The following is a lot of an article published in August of 2013 by someone WAY THE HELL ahead of me! It's at
[Link: siemon.com]A standards-based UTP network cabling system requires no path to ground. However, according to ANSI-J-STD-607-A “Commercial Building Grounding (Earthing) and Bonding Requirements For Telecommunications”, screened and shielded cabling channels are required to be bonded through a conducting path to the Telecommunications Grounding Busbar (TGB) in the telecommunications room (TR). Like UTP systems, F/UTP and S/FTP horizontal cable is terminated to outlets at the work area and in the TR. Screened and shielded connector designs, such as Siemon’s Z-MAX™ 6A Shielded and TERA® outlets, automatically ground to the patch panel in the TR during installation, without the need to individually provide a ground termination for each outlet. The only additional step required to ground these F/UTP and S/FTP cabling systems is to connect a 6 AWG wire from the ground lug provided on the patch panel to the TGB.
The recommended grounding sequence is as follows: the , the outlet self-grounds to the patch panel, and then the panel is grounded to the equipment rack or adjacent metallic pathways. The basic sequence is reflected in the diagram below.
1. F/UTP cables screen or the S/FTP shield is terminated by the outlet
2. Outlet makes contact with patch panel’s grounding strip as outlets are snapped into place
3. Panel is grounded to equipment rack or adjacent metal pathways via a 12 AWG wire attached to panel ground lug
4. 6 AWG ground wire connects rack to the TGB