C4 Wireless Dimmer Question
This thread has 15 replies. Displaying all posts.
Post 1 made on Thursday December 8, 2011 at 13:18
BisyB
Advanced Member
Joined:
Posts:
May 2006
964
Have a client with melted C4-Dim1-Z-x dimmers. The original installer obviously didn't figure on the rating for a multi-gang install.

Can these dimmers just be swapped or do the new dimmers need to be programmed into the system or activated?
Web Design | Hosting - www.bz303.com
Post 2 made on Thursday December 8, 2011 at 13:35
chicagoinstaller
Advanced Member
Joined:
Posts:
September 2004
993
programmed.

It will have to be re-id'd into the programming then refreshed.
and updated if it isnt already a switch at that operating system level.

The switch will work with programming as a dimmer until you add it in, so don't worry about leaving them in the dark. :)

Dont blame the installer yet... maybe the customer decided to swap the 75-100 watt bulbs in the place of the old bulbs and didnt see it as an issue until it melted.

CI
If you can't be good, be good at it.
Post 3 made on Thursday December 8, 2011 at 13:49
Total Control Remotes
Super Member
Joined:
Posts:
July 2006
2,987
When implementing lightiing systems total potential load of the fixture or light sets should always be taken into consideration - not just the wattage of the current bulbs...
OP | Post 4 made on Thursday December 8, 2011 at 14:25
BisyB
Advanced Member
Joined:
Posts:
May 2006
964
Thanks for the feedback. House is 3 years old with original lighting and the 3 gang box where this is happening has loads that are all original and fixture rated total loads of over 800w each. Should have been in separate boxes to start. I'll find an RC C4 dealer to reprogram. Thanks again.
Web Design | Hosting - www.bz303.com
Post 5 made on Thursday December 8, 2011 at 14:27
chicagoinstaller
Advanced Member
Joined:
Posts:
September 2004
993
:)

Last edited by chicagoinstaller on December 8, 2011 14:45.
If you can't be good, be good at it.
Post 6 made on Thursday December 8, 2011 at 14:41
BlackWire Designs
Senior Member
Joined:
Posts:
September 2006
1,401
the dimmers are 1000 watts with both heat sinks, 800 watts with 1 removed and 600 watts with both removed

If its just 1 or 2 lights being IDed i can do it for you. THey need to have a 4sight account with a current subscription
BlackWire Designs
Post 7 made on Thursday December 8, 2011 at 14:58
SDZD
Senior Member
Joined:
Posts:
October 2003
1,082
On December 8, 2011 at 14:41, BlackWire Designs said...
the dimmers are 1000 watts with both heat sinks, 800 watts with 1 removed and 600 watts with both removed

If its just 1 or 2 lights being IDed i can do it for you. THey need to have a 4sight account with a current subscription

This is both correct and incorrect.
The dimmers are 1000W with or without the tabs (what you are calling the heat sinks)

Everytime you add another dimmer to the electrial box you need to derate the dimmer.
1 Dimmer in a box is 1000 Watts.
2 Dimmers in a 2 Gang box is going to be 800Watts
3 Dimmers in a 3 Gang box is going ot 600 Watts and
4 Dimmers in a 4 Gang box is going to be 400 Watts.

You will need to reprogram any replacement dimmers with Composer You will NOT be able to do this with Composer Home.
OP | Post 8 made on Friday December 9, 2011 at 10:13
BisyB
Advanced Member
Joined:
Posts:
May 2006
964
Here's the center dimmer that took the brunt the damage. The other two were functioning but breaking down.

Web Design | Hosting - www.bz303.com
Post 9 made on Friday December 9, 2011 at 11:19
SDZD
Senior Member
Joined:
Posts:
October 2003
1,082
On December 9, 2011 at 10:13, BisyB said...
Here's the center dimmer that took the brunt the damage. The other two were functioning but breaking down.


I think the homeowner is very lucky that the house didn't burn down.
Post 10 made on Friday December 9, 2011 at 12:55
BlackWire Designs
Senior Member
Joined:
Posts:
September 2006
1,401
On December 8, 2011 at 14:58, SDZD said...
This is both correct and incorrect.
The dimmers are 1000W with or without the tabs (what you are calling the heat sinks)

Everytime you add another dimmer to the electrial box you need to derate the dimmer.
1 Dimmer in a box is 1000 Watts.
2 Dimmers in a 2 Gang box is going to be 800Watts
3 Dimmers in a 3 Gang box is going ot 600 Watts and
4 Dimmers in a 4 Gang box is going to be 400 Watts.

You will need to reprogram any replacement dimmers with Composer You will NOT be able to do this with Composer Home.

Umm.. no i am correct.. You are incorrect. A dimmer with no heatsinks and a 1000 watt load = burn your fingers when you touch the screws or heat sink.. If you had 3 dimmers in a box like so

dimmer with 1 heat sink - dimmer no heat sink - dimmer with 1 heat sink then your rating would be 800 - 600 - 800
BlackWire Designs
Post 11 made on Friday December 9, 2011 at 12:57
ichbinbose
Select Member
Joined:
Posts:
August 2011
1,824
On December 9, 2011 at 12:55, BlackWire Designs said...
Umm.. no i am correct.. You are incorrect. A dimmer with no heatsinks and a 1000 watt load = burn your fingers when you touch the screws or heat sink.. If you had 3 dimmers in a box like so

dimmer with 1 heat sink - dimmer no heat sink - dimmer with 1 heat sink then your rating would be 800 - 600 - 800

I would have to agree with kevin on this. aka blackwire
Post 12 made on Friday December 9, 2011 at 13:03
BlackWire Designs
Senior Member
Joined:
Posts:
September 2006
1,401
BTW to be clear the dimmer will still control 1000 watts with out the heat sinks but its going to be BURNING hot
BlackWire Designs
OP | Post 13 made on Friday December 9, 2011 at 13:20
BisyB
Advanced Member
Joined:
Posts:
May 2006
964
They were lucky the damage was in the box only. I can understand the derating options. Normal derating the 800-600-800 would apply as you remove tabs on both sides on the center dimmer and only the inner tabs one on the side dimmers. Given this spec on C4's website though, they make it seem like as soon as you have 3 dimmers in a box, regardless of tabs or heatsinks, it is 600-600-600.

Good question for C4.

[Link: control4.com]
Web Design | Hosting - www.bz303.com
Post 14 made on Saturday December 10, 2011 at 04:09
Mygon
Lurking Member
Joined:
Posts:
December 2011
1
SDZD, you are correct.
Let me help BW here. Dimmer is a 1000W no matter what you do to it. Both tabs off it is still a 1000W dimmer. It's just rated for 600. Doesnt mean its still not a 1000W dimmer. You might have been correct if the description on the box said "1000/800/600 dimmer".
Post 15 made on Saturday December 10, 2011 at 08:06
jimstolz76
Loyal Member
Joined:
Posts:
December 2007
5,607
On December 10, 2011 at 04:09, Mygon said...
SDZD, you are correct.
Let me help BW here. Dimmer is a 1000W no matter what you do to it. Both tabs off it is still a 1000W dimmer. It's just rated for 600. Doesnt mean its still not a 1000W dimmer. You might have been correct if the description on the box said "1000/800/600 dimmer".

Yeah, but who cares if it's a 1000W dimmer if it's being installed in a spot where it has to be derated to 600W?
Page 1 of 2


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.