This thread has 29 replies. Displaying posts 16 through 30.
Post 16 made on Thursday December 11, 2014 at 18:51
FP Crazy
Super Member
Joined:
Posts:
June 2003
2,940
On December 11, 2014 at 13:03, buzz said...
In one house I found the cable "ground" connected to an isolated one foot section of copper water pipe. I guess someone followed the directions literally -- "Connect ground terminal to copper water pipe."

Was there water in the pipe? If so, it was probably a relatively low resistance ground to mother earth, unless the pipe had no water in it.

Not suggesting it is ideal though
Chasing Ernie's post count, one useless post at a time.
OP | Post 17 made on Thursday December 11, 2014 at 20:31
FreddyFreeloader
Super Member
Joined:
Posts:
April 2004
3,243
On December 11, 2014 at 10:56, Ernie Gilman said...
While this should not be a problem, you also should not have hum, so look into things that should not be problems!

Yes, there's no hum when the rack is powered by the outlet next to the rack without the UPS. It does, however, hum obnoxiously when plugged into outlet in other room.

So you didn't unplug the video components, such as your satellite receiver, cable box, DVD, game, Roku, etc.? Just the CD player and the dual cassette? An actual list of what you've got, plus a list of what's not in the same room, might be helpful.

I did try unplugging everything but power to the preamp and amp, started adding things one at a time, power first (DirecTv AV genie then Oppo blu ray, PS3 and finally a Denon AVR for Zone 2.). As soon as I start connecting HDMI cables the buzz starts. The Denon seems to add the most.

Well, yes. But when you connected to power in the other room, was ANYTHING else in the system connected to power? From what you've described so far, you have a projector and a system in one room with no leads running to any other room at all; it's important to know about that. This latest hum source seems to be interaction between the ground in that other room and some other ground the equipment is connected to... but you haven't actually described all the wiring.

The rack has a dedicated 20A circuit. Everything including the projector is powered from the rack. The "other room" is really just the hallway which is on some other electrical circuit which may include some incandescent lights, but that's about it. There is nothing else running besides furnace and it's on it's own circuit.

Agreed, Looks like I should look a little closer at the house wiring. No reason the system should have a problem ANY circuit if it doesn't have a problem on one.
Post 18 made on Thursday December 11, 2014 at 21:13
Ranger Home
Super Member
Joined:
Posts:
June 2007
3,486
On December 11, 2014 at 11:36, sofa_king_CI said...
Have you tried Fedex instead ;)

hahahahaha
Post 19 made on Friday December 12, 2014 at 00:01
King of typos
Loyal Member
Joined:
Posts:
June 2002
5,279
Since you are dealing with an ups. Have you tried with it unplugged from the outlet? So that the UPS is providing a "clean" source of power? When the UPS is powering the system, does the hum still sound?

KOT
OP | Post 20 made on Friday December 12, 2014 at 00:05
FreddyFreeloader
Super Member
Joined:
Posts:
April 2004
3,243
On December 12, 2014 at 00:01, King of typos said...
Since you are dealing with an ups. Have you tried with it unplugged from the outlet? So that the UPS is providing a "clean" source of power? When the UPS is powering the system, does the hum still sound?

KOT

Oh my... never considered that, great idea.

On December 11, 2014 at 11:36, sofa_king_CI said...
Have you tried Fedex instead ;)

Good one, but what's funnier is...

On December 11, 2014 at 04:00, buzz said...
I always start tracing hum problems by disconnecting the cable or satellite feed. Chronically, these systems are improperly grounded.

Great advice Buzz, but your not welcome here.
Post 21 made on Friday December 12, 2014 at 00:13
edizzle
Loyal Member
Joined:
Posts:
March 2005
5,916
try swapping the breaker in the electrical panel to the opposit phase. this should be easily accomplished as long as the panel is not full.
I love supporting product that supports me!
Post 22 made on Friday December 12, 2014 at 01:40
King of typos
Loyal Member
Joined:
Posts:
June 2002
5,279
On December 12, 2014 at 00:13, edizzle said...
try swapping the breaker in the electrical panel to the opposit phase. this should be easily accomplished as long as the panel is not full.

That would be great troubleshooting. But this statement by the OP kinda scares me from that idea.

On December 11, 2014 at 00:47, FreddyFreeloader said...
One last thing I would like to mention that was strange, is that when troubleshooting and looking at at the APC, I started off by bypassing it and plugged an extension cord straight into an outlet in a different room and for some reason the hum got like 10x louder. Tried it back in the dedicated outlet for the rack and it cleared up completely. Wonder what was up with that other circuit and if it's related at all to to my problem.

If, you Freddy, are able to swap the circuit to the other phase and the hum goes away. Or gets louder. Then might I suggest turning one breaker off at a time. After each switch off, listen for the hum. Hopefully one of the breakers will cause the hum to go away. If so, then whatever is on that particular circuit is causing the hum.

KOT
Post 23 made on Friday December 12, 2014 at 09:46
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,321
On December 11, 2014 at 12:08, King of typos said...
Then there are cable company guys who run the cable on the opposite side of the house that the power comes in. The electrician for the power grounded it right at the service entry for the power company. The cable guy grounds the cable at the nearest water pipe, example base board heat.

By law, this isn't legal at least that's what I was told in school. Due to the imbalance of the grounding spots. Granted, the hot water pipe is grounded at the same spot as the electrical service. However, how many solder joints has it gone through? 3, 4, 10 or more?

KOT

That's common, but my satellite equipment wasn't even grounded by the installers- I called DirecTV and told them it needed to be grounded properly and they came back for that because I asked if they wanted me to quote the NEC article I was holding in my hand.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 24 made on Friday December 12, 2014 at 09:57
highfigh
Loyal Member
Joined:
Posts:
September 2004
8,321
The first thing I would do is have the electrical service checked for wiring errors and grounding. It's possible that someone added outlets and didn't follow code. It's also possible that grounded outlets were installed and a wire broke inside of the junction box and the lamp connected to it still works. Once that's done, I would try a different APC to see if that has an internal problem. This should be obvious- it will make noise with one and not with the other.

The projector was said to be on the same circuit as the rack- has anyone proved this, or is it assumed? I would insert a circuit tester in the projector's receptacle and turn off the breaker for that room- if the tester shows power, it's a ground loop in that room. The fact that it's louder when the extension cord is used could mean  the cord may have a problem causing more voltage drop or the other room's wiring is bad. If that room and the EV room share a grounding point outside of the panel will cause this and when conduit is used, sometimes the hot and neutral are fed without making sure the ground to the panel is 'unbroken'. Sometimes, the neutral is omitted and the one from another room is used when the conduit is so full they can't pull a new one and in some cases, the conduit is the ground conductor and the screw on a coupler is loose or corroded- it only takes one to break the ground.
My mechanic told me, "I couldn't repair your brakes, so I made your horn louder."
Post 25 made on Friday December 12, 2014 at 11:09
MediaImageAV
Long Time Member
Joined:
Posts:
June 2012
366
On December 10, 2014 at 19:58, FreddyFreeloader said...
Problem goes away completely when I power my rack straight from the electrical outlet and not by the APC.

Doesn't this indicate that the noise is being introduced by the APC? If any of the other electrical issues mentioned caused noise wouldn't that noise also be present without the APC? Is the APC grounded to the rack? Can you isolate it from the rack(no screws)?
Post 26 made on Friday December 12, 2014 at 13:11
buzz
Super Member
Joined:
Posts:
May 2003
4,371
On December 11, 2014 at 18:51, FP Crazy said...
Was there water in the pipe? If so, it was probably a relatively low resistance ground to mother earth, unless the pipe had no water in it.

Not suggesting it is ideal though

No water, or earth. The cut away, isolated section of pipe was not so neatly tucked up under the floor joists.

Pure water is not a very good conductor. Dry earth is not much of a conductor either. Minerals dissolved in water enhance the earth's conductivity.
Post 27 made on Friday December 12, 2014 at 23:51
Ernie Gilman
Yes, That Ernie!
Joined:
Posts:
December 2001
30,104
On December 12, 2014 at 13:11, buzz said...
Pure water is not a very good conductor. Dry earth is not much of a conductor either. Minerals dissolved in water enhance the earth's conductivity.

Minerals dissolved in water enhance the water's conductivity even more!
A good answer is easier with a clear question giving the make and model of everything.
"The biggest problem in communication is the illusion that it has taken place." -- G. “Bernie” Shaw
OP | Post 28 made on Monday December 15, 2014 at 17:51
FreddyFreeloader
Super Member
Joined:
Posts:
April 2004
3,243
On December 12, 2014 at 00:01, King of typos said...
Since you are dealing with an ups. Have you tried with it unplugged from the outlet? So that the UPS is providing a "clean" source of power? When the UPS is powering the system, does the hum still sound?

KOT

I was there today and low and behold, hum IS present when the system is running on the APC's battery power. It has a slightly different sound but same intensity. Hum goes away when everything gets powered by the naked wall outlet.

Also, to those of you who were asking if I know the projector is on the same circuit. the projector is powered by a power INLET, twist and lock, above the rack where the line feeds into the outlet at the projector, so yes the projector is powered directly from the UPS.

Lastly FWIW I ran an extension cord back out to the hallway outlet and again got awful hum from that naked outlet. This baffles me because this is an everyday 3 bedroom house and never once Have I not been able to use whatever outlet is around to power my system and not have a buzz that was not related to the cable company's grounding.

Once again, when the system is powered by its own naked power outlet without the UPS it works perfectly.

Last edited by FreddyFreeloader on December 15, 2014 17:58.
Post 29 made on Monday December 15, 2014 at 18:13
King of typos
Loyal Member
Joined:
Posts:
June 2002
5,279
I should've asked to have you have the UPS power the entire system. And if hum was present, as it was, then unplug any cable that is coming in from the outside. For example the cable for cable TV, CAT-5 cabling or anything else that is "foreign". Basically make the entire system run off of the UPS. If the hum it still present there, then it's most likely in the UPS. If it's not, then plug each of the foreign cables one at a time until the hum comes back. Then verify it's that particular cable, or a combination of the cables.

I am baffled by the fact that with out the UPS and it plugged into the room next door, the hum is present. But there again, this is why I stated the above for the foreign cables.

KOT
Post 30 made on Monday December 15, 2014 at 21:37
buzz
Super Member
Joined:
Posts:
May 2003
4,371
Be sure to check to see if there is an unexpected ground associated with the projector. (perhaps in its mount)
Page 2 of 2


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.