Substituting Cresnet with Cat5
This thread has 25 replies. Displaying posts 1 through 15.
Post 1 made on Tuesday February 16, 2010 at 05:33
Gman-north
Select Member
Joined:
Posts:
February 2009
2,244
Have a customer that bought a house that was outfitted with a system that was wired with cat 5 to control points. The cat5 runs are approx 75 feet. The old system is fried and he would like to replace with a Crestron system. Specifically APADs for interfaces. Has anyone successfully used cat5 for control wires? I know Crestron doesn't support this but I have heard that some dealers have done this before. Just not sure how stable it is. Any input would be appreciated.
Post 2 made on Tuesday February 16, 2010 at 07:00
Bruce Sinclair
Active Member
Joined:
Posts:
April 2003
694
I had to do this in a home 3 years ago and it is still working well. Use two conductors each for power and ground then use a twisted pair for Y and Z. Cresnet wire is still the best solution when you have a choice.
Bruce Sinclair CMB Integrations LLC DMC-E
"Those who are most critical, often have no real skills themsevles"
Post 3 made on Tuesday February 16, 2010 at 08:18
GotGame
Super Member
Joined:
Posts:
February 2002
4,022
Works fine in my own home. Pick a twisted pair for y and z and the remaining conductors make power and ground.
I may be schizophrenic, but at least I have each other.
Post 4 made on Tuesday February 16, 2010 at 08:46
Mr. Brad
Advanced Member
Joined:
Posts:
April 2008
934
I used CAT5 in my own house to connect numerous APADs. Crestron has a specific data sheet for this connection. I suggest you go online or contact support to get a copy. As mentioned in an earlier post, they specify sharing pairs for power, but I’m not sure about data.

I do NOT love the APAD as an interface. They have the new TPMC-4SM that is POE, is designed for a single CAT5 and will blow the doors off the APAD if you can handle the price. Did I mention that I didn’t love the APAD? I meant to say, I can’t imagine ever designing one into a new job.
Post 5 made on Tuesday February 16, 2010 at 08:57
jmacdonald
Active Member
Joined:
Posts:
November 2006
695
I've used Cat 5 for cresnet for years....back to 1999.

I would use a pair for every signal : 24, Y, Z and G.

You could still use 1 pair for Y and G.

I would also use Cat5 for RS-232, and IR : you could use it over 100'.
John / Simplevu
[Link: facebook.com]
[Link: simplevu.com]
Post 6 made on Tuesday February 16, 2010 at 09:04
roddymcg
Loyal Member
Joined:
Posts:
September 2003
6,796
It was the norm for many to cut costs and use Cat5, I have even had to use16/4 in a pinch. No I did not wire this way. Just be careful and very conservative with your Crestnet power calculations when doing this...

Obviously run Crestnet wire whenever possible...
When good enough is not good enough.
OP | Post 7 made on Tuesday February 16, 2010 at 09:05
Gman-north
Select Member
Joined:
Posts:
February 2009
2,244
On February 16, 2010 at 08:46, Mr. Brad said...
I do NOT love the APAD as an interface. They have the new TPMC-4SM that is POE, is designed for a single CAT5 and will blow the doors off the APAD if you can handle the price. Did I mention that I didn’t love the APAD? I meant to say, I can’t imagine ever designing one into a new job.

The job is a bit cost restrictive but now that you mention it, I'll try him on with the TPMC-4SM. Will throw in a couple of CEN-SW-POE-5 switches to get power to the panels.
OP | Post 8 made on Tuesday February 16, 2010 at 09:08
Gman-north
Select Member
Joined:
Posts:
February 2009
2,244
On February 16, 2010 at 08:57, jmacdonald said...
I would also use Cat5 for RS-232, and IR : you could use it over 100'.

Not sure that I'd push thnvelope with 232 over 75 feet.....
Post 9 made on Tuesday February 16, 2010 at 09:53
Audible Solutions
Super Member
Joined:
Posts:
March 2004
3,246
On February 16, 2010 at 08:57, jmacdonald said...
I've used Cat 5 for cresnet for years....back to 1999.

I would use a pair for every signal : 24, Y, Z and G.

Under no circumstances should you follow this advice and split the pairs on a UTP data cable. While it might work and I know of some large salons who've foolishly hit on this particularly wiring scheme it is not only wrong it will likely cause issues on a larger system.

On February 16, 2010 at 08:57, jmacdonald said...
You could still use 1 pair for Y and G.

I would also use Cat5 for RS-232, and IR : you could use it over 100'.

This is far better advice. When using CAT5 for Cresnet I use 1pair + 1 wire for power and ground ( eg., blue pair + brown for +24, Green pair + brown/white for ground and orange pair for Y and Z ). Be sure to do a voltage drop calculation, particularly when using CAT5 for power. At 75 feet with APADs you will be fine if you follow my 3 wire for power and ground.

I have also used CAT5 for serial at 100 ft. Given the gage you will want to be careful. You will also may run out of wires since smart money would have each pair as signal and ground (eg., blue for TX$, blue/white for TX$ gnd; Orange for RX$, OR/white for RX$ gnd. Green for RTS/CTS, Brown for DTR/DSR ).

Alan
"This is a Christian Country,Charlie,founded on Christian values...when you can't put a nativiy scene in front fire house at Christmas time in Nacogdoches Township, something's gone terribly wrong"
Post 10 made on Tuesday February 16, 2010 at 11:35
mr2channel
Select Member
Joined:
Posts:
August 2002
1,701
I do not have the document on the pc I am on now, but Crestron does have a document posted on the dealer side of the site regarding how they want Cat5 termitated along with a distance calculator as it relates to power draw.

hope that helps.
What part of "A well regulated Militia, being necessary to the security of a free State, the right of the people to keep and bear Arms, shall not be infringed." do you not understand?
Post 11 made on Tuesday February 16, 2010 at 14:06
kkrussell
Lurking Member
Joined:
Posts:
December 2009
4
Per Crestron True Blue Tech several years ago, think about 4 years ago or so, when wiring with Cat5,

24 is the orange pair
y is blue
z is blue white
G is the green pair.
Brown pair is unused

Like I said, that's how Crestron told us to do cat5 years ago, if you have a problem, that's the first question they will ask you though, are you using cat5 or cresnet.
Post 12 made on Tuesday February 16, 2010 at 16:17
mr2channel
Select Member
Joined:
Posts:
August 2002
1,701
FWIW I yanked a full elan system that had cat3 cable in a 7Kft house and put in an adagio a few years back with apads and 12 button keypads and worked fine and so far no call backs with issues....the real fun part was integrating the z600 door station...lets just say it involved a couple relays and power supplies.
What part of "A well regulated Militia, being necessary to the security of a free State, the right of the people to keep and bear Arms, shall not be infringed." do you not understand?
Post 13 made on Tuesday February 16, 2010 at 16:36
39 Cent Stamp
Elite Member
Joined:
Posts:
May 2007
17,518
On February 16, 2010 at 08:46, Mr. Brad said...
I used CAT5 in my own house to connect numerous APADs. Crestron has a specific data sheet for this connection. I suggest you go online or contact support to get a copy. As mentioned in an earlier post, they specify sharing pairs for power, but I’m not sure about data.

I do NOT love the APAD as an interface. They have the new TPMC-4SM that is POE, is designed for a single CAT5 and will blow the doors off the APAD if you can handle the price. Did I mention that I didn’t love the APAD? I meant to say, I can’t imagine ever designing one into a new job.

What he said.
Avid Stamp Collector - I really love 39 Cent Stamps
Post 14 made on Wednesday February 17, 2010 at 06:28
ejfiii
Select Member
Joined:
Posts:
July 2003
2,021
That doc is no longer available on true blue support site. I think they just gave up given the expense of supporting dealers who think you can do this

On February 16, 2010 at 08:57, jmacdonald said...
I've used Cat 5 for cresnet for years....back to 1999.

I would use a pair for every signal : 24, Y, Z and G.

I sincerely hope you are not remembering correctly and have not really been wiring crestron homes this way since 1999.
Post 15 made on Wednesday February 17, 2010 at 10:17
jmacdonald
Active Member
Joined:
Posts:
November 2006
695
On February 16, 2010 at 09:08, Gman-north said...
Not sure that I'd push thnvelope with 232 over 75 feet.....

it works! i've done it more than once.

In thoses days, I was working for a company. If they gave me cat5 to do it, I would.

Time has changed.
John / Simplevu
[Link: facebook.com]
[Link: simplevu.com]
Page 1 of 2


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.