Crestron Rack2 Overloading C2N-SPWS300
This thread has 5 replies. Displaying all posts.
Post 1 made on Thursday May 17, 2012 at 10:40
Deepseadata
Long Time Member
Joined:
Posts:
July 2011
42
Hi guys,

While I wait for my installer to get back to me I thought I'd try to educate myself as to why my Rack2 "could" be overloading its 24vdc channel of my C2N-SPWS300?

It's been working in its spot for about 6 years.

I had a UPS go boom a week ago and just replaced it. Everything was working fine until I noticed my iPad wasn't able to connect to the Rack2.

I pulled it out and saw "overload" lit. I reset it... the Rack2 blinked a couple times and then the overload came back on. When I unplug the Rack2 and reset the SPWS300's channel resets fine. When I plug the Rack2 back in it overloads again.

Has anyone had a Rack2 go south on them before?
60% of the time I'm wrong all the time.
Post 2 made on Thursday May 17, 2012 at 11:41
39 Cent Stamp
Elite Member
Joined:
Posts:
May 2007
17,518
Everything goes south at some point. The Rack 2 needs 12 watts. 1 channel on the power supply provides 75. (We try and stay around 60 on each channel to stay under 85%). Do you have anything else on the channel with the Rack2? If not i would measure wattage coming from the power supply channel. If its checking out then i would connect the Rack2 to another power supply channel to see if it also overloads that one. If it does then chances are your Rack2 has a problem or maybe something connected to its HUB (if it has one).
Avid Stamp Collector - I really love 39 Cent Stamps
Post 3 made on Thursday May 17, 2012 at 12:07
Tom Luczywo
Founding Member
Joined:
Posts:
November 2001
115
Voltage testing is key.  And also test with it under load.  Is anything connected Cresnet to the Rack2 that isn't connected to a leg on the 300?  What happens if you try the other side of the 300?
Post 4 made on Thursday May 17, 2012 at 14:26
Sean@iTank
Long Time Member
Joined:
Posts:
August 2011
193
On May 17, 2012 at 11:41, 39 Cent Stamp said...
Everything goes south at some point. The Rack 2 needs 12 watts.

The RACK2 uses 12 watts without any cards installed. A fully loaded chassis could use 50W or more.
Post 5 made on Thursday May 17, 2012 at 14:54
Audible Solutions
Super Member
Joined:
Posts:
March 2004
3,246
On May 17, 2012 at 12:07, Tom Luczywo said...
Voltage testing is key.  And also test with it under load.  Is anything connected Cresnet to the Rack2 that isn't connected to a leg on the 300?  What happens if you try the other side of the 300?

Yep, and check to see if the fan has stopped running.
"This is a Christian Country,Charlie,founded on Christian values...when you can't put a nativiy scene in front fire house at Christmas time in Nacogdoches Township, something's gone terribly wrong"
Post 6 made on Thursday May 17, 2012 at 14:59
39 Cent Stamp
Elite Member
Joined:
Posts:
May 2007
17,518
On May 17, 2012 at 14:26, Sean@iTank said...
The RACK2 uses 12 watts without any cards installed. A fully loaded chassis could use 50W or more.

Good catch. I could have sworn I typed that/this..."rack2 could possibly be using up the channel".
Avid Stamp Collector - I really love 39 Cent Stamps


Jump to


Protected Feature Before you can reply to a message...
You must first register for a Remote Central user account - it's fast and free! Or, if you already have an account, please login now.

Please read the following: Unsolicited commercial advertisements are absolutely not permitted on this forum. Other private buy & sell messages should be posted to our Marketplace. For information on how to advertise your service or product click here. Remote Central reserves the right to remove or modify any post that is deemed inappropriate.