I'm assuming you mean 10BaseT, 100BaseT and 1000BaseT.
Pins 1,2,3, and 6 are all used on 10/100 networks. Pins 1-8 are used on Gigabit or 1000BaseT. No matter if the termination is TIA-568A or B, the green pair is going to be used on pins 1 and 2, or 3 and 6. For this reason, if the green pair is truly damaged, you will need to move them into a position that isn't used such as where the brown or blue pair would normally go. Whatever pair you swap it with will go back where the green pair goes.
Here is an example that should work:
1 - Blue Stripe 2 - Blue 3 - Orange Stripe 4 - Green 5 - Green Stripe 6 - Orange 7 - Brown Stripe 8 - Brown
|
|