SOLVED! URC THZ-100 Thermostat Heat Cycle: Blower High Side when burner ignites
This thread has 8 replies. Displaying all posts.
Post 1 made on Monday November 14, 2016 at 22:30
FreddyFreeloader
Super Member
Joined:
Posts:
April 2004
3,243
But it's not supposed to. Burner is supposed to light for a minute or so then the furnace itself turns the blower onto low. Instead it appears that when the tstat turns heat on both the Y (Blower high speed) and W (Gas valve) contacts get closed to the common and it should just be W closing to C.

This is a single stage system at my own house. Two actual industry guys say it's hooked up right but that all thermostats have a dip switch or jumper on the back to designate electric or gas heat (fan goes on high same time on electric to keep heating element from self-destructing). But I cant find any switch on it or in the manual and support doesn't seem to understand the real world side.

In TC programming there are lots of settings but nothing that seems to apply. There is a choice for system type but gas and electric are within the same choice.

Last edited by FreddyFreeloader on November 17, 2016 23:39.
Post 2 made on Tuesday November 15, 2016 at 01:12
Daniel Tonks
Wrangler of Remotes
Joined:
Posts:
October 1998
28,780
Interesting - I don't see any signs of this being a setting choice. I guess they just didn't see the issue with a bit of cold air coming out the vents.

Seems like it would be an easy firmware change to implement, though.
OP | Post 3 made on Wednesday November 16, 2016 at 23:49
FreddyFreeloader
Super Member
Joined:
Posts:
April 2004
3,243
I got the case escilated and turns out it's just made that way and no way to change it. Fascinating the product has been out this long and this is the first time it has seemed come up.

The other thing other than cold air at first is that with gas heat the blower is supposed to run on low. The THZ was making it run on high which is actually counterproductive as far as efficiency.
OP | Post 4 made on Thursday November 17, 2016 at 23:36
FreddyFreeloader
Super Member
Joined:
Posts:
April 2004
3,243
Great news I fingered it out. I had all but given up, started thinking about just using it downstairs where we have some radiant floor heat, and it occurred to me....
Simply lie to Accelerator and tell it you have RADIANT HEAT. With radiant there is no fan so the stat behaves the way it does with gas and does not turn the fan on for heat, just the burner. The burner tells the fan when to come on not the stat.

Downloaded to the MRX and checked everything w/ a meter first and it works perfectly. A simple relabeling of the Accelerator dropdown choice would clear this up, but again, truly amazed to be the first person in the world to be aware this even happens. Other than that awesome piece!
Post 5 made on Sunday November 20, 2016 at 10:33
Ranger Home
Super Member
Joined:
Posts:
June 2007
3,486
Its because you are the only person in the world using that thermostat!? :)
Post 6 made on Sunday November 20, 2016 at 10:37
King of typos
Loyal Member
Joined:
Posts:
June 2002
5,280
Nope, the only person in the world who has brains to pay attention to the cold air coming through the vents. And knowing that, that isn't correct.

Great job in out tricking the high tech thermostat.

KOT
Post 7 made on Sunday November 20, 2016 at 13:13
kgossen
Super Member
Joined:
Posts:
March 2008
3,026
On 1479656249, King of typos said...
Great job in out tricking the high tech thermostat.

KOT

Calling a thermostat high tech that can't do what a $50 Home Depot one will is a bit of a stretch. It is a URC so to be expected.
"Quality isn't expensive, it's Priceless!"
OP | Post 8 made on Sunday November 20, 2016 at 18:46
FreddyFreeloader
Super Member
Joined:
Posts:
April 2004
3,243
On November 20, 2016 at 13:13, kgossen said...
Calling a thermostat high tech that can't do what a $50 Home Depot one will is a bit of a stretch. It is a URC so to be expected.

I've pretty much figured out that none are really too high tech. They're pretty much a relay with three to five contacts that close under whatever conditions. I do try to stay away from the mainstream cloud based stuff when possible so when you check this status on any of the other interfaces you pretty much get an instant readout
OP | Post 9 made on Sunday November 20, 2016 at 18:51
FreddyFreeloader
Super Member
Joined:
Posts:
April 2004
3,243
...


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.