NEC, Slabs, Wet Locations
This thread has 14 replies. Displaying all posts.
Post 1 made on Monday September 18, 2017 at 17:06
PHSJason
Advanced Member
Joined:
Posts:
December 2002
994
Cross-post from IP
Would like to start a dialog about Code and performance requirements for cables installed in floor boxes or conduits encased in concrete. These are typically conference rooms with mics, data, HDMI, etc but are becoming more and more common as people finish basements, garages etc. This thread deals ONLY with concrete in direct contact with the ground(slab).

I ran into this a few weeks ago and thought I might be able to save some headache for someone else.
The install was an older building wired years ago by another LV company. Swapped a mixer and had noise from three mics that had cables running through conduit into floor boxes. Investigated and found water in the conduits. Electrician said ‘wet location, use the right cables’. Dug in and found the following:

From the NEC definition:
Location, Wet. Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.

By definition, this conduit and any boxes/conduits that any of us install in slabs are considered to be in a wet location.

NEC 300.5
(B) Wet Locations
The interior of enclosures or raceways installed underground shall be considered to be a wet location. Insulated conductors and cables installed in these enclosures or raceways in underground installations shall be listed for use in wet locations and shall comply with 310.10(C). Any connections or splices in an underground installation shall be approved for wet locations.
Also NEC 300.9 Raceways in Wet Locations Above
grade
. Where raceways are installed in wet locations above grade, the interior of these raceways shall be considered to be a wet location. Insulated conductors and cables installed in raceways in wet locations
above grade shall comply with 310.10(C).

NEC 310.10 (c) Wet Locations
Insulated conductors and cables used in wet locations shall comply with one of the following:
(1) Be moisture-impervious metal-sheathed.
(2) Be types MTW, RHW, RHW-2, TW, THW, THW-2, THHN, THWN, THWN-2, XHHW, XHHW-2, ZW
(3) Be of a type listed for use in wet locations.

Where this leads us is to the conclusion that any cables that we install in wet locations need to be rated for wet location use. This is where the discussion splits into legal versus operational.

Legal – Is this a correct interpretation of this rule? There are a lot of exclusions granted for communication cables, but none seem to trump the general location/rating issue. Most of the installation references in 700-800 point to Chapter 3 raceways.
There are some exclusions still on the books for POTS, but where does this leave Data, HDMI, VGA, Audio, HDBase-T, etc? What does the 2017 say? It appears that the reason this hasn’t been a big issue is that in a lot of cases, the low-voltage cables get installed in the conduits after final inspection has been completed and therefore the conduits get inspected, but not the cables that end up inside them.

Operational – Even if you can legally find an exclusion that allows you to get away with using a cable not rated for the application, is this doing your clients a big disservice? It is a fact of life that conduits and boxes in slabs will eventually have water in them. Cables sitting in water will fail eventually. Should we opt to take the high road on this issue and always install ‘wet-location rated’ cables any time that we run into a slab? Who is a good supplier for wet-location rated HDMI cables?
Post 2 made on Monday September 18, 2017 at 21:13
chris-L5S
Senior Member
Joined:
Posts:
August 2008
1,027
On September 18, 2017 at 17:06, PHSJason said...
Cross-post from IP

Operational – Even if you can legally find an exclusion that allows you to get away with using a cable not rated for the application, is this doing your clients a big disservice? It is a fact of life that conduits and boxes in slabs will eventually have water in them. Cables sitting in water will fail eventually. Should we opt to take the high road on this issue and always install ‘wet-location rated’ cables any time that we run into a slab? Who is a good supplier for wet-location rated HDMI cables?

It usually comes down to cost. What is your client willing to spend?

HDMI for wet locations, I would recommend direct burial Cat cable with extenders. If the customer says cost is too high, then give them what they want and have them sign a waiver that the cable is not rated for this enviorment.
Post 3 made on Tuesday September 19, 2017 at 00:25
Audiophiliac
Super Member
Joined:
Posts:
August 2006
3,311
How does water get in the conduit? Unglued or poorly glued junctions? Does the glue eventually fail? Is the glue permeable? Is the conduit permeable? I always assumed schedule 80 with properly glued junctions were water tight. Wrong?

We do not deal with this often so I am just throwing curiosity out there.
"When I eat, it is the food that is scared." - Ron Swanson
Post 4 made on Tuesday September 19, 2017 at 00:42
para19
Long Time Member
Joined:
Posts:
December 2012
124
On September 19, 2017 at 00:25, Audiophiliac said...
How does water get in the conduit? Unglued or poorly glued junctions? Does the glue eventually fail? Is the glue permeable? Is the conduit permeable? I always assumed schedule 80 with properly glued junctions were water tight. Wrong?

We do not deal with this often so I am just throwing curiosity out there.

Condensation...

Difference in temperature of the air in the conduit and the outside/inside wall of the conduit.
There is always money in the banana stand...
Post 5 made on Tuesday September 19, 2017 at 00:47
Audiophiliac
Super Member
Joined:
Posts:
August 2006
3,311
Oh duh. Must be late. :p
"When I eat, it is the food that is scared." - Ron Swanson
Post 6 made on Tuesday September 19, 2017 at 08:43
iimig
Senior Member
Joined:
Posts:
April 2011
1,154
See 800.47. The requirements that insulated conductors and cables in wet locations be listed for wet locations [310.10(C) do not apply to communications cables.

All of the cable types mentioned in article 310 are for power and light.

The way the NEC is written, the first 3 chapters set the groundwork for installation of any kind of cable or device, but anything specific to low voltage starts in chapter 8. (That is oversimplified but close enough)

Is it a good idea? Yes. Always practical, especially with preterminated HDMI? No
The less I say, the smarter I will appear
Post 7 made on Tuesday September 19, 2017 at 12:18
ericspencer
Active Member
Joined:
Posts:
December 2011
536
You do a huge disservice to your customer not using OSP cable in "wet locations" and buried conduit always becomes a wet location. Odds are you will not find any HDMI cable that will suffice. OSP rated Cat cables/fiber and extenders is the best option.
Not my circus, not my monkeys
OP | Post 8 made on Tuesday September 19, 2017 at 16:55
PHSJason
Advanced Member
Joined:
Posts:
December 2002
994
On September 19, 2017 at 08:43, iimig said...
See 800.47. The requirements that insulated conductors and cables in wet locations be listed for wet locations [310.10(C) do not apply to communications cables.

800.47 deals with underground cables entering into a building, 800.110 is for cables inside buildings.
800 Section V - Installation Methods Within Buildings
800.110 Raceways for Communication Wires and Cables
800.110(A) Types of Raceways
Communication wires and cables shall be permitted to be installed in any raceway that complies with either (A)(1) or (A)(2).
(1) Raceways recognized in Chapter 3
Communications wires and cables shall be permitted to be installed in any raceway included in Chapter 3. The raceways shall be installed in accordance with the requirements of Chapter 3.
(2) Other permitted raceways
Communications wires and cables shall be permitted to be installed in listed Plenum communication raceway, listed riser communication raceway, or listed general purpose communication raceway selected in accordance with the provisions of 800.113 and installed in accordance with 362.24 through 362.56, where the requirements applicable to electrical non-metallic tubing apply.
800.113 (A) Listing
Communication wires, cables, and raceways installed in buildings shall be listed.

I do not see anywhere other than 800.47 any exceptions that would allow for cables not 'wet-location' rated to be installed in conduit in a slab inside of a building. Quite the opposite as 800.113 (A) requires all communication cables installed inside of a building to be listed.
OP | Post 9 made on Tuesday September 19, 2017 at 17:00
PHSJason
Advanced Member
Joined:
Posts:
December 2002
994
On September 19, 2017 at 00:25, Audiophiliac said...
How does water get in the conduit? Unglued or poorly glued junctions? Does the glue eventually fail? Is the glue permeable? Is the conduit permeable? I always assumed schedule 80 with properly glued junctions were water tight. Wrong?

We do not deal with this often so I am just throwing curiosity out there.

We live in what is considered a 'desert' due to limited annual rainfall. In this last case, this was the amount of water that could be vacuumed out of a 1" conduit no more than 30' in length before it went up a wall.
[Link: photos.app.goo.gl]

As you can see, any cable that sits in this for a period of time will fail and they will look like this:
[Link: photos.app.goo.gl]


Edited to fix photos

Last edited by PHSJason on September 20, 2017 17:07.
Post 10 made on Tuesday September 19, 2017 at 17:13
iimig
Senior Member
Joined:
Posts:
April 2011
1,154
On September 19, 2017 at 16:55, PHSJason said...
800.47 deals with underground cables entering into a building, 800.110 is for cables inside buildings.

Somewhat true, but 800.47 explicitly says "underground communications wires" not only "cables entering buildings." It's not only what they say, but sometimes what they don't.

800 Section V - Installation Methods Within Buildings
800.110 Raceways for Communication Wires and Cables
800.110(A) Types of Raceways
Communication wires and cables shall be permitted to be installed in any raceway that complies with either (A)(1) or (A)(2).
(1) Raceways recognized in Chapter 3
Communications wires and cables shall be permitted to be installed in any raceway included in Chapter 3. The raceways shall be installed in accordance with the requirements of Chapter 3.
(2) Other permitted raceways
Communications wires and cables shall be permitted to be installed in listed Plenum communication raceway, listed riser communication raceway, or listed general purpose communication raceway selected in accordance with the provisions of 800.113 and installed in accordance with 362.24 through 362.56, where the requirements applicable to electrical non-metallic tubing apply.
800.113 (A) Listing
Communication wires, cables, and raceways installed in buildings shall be listed.

800.113(A) simply requires that they be listed. If it's a plenum, use plenum wire. If it's riser, use riser wire. 800.110 also indicates that communications wire *CAN* be installed into designated raceways. Not that they have to.
I do not see anywhere other than 800.47 any exceptions that would allow for cables not 'wet-location' rated to be installed in conduit in a slab inside of a building. Quite the opposite as 800.113 (A) requires all communication cables installed inside of a building to be listed.

There are only so many listings for Communications wire. Plenum, Riser, General Purpose. There is no provision for underground like other wire types. OSP or Outside Plant is a good idea but not required by any means.

I only know all this because a few years ago I did 432 classroom hours of training on the NEC and other NFPA publications for an Oregon Limited Energy A license.
The less I say, the smarter I will appear
OP | Post 11 made on Tuesday September 19, 2017 at 17:47
PHSJason
Advanced Member
Joined:
Posts:
December 2002
994
On September 19, 2017 at 17:13, iimig said...
Somewhat true, but 800.47 explicitly says "underground communications wires" not only "cables entering buildings." It's not only what they say, but sometimes what they don't.

I will have to agree to disagree. 800.110 fits better when dealing explicitly with cables inside of a building. In order for 800.47 to apply, the slab would have to be classified as 'underground' and not inside the building. If the slab is considered inside the building, then the exemption from 800.47 would not apply and the installation methods in chapter 3 would govern our conduits.

I only know all this because a few years ago I did 432 classroom hours of training on the NEC and other NFPA publications for an Oregon Limited Energy A license.

I did my OR LE years ago and while the classes teach a lot, there is always more to learn and not even the AHJ knows it all.
Post 12 made on Tuesday September 19, 2017 at 22:24
Ranger Home
Super Member
Joined:
Posts:
June 2007
3,486
On September 19, 2017 at 17:00, PHSJason said...
We live in what is considered a 'desert' due to limited annual rainfall. In this last case, this was the amount of water that could be vacuumed out of a 1" conduit no more than 30' in length before it went up a wall.



As you can see, any cable that sits in this for a period of time will fail and they will look like this:

i see no images or links but when i reply it appears something is attached to your post.
Post 13 made on Wednesday September 20, 2017 at 08:05
Mario
Loyal Member
Joined:
Posts:
November 2006
5,681
On September 19, 2017 at 00:25, Audiophiliac said...
How does water get in the conduit? ... Is the conduit permeable? I always assumed schedule 80 with properly glued junctions were water tight. Wrong?

PVC is not water permeable.
Schedule 10 is used for sprinklers all the time.
Schedule 80 is simply thicker, offering additional protections against damage.
Post 14 made on Wednesday September 20, 2017 at 08:07
Mario
Loyal Member
Joined:
Posts:
November 2006
5,681
Jason, your pics are not showing up on my computer.
Did you host them on Pakistani porn server that my host is blocking?
OP | Post 15 made on Wednesday September 20, 2017 at 17:05
PHSJason
Advanced Member
Joined:
Posts:
December 2002
994
On September 20, 2017 at 08:07, Mario said...
Jason, your pics are not showing up on my computer.
Did you host them on Pakistani porn server that my host is blocking?

If by Pakistani porn server, you mean Google photos, then yes. Yes I did host them there.....
Forgot that google photos always works for the owner of the photos, and others cannot view.


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.

Hosting Services by ipHouse