Post 16 made on Monday March 23, 2015 at 05:53
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
Schlepp, I asked you to explain how the guy was shocked. You did not do it.

Think, in other words, and explain the shock. Explain where the power came from, how it got to him, and how it got to ground. Draw yourself a schematic. I don't think you can. Telling me to think about a neutral is no answer.

On March 22, 2015 at 20:15, Neurorad said...
I'll mention I that guy in the shower was shocked because the house was grounded think.

Thanks. It make sense now.
That guy was probably shocked because the house was properly grounded to a cold water pipe.

This is what Schlepp is missing. A guy who gets shocked while he's in the shower is in contact with a cold water pipe and a drain. This has tiny percentages of zero to do with any neutral in the house unless the shower wall has an open junction box in it. Unlikely but possible. My son just uncovered a bathroom light fixture that switches the neutral to turn it on and off. Bad idea but doesn't influence his shower experiences. (The switch and all other lighting circuitry is not in the shower.)

On March 22, 2015 at 20:57, King of typos said...
And probably had galvanized pipes for the drain. Thus why he had a shocking experience in the shower. Still points to an improper ground, as the drain pipes should have been grounded with the cold/hot water pipes as well.

Two times now someone mentions galvanized pipes. Why? They don't conduct quite as well as copper, so an electrically hot pipe would be more of a problem if it were copper, but galvanized is being blamed for something. Somehow.

If the drain pipes were PVC or ABS or whatever they use now a days, the cold/hot water pipes that became electrically hot, wouldn't have affected him at all. Unless the water acted as the "ground". But even on a first floor house, that pipe has to go down a foot or two, to which point there won't be a continuos stream of water to reach the ground.

This is mostly valid. Distilled water doesn't conduct electricity, but water with minerals may. Water with soap may. And that drop of a foot or two will probably have electrical paths that come and go as the water flows down the pipe.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
OP | Post 17 made on Monday March 23, 2015 at 07:33
King of typos
Loyal Member
Joined:
Posts:
June 2002
5,279
Copper pipe for the hot and cold and galvanized for the drain.

The hot and cold are more than likely bonded to ground. The galvanized drain is not. So where the drain pipe goes out of the house is far from the ground rod for the house. Thus a potential voltage difference.

To explain voltage in the ground with a different senairo. Picture a circuit going out to power a light pole for a house. It's a direct burial wire, so it's more acceptable to damage. The home owner is complaining that the light will some times dim, go out, come back on and dim again. Ok, so there must be a break that is making and losing contact. There's also snow on the ground. But about 13 feet from the light pole, there's a spot where there's no snow. Dig there and there is the break in the wire.

Question is, why was there no snow there? Because voltage was leaking into the ground and the ground basically became a "dirty" heated blanket.

KOT
Post 18 made on Monday March 23, 2015 at 12:40
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,321
My parent's garage was wired by a friend, who was an EE. The lawn care guys refused to plug anything into the outlet on the garage because they were shocked many times but I was never able to repeat the problem when I would go there. Turns out, the problem was caused by the way EE wired the three-way switch for the light for the end of the sidewalk, at the alley- he was switching the neutral and the metal J-box was mounted over aluminum siding. Flip the switches one way, it was fine and the other, ZZZZZZZZZZZZZZZZZ! I found this by closing the aluminum-framed jalousy window when I was barefoot and at that time, I understood EXACTLY why they didn't use that outlet. Never blew a breaker, either.

If nobody has ever had the same problem in that area, I would say it was caused by someone working their magic when they added/changed wiring in that house.

Last edited by highfigh on March 23, 2015 12:51.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 19 made on Monday March 23, 2015 at 17:02
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
On March 22, 2015 at 16:56, schlepp571 said...
I would look at an open neutral before I made that broad statement. I didn't mean to chuck insults Ernie :). Just an EE trying to be rational. Sorry I got you wound up.

On March 23, 2015 at 12:40, highfigh said...
My parent's garage was wired by a friend, who was an EE.

If schlepp had come up with an explanation for the guy's shock, I would not be saying this, but now I have to: with this post I rest my case.

Here we have two EEs trying to be rational. One won't use his extensive knowledge to show me how and where my explanation is wrong, by providing one of his own. The other one hooks up a switch in a completely dumb and incidentally possibly fatal manner.

schlepp, I'm not trying to wind you up. I'm trying to get you to explain in detail what is wrong with my explanation, which you totally reject.
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 20 made on Tuesday March 24, 2015 at 12:42
tomciara
Loyal Member
Joined:
Posts:
May 2002
7,962
Not disputing the "switching neutral" comments, but I would only mention 1) Sometimes a white gets used for a switch leg in a 3-way if no 14/3 has been run but is not the neutral; 2) Sometimes a back-fed circuit uses a white for a switch leg but again, is not the neutral.

Closer inspection may have proved neutral is indeed being switched, but all I am saying is that just because it is white does not guarantee it is a neutral.
There is no truth anymore. Only assertions. The internet world has no interest in truth, only vindication for preconceived assumptions.
Post 21 made on Tuesday March 24, 2015 at 15:12
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
I'm just baffled. A power line hits the ground. A guy gets a shock in his shower. A cable box burns up and starts a fire.

How is that in any way related to switching a neutral? Was the neutral in the shower?
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
Post 22 made on Tuesday March 24, 2015 at 15:53
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,321
We don't have enough info to determine what caused him to be shocked and the cook the cable box. All we can do is speculate.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 23 made on Tuesday March 24, 2015 at 15:54
BrettLee3232
Long Time Member
Joined:
Posts:
December 2009
423
That's why I always pound in a grounded near every rack lol
Knowing that Gold went up a few K makes me think "well now I have to do a better job on selling more equipment".

-Me... Jan. 2014
Post 24 made on Tuesday March 24, 2015 at 16:26
Hi-FiGuy
Super Member
Joined:
Posts:
January 2004
2,836
On March 22, 2015 at 09:18, Nded said...
What really drives us crazy is when we are able to determine beyond a doubt that the reason for a problem is improper grounding of the rack, and the custom installer thinks we are just blowing smoke. Eventually we are able to persuade them to try grounding the rack, and the problem goes away like magic. I am just amazed how many installers don't learn some of the fundamentals of electricity and electronics.

By the way, if you are reading this, then you are probably not one of the installers that doesn't get grounding.

Ok then what is the proper way to ground a rack?

Do you agree with this link [Link: engineereducators.com]
Post 25 made on Tuesday March 24, 2015 at 16:32
Mr. Stanley
Elite Member
Joined:
Posts:
January 2006
16,954
This is all very shocking...
"If it keeps up, man will atrophy all his limbs but the push-button finger."
Frank Lloyd Wright
Post 26 made on Tuesday March 24, 2015 at 16:46
Neurorad
Super Member
Joined:
Posts:
September 2007
3,011
Middle Atlantic has a great Power Paper which covers the proper way to ground a rack. I've seen this posted here before, not new to most here.

[Link: middleatlantic.com]
TB A+ Partner
Believe nothing, no matter where you read it, or who said it, no matter if I have said it, unless it agrees with your own reason and your own common sense. -Buddha
Post 27 made on Tuesday March 24, 2015 at 18:53
Mr. Stanley
Elite Member
Joined:
Posts:
January 2006
16,954
I saw a video the other day with two blacks and a white in a 3 - way.
"If it keeps up, man will atrophy all his limbs but the push-button finger."
Frank Lloyd Wright
Post 28 made on Tuesday March 24, 2015 at 19:54
Hi-FiGuy
Super Member
Joined:
Posts:
January 2004
2,836
On March 24, 2015 at 16:46, Neurorad said...
Middle Atlantic has a great Power Paper which covers the proper way to ground a rack. I've seen this posted here before, not new to most here.

[Link: middleatlantic.com]

Thank you, forgot about their white papers.
Post 29 made on Tuesday March 24, 2015 at 20:04
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,321
On March 24, 2015 at 15:54, BrettLee3232 said...
That's why I always pound in a grounded near every rack lol

So, you add a ground that could possibly cause ground loops, assuming the house' wiring already meets NEC? The rack is supposed to be grounded to the main ground point, not your own. It may work, but.....
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 30 made on Tuesday March 24, 2015 at 20:05
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,321
On March 24, 2015 at 18:53, Mr. Stanley said...
I saw a video the other day with two blacks and a white in a 3 - way.

Was one of them wearing a piece of tape, with a different color? That was probably the traveler.

At least, I think that's what they call the odd one.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Page 2 of 3


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.