...
Most power amps don't need it and many surge suppressors actually limit the peak current drawn by Class AB amps when they're operating at a high output level. Make sure whatever you use is able to handle what is being demanded. If the amps have a DSP, it's a different issue- most other amps aren't so delicate.

I agree.

The amp's power transformer and power supply are an effective suppressor. An amp with a separate, small power line line connected power supply for DSP or similar functions would be more vulnerable to transients when the main supply is turned OFF. A switch mode power supply would be slightly more vulnerable than the typical brute force analog supply.

It's a little over the top, but one approach might be to install a sub panel for the electronics (which might include computers and such) and use surge suppression on that panel as a sort of "first responder".

In this sort of environment, in addition to the risk from power grid transmitted transients, there will be some local transients created by the restaurant equipment power switching -- especially if the restaurant owner is a cheapskate.
Post 10 made on Tuesday April 17, 2018 at 08:57
radiorhea
Super Member
Joined:
Posts:
May 2002
3,264
I was a Furman guy for a loooonnnnggg time. After frequent electrical storms here, I switched to SurgeX. Have not lost anything since.
Drinking upstream from the herd since 1960
Post 11 made on Tuesday April 17, 2018 at 09:07
Mac Burks (39)
Elite Member
Joined:
Posts:
May 2007
17,518
We use crestron Sonnex for DA. Crown or Sonance for outdoor speakers and misc sub amps. I only route the master sonnex through racklink so that I can remotely power cycle it. All other amps are plugged directly into power. All rack power comes from a middle atlantic exact power rack.

The only amps I have replaced we're 15-20 years old. One was a bryston that just rotted into a puddle of brown goo inside. The other was an NAD amp in a theater that started having an issue with noise on one channel.
Avid Stamp Collector - I really love 39 Cent Stamps
Post 12 made on Tuesday April 17, 2018 at 09:16
buzz
Super Member
Joined:
Posts:
May 2003
4,376
Part of the "correct answer" depends on the locale. In a "lightning alley" sort of area one cannot get enough surge suppression. In other areas I don't get too excited about transients.

There can always be one off sorts of events. In my area there is a little two story supermarket structure that was nearly destroyed by a direct lightning strike. There were weeks of major repairs. This building is nestled in an area with several nearby high rise buildings and lots of three and four story homes. Visually scanning the area one would think that this was the least likely building to attract a strike. This is not a "lightning alley".
Post 13 made on Tuesday April 17, 2018 at 12:59
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
On April 17, 2018 at 08:48, buzz said...
In this sort of environment, in addition to the risk from power grid transmitted transients, there will be some local transients created by the restaurant equipment power switching -- especially if the restaurant owner is a cheapskate.

With this kind of situation, it might be good to think up a circular kind of argument for the customer. This is my first shot at it, just to get the idea across. I'm sure you can come up with something more convincing:

"Oops, I see you're having trouble approving the budget needed for sufficient surge protection on the power amps, where it's very necessary, which tells me that other decisions may have been made about "economy" with wiring and switching, decisions which almost PREDICT that there will be a need for better transient protection right at the components. In other words, I see a danger here that economic decisions might backfire on you. There is always a possibility that what experts call 'value engineering' might result in problems."
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 14 made on Tuesday April 17, 2018 at 16:53
g007
Long Time Member
Joined:
Posts:
October 2015
87
Krassyg

You do not have to guess, have someone come out and do a power quality test.

They will hookup a power quality monitoring device, Fluke, BMI and recommend a solution.

Their could be more severe problems that are not apparent.
Post 15 made on Tuesday April 17, 2018 at 17:01
g007
Long Time Member
Joined:
Posts:
October 2015
87
Krassyg

The ideas presented in the reply’s are noted and may get the job done, but.

They are suggestions based on assumptions!

We all know what happens when we assume!!
Find in this thread:
Page 1 of 5


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.