Inspector insists we hang wire bundle from wires supporting Tbar
This thread has 14 replies. Displaying all posts.
Post 1 made on Tuesday August 29, 2017 at 15:14
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
Not that I want to get into an argument with an electrical inspector...

But we're building out a restaurant, mindful of the one time recently when we attached and supported our cabling from the hanger wires installed for the Tbar. Low voltage is hardly ever paid any attention by any inspector, but the electrical inspector told us we had to separately support that wire bundle.

That makes sense. We did it.

In our latest buildout, we installed separate hanger wires from the ceiling and made a wire bundle path. The electrical inspector told us we'd have to move them and attach them to the Tbar grid support wires.

He went on to say that we could not make any penetrations in the ceiling. In this case that means about a half dozen ceiling-mount cameras can't be mounted as designed. Furthermore, he came up with a way that he said would be okay. I haven't talked in detail with my partner about this, but it was something about running the camera wires up through the Tbar grid bars. That can't happen because the connectors are larger than the width of the grid bars.

In the past we've been allowed to connect to Tbar hanger wires, but those were remodels and this is new construction.

Anybody ever been told to hang wire bundles from Tbar support wires?
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 2 made on Tuesday August 29, 2017 at 15:30
lippavisual
Senior Member
Joined:
Posts:
December 2007
1,463
Never been told to hang from existing TBar stringer supports, especially new construction. Have always been told to provide our own supports.

The only exception to that is a few existing construction projects where the drop ceiling was 15' below the ceiling deck, with no access to get that high without tearing down the drop ceiling. In this instance we used the Caddy J-hooks that have a clip pre-installed to slide them on to the stringer wire.
Post 3 made on Tuesday August 29, 2017 at 16:55
Rob Grabon
Founding Member
Joined:
Posts:
November 2001
1,392
Since the NEC 330-11 (2) states wiring is not to be attached to the ceiling support grid. We request written notice that you would like our cabling installed otherwise.
Technology is cheap, Time is expensive.
Post 4 made on Tuesday August 29, 2017 at 19:53
FreddyFreeloader
Super Member
Joined:
Posts:
April 2004
3,243
What the heck kind of cameras are you doing where the connector is already on the wire?
Post 5 made on Tuesday August 29, 2017 at 20:41
edizzle
Loyal Member
Joined:
Posts:
March 2005
5,916
On August 29, 2017 at 16:55, Rob Grabon said...
Since the NEC 330-11 (2) states wiring is not to be attached to the ceiling support grid. We request written notice that you would like our cabling installed otherwise.

BAM!!!
I love supporting product that supports me!
OP | Post 6 made on Wednesday August 30, 2017 at 11:46
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
On August 29, 2017 at 19:53, FreddyFreeloader said...
What the heck kind of cameras are you doing where the connector is already on the wire?

I think we're misunderstanding one another. My answer should make that obvious:

Every camera I've ever seen has connectors already on the wire. The wire that comes out of the back of the camera used to split into two wires, with a BNC on one wire and a power connector on the other wire. Newer cameras have a wire with an RJ-45 on it. Some of these cameras also have an additional wire, some of which end in bare pigtails.

What cameras do you use that DON'T have connectors on the wire, that have either blunt-cut wire or stripped ends on pigtails?
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
OP | Post 7 made on Wednesday August 30, 2017 at 11:55
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
Some clarification: the inspector thought there had been wires in place for us running from the 20 foot ceiling down to the grid structure, and it looked to him like we had cut off the connection down to the grid. So he ordered us to install, or in his eyes reinstall, the wires so they went all the way down to the grid. Maybe he thought we had reduced the support for the tbar. Who knows what evil lurks in the mind of the AHJ?

He totally missed the somewhat obvious fact that the exact wires he was complaining about didn't come from the ceiling, but from support bars under A/C ducting.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 8 made on Wednesday August 30, 2017 at 15:23
Neurorad
Super Member
Joined:
Posts:
September 2007
3,011
"Wire clip" or "wire mount" j-hook





TB A+ Partner
Believe nothing, no matter where you read it, or who said it, no matter if I have said it, unless it agrees with your own reason and your own common sense. -Buddha
OP | Post 9 made on Thursday August 31, 2017 at 12:19
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
Yes, that exact product, but now I see I missed something obvious.

We've been told not to use these hangers on Tbar support wires. Those wires are identical to the ones shown in the photo, running from ceiling to grid structure.

Instead, we're to add our own support wires from the ceiling, but the bottoms of those wires have to end up somewhere... which would have to be at the grid. That also would look just like the wires in the photo. So how would anyone know if the wires we attach to were put in to support the grid or to support our cables?
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 10 made on Thursday August 31, 2017 at 16:21
edizzle
Loyal Member
Joined:
Posts:
March 2005
5,916
the bottoms of the wires DO NOT have to end anywhere. they just hang.
I love supporting product that supports me!
Post 11 made on Thursday August 31, 2017 at 18:32
ShaferCustoms
Long Time Member
Joined:
Posts:
March 2014
380
On August 31, 2017 at 16:21, edizzle said...
the bottoms of the wires DO NOT have to end anywhere. they just hang.

I believe an up to date NEC code book and a BICSI manual could be handy here.

I'm not going to go look it up

Yet, at some point, and/or due to design

The ceiling support wires where not supposed to be used for ANYTHING except for supporting the ceiling grid.

If/when you add your own support wires, they must be attached to the grid.

There are points of attachment meant to support the grid only

I believe the reason you attach yours, is so that it's not swinging around up there and designates it as a "wire" support.
Post 12 made on Thursday August 31, 2017 at 18:58
Audiophiliac
Super Member
Joined:
Posts:
August 2006
3,311
Wait until inspector gadget leaves and do your thing......whatever your thing normally is.
"When I eat, it is the food that is scared." - Ron Swanson
Post 13 made on Friday September 1, 2017 at 15:02
ericspencer
Active Member
Joined:
Posts:
December 2011
536
300.11 Securing and Supporting.
(A) Secured in Place. Raceways, cable assemblies, boxes, cabinets, and fittings shall be securely fastened
in place. Support wires that do not provide secure support shall not be permitted as the sole support. Support wires and associated fittings that provide secure support and that are installed in addition to the ceiling grid support wires shall be permitted as the sole support. Where independent support wires are used, they shall be secured at both ends. Cables and race ways shall not be supported by ceiling grids.
Not my circus, not my monkeys
Post 14 made on Saturday September 2, 2017 at 09:41
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,322
On August 31, 2017 at 16:21, edizzle said...
the bottoms of the wires DO NOT have to end anywhere. they just hang.

Aw, now you've done it! He's gonna be forced to explain that if they don't end somewhere, they'll each go on forever.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 15 made on Saturday September 2, 2017 at 09:42
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,322
On August 31, 2017 at 12:19, Ernie Gilman said...
So how would anyone know if the wires we attach to were put in to support the grid or to support our cables?

You could put some kind of tag on them, paint the ends, etc.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.

Hosting Services by ipHouse