It is type CL2 wire which is suitable for general purpose, which means that it can be installed just about anywhere EXCEPT for riser, duct, plenum, and environmental air installations. So the short answer is yes, it may be installed in conduit technically. However, if the conduit is installed in a damp or wet location, the inside of the conduit is considered a damp or wet location, which means that the wire must be identified for use in a damp or wet location. This wire does not appear to be rated for damp or wet locations.
110.11 says that no conductors shall be located in damp or wet locations (unless identified for use in those locations).
If the conduit is installed in a dry location, you are fine.
|
|