Post 16 made on Thursday January 14, 2016 at 20:06
Fiasco
Senior Member
Joined:
Posts:
July 2009
1,282
On January 14, 2016 at 19:13, goldenzrule said...
What would you suggest as the best course of action?

Depends upon where the switch is located. If it's in mechanical space, install a contactor. They are inexpensive and easy to install.

If it's in a finished wall, change the bulbs.
Pump House on Facebook: [Link: facebook.com]
Post 17 made on Thursday January 14, 2016 at 20:14
Fiasco
Senior Member
Joined:
Posts:
July 2009
1,282
On January 14, 2016 at 19:23, fcwilt said...
- Why a contactor as a practical matter?

It's a practical matter because of the cost vs benefits. Contactors are cheap and easy to install. Contactors should be standard practice in all your future new construction (or retro upgrades where it can be installed without tearing into finished surfaces) for exterior lighting loads that are switched, have the chance of being extended or have the potential to take in water.


I've lived in/worked on homes for 40+ years that had dimmers on outside circuits and never had an issue that would suggest a contactor as being required.

In 40 years of working in homes you have never seen a dimming circuit with a contactor because you can't dim a contactor. It's either on or off.

Outside circuits are going to be GFI protected so water getting in is going to trip that.

Where's the GFI protection? If it's holiday receptacles, it's at the receptacle. If it's lighting it's at the panel behind the 8ANS which will fry before the GFI trips.

- Increasing the load outside of spec can happen on any circuit inside or out.

Increasing the load outside of spec can happen, which is why you use a contactor. Just as long as the load is within the spec of the contactor/conductors/breaker it's no worry. Even if the load goes over spec, the 8ANS is protected and the service call is for line voltage and not low voltage. And, even then, the replacement part is a $30 contactor, not a $100 switch.

If you found a fixture or circuit carrying too much load because the wrong bulbs were installed would you not change them simply because somebody else, at some future time, might change them again?

And what you describe is exactly why changing the bulbs is not a permanent solution, whereas a contactor is. I would fix it correctly the first time so I don't have to roll a truck on a service call down the road if someone changes the light bulbs.

Last edited by Fiasco on January 14, 2016 20:23.
Pump House on Facebook: [Link: facebook.com]
OP | Post 18 made on Thursday January 14, 2016 at 20:40
goldenzrule
Loyal Member
Joined:
Posts:
July 2007
8,474
On January 14, 2016 at 20:06, Fiasco said...
Depends upon where the switch is located. If it's in mechanical space, install a contactor. They are inexpensive and easy to install.

If it's in a finished wall, change the bulbs.

Finished wall. Switch is by the front door in a 3 gang box with 2 other switches.
Post 19 made on Thursday January 14, 2016 at 20:50
Fiasco
Senior Member
Joined:
Posts:
July 2009
1,282
Where is the switch in the gangbox? You have to de-rate the load the switch can handle because it is ganged.

The 8ANS can handle 6 amps non-ganged. It can do 5 at the end of a gangbox and only 3.5 in the middle.

Pull the switch and throw a clamp on ampmeter on it to see what it is pulling under load.

If it is in the middle and pulling 5 amps or less, get a new 8ANS and move it to the end of the gangbox (you broke off the cooling tabs to put it in the middle).

If its over 5 amps and all of the loads are incadescent dimmable (not magnetic low voltage) you can put in a RRD-10ND which can handle 800 watts on the end of a gangbox and 650 watts in the middle.

If it's over that, the RRD-8S-DV switch can handle 8 amps on the end of a gangbox and 7 amps in the middle.

Last edited by Fiasco on January 14, 2016 21:02.
Pump House on Facebook: [Link: facebook.com]
Post 20 made on Thursday January 14, 2016 at 20:57
Mario
Loyal Member
Joined:
Posts:
November 2006
5,681
Doesn't Luton make appliance switch or relay switch?
That would be rated at 15Amps.
Post 21 made on Thursday January 14, 2016 at 21:16
Trunk-Slammer -Supreme
Loyal Member
Joined:
Posts:
November 2003
7,462
On January 14, 2016 at 20:01, goldenzrule said...
Existing, meaning the non Ra2 switch that was in place beforehand? BTW, I removed the ra2 switch for now and put the old one back that thankfully the electrician left. I couldn't reach him before leaving and did not feel comfortable leaving it in that state.

Existing meaning the Ra2.


You put it back to a standard switch it should cause no problems since that basic switch will handle the load.


As others have mentioned, a contactor is a good choice, but is there any possibility of access to the wiring?
Post 22 made on Thursday January 14, 2016 at 21:20
Fiasco
Senior Member
Joined:
Posts:
July 2009
1,282
On January 14, 2016 at 21:16, Trunk-Slammer -Supreme said...
Existing meaning the Ra2.

You put it back to a standard switch it should cause no problems since that basic switch will handle the load.

As others have mentioned, a contactor is a good choice, but is there any possibility of access to the wiring?

I think after he throws a clamp meter on it a DV will handle the load. I would think the 8ANS would be shutting completely down to overheat if the load was higher then the DV could do.
Pump House on Facebook: [Link: facebook.com]
Post 23 made on Thursday January 14, 2016 at 21:21
Fiasco
Senior Member
Joined:
Posts:
July 2009
1,282
On January 14, 2016 at 20:57, Mario said...
Doesn't Luton make appliance switch or relay switch?
That would be rated at 15Amps.

The appliance switch is a corded plugin module.

Pump House on Facebook: [Link: facebook.com]
Post 24 made on Friday January 15, 2016 at 02:09
drewski300
Super Member
Joined:
Posts:
January 2007
3,849
You guys all have the tools to monitor RF spectrum, HDMI connectivity, network connectivity, etc, etc, etc. Go buy a meter with an amp clamp like [Link: amazon.com]. Pull the switch out of the wall, turn it on, and clamp the meter around the load wire with the switch turned on. If the running amps are over 8, you should figure out a different solution (like the contactor mentioned). The switch will heat up significantly because if it's pushing 8 amps through it much like a dimmer is only listed for 600 watts or 1000 watts.

The landscape lights are likely fed from a 12v transformer(s).

*As listed, if the switch is running a motor, fountain pump, etc. over 5.8A, then you should figure out a different solution.
**If the switch is ganged with other switches, the rated is less as well.
"Just when I thought you couldn't possibly be any dumber, you go and do something like this... and totally redeem yourself!"
Post 25 made on Friday January 15, 2016 at 02:34
Mario
Loyal Member
Joined:
Posts:
November 2006
5,681
On January 15, 2016 at 02:09, drewski300 said...
You guys all have the tools to monitor RF spectrum, HDMI connectivity, network connectivity, etc, etc, etc. Go buy a meter with an amp clamp like [Link: amazon.com]. Pull the switch out of the wall, turn it on, and clamp the meter around the load wire with the switch turned on. If the running amps are over 8, you should figure out a different solution (like the contactor mentioned). The switch will heat up significantly because if it's pushing 8 amps through it much like a dimmer is only listed for 600 watts or 1000 watts.

The landscape lights are likely fed from a 12v transformer(s).

*As listed, if the switch is running a motor, fountain pump, etc. over 5.8A, then you should figure out a different solution.
**If the switch is ganged with other switches, the rated is less as well.

Nah, that's too much money.
All you need is 12-15 bucks
[Link: m.harborfreight.com]
Post 26 made on Friday January 15, 2016 at 06:46
Don Heany
Senior Member
Joined:
Posts:
September 2008
1,178
This- [Link: lutron.com]

Edit- they have a switched version....
Post 27 made on Friday January 15, 2016 at 08:37
fcwilt
Senior Member
Joined:
Posts:
September 2003
1,283
On January 14, 2016 at 20:14, Fiasco said...
It's a practical matter because of the cost vs benefits. Contactors are cheap and easy to install. Contactors should be standard practice in all your future new construction (or retro upgrades where it can be installed without tearing into finished surfaces) for exterior lighting loads that are switched, have the chance of being extended or have the potential to take in water.

In 40 years of working in homes you have never seen a dimming circuit with a contactor because you can't dim a contactor. It's either on or off.

Where's the GFI protection? If it's holiday receptacles, it's at the receptacle. If it's lighting it's at the panel behind the 8ANS which will fry before the GFI trips.

Increasing the load outside of spec can happen, which is why you use a contactor. Just as long as the load is within the spec of the contactor/conductors/breaker it's no worry. Even if the load goes over spec, the 8ANS is protected and the service call is for line voltage and not low voltage. And, even then, the replacement part is a $30 contactor, not a $100 switch.

And what you describe is exactly why changing the bulbs is not a permanent solution, whereas a contactor is. I would fix it correctly the first time so I don't have to roll a truck on a service call down the road if someone changes the light bulbs.

Well you make some interesting points but I do not agree with your conclusions.

For one I never said anyone was trying to dim a contactor.

And the GFI will trip long before the dimmer will fry.

But your entitled to your opinions and as long as you meet code then do whatever you like.
Regards, Frederick C. Wilt
Post 28 made on Friday January 15, 2016 at 12:28
Fiasco
Senior Member
Joined:
Posts:
July 2009
1,282
On January 15, 2016 at 08:37, fcwilt said...
Well you make some interesting points but I do not agree with your conclusions.

For one I never said anyone was trying to dim a contactor.

And the GFI will trip long before the dimmer will fry.

But your entitled to your opinions and as long as you meet code then do whatever you like.

How about this. *why not* use a contactor for outside switched loads in new construction or where it's feasible to do it in a remodel?
Pump House on Facebook: [Link: facebook.com]
Post 29 made on Friday January 15, 2016 at 13:09
fcwilt
Senior Member
Joined:
Posts:
September 2003
1,283
On January 15, 2016 at 12:28, Fiasco said...
How about this. *why not* use a contactor for outside switched loads in new construction or where it's feasible to do it in a remodel?

At least a couple of reasons.

- your solving a problem that my experience says does not exist.

- lots of customers like being able to dim outside lights.

Have you had any issues with inspectors not being sure if it meets code or not?

Have you had any issues with the contactor not meeting the minimum load requirements of the controlling device?
Regards, Frederick C. Wilt
Post 30 made on Friday January 15, 2016 at 18:28
Trunk-Slammer -Supreme
Loyal Member
Joined:
Posts:
November 2003
7,462
On January 15, 2016 at 13:09, fcwilt said...
- lots of customers like being able to dim outside lights.

Really?


I find that very surprising. I would think it's more like "I had ONE client that wanted to dim the outside lights for some reason no one could understand.".
Page 2 of 3


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.