Post 2 made on Tuesday March 2, 2010 at 19:17
dinom
Active Member
Joined:
Posts:
February 2004
643
The 12V/100mA spec. is for when the port is configured as a trigger "output". Basically, it uses the XP-8 power supply to source the voltage and current.

The 30VDC at 3 Amps is the contact closure spec. when using the relay as a simple single pole, single pole switch, which is what you'd be doing with the garage door hookup (set up as normally open). In device properties of the XP-8, under Relay Type tab, make sure Contact Closure (default) is selected for the appropriate port.

I'd say you're OK.